CHAPTER 5: SETPOINTS
5.2 PRODUCT SETUP
GEK-106310-AF
F650 DIGITAL BAY CONTROLLER
5-7
For this setting change to take effect, a reboot is required.
5.2.1.3 MODBUS protocol
ModBus Slave Addresses for serial and Ethernet communication and the ModBus port number used for ModBus TCP/IP. For
more detailed information go to appendix B in this manual.
5.2.1.4 DNP3 slave
Physical port, Slave Address for DNP, IP Addresses for Masters, TCP/UDP Port, Unsolicited Response parameters, Analog
scale factors and deadbands, message fragment size, Binary input block. For more detailed information go to appendix C
in this manual. DNP protocol is available for standard and IEC61850 models but it is not available Procome models.
Table 5-5: DNP protocol settings
Product Setup > Communication settings >ModBus ProtocoL
Name
Default Value
Step
Range
ModBus Address COM1 254
1
[1 : 255]
ModBus Address COM2 254
1
[1 : 255]
ModBus Port Number
502
1
[0 : 65535]
Product Setup > Communication settings >DNP3 Slave
DNP3 Slave 1 > DNP3 Slave 2 > DNP3 Slave 3
Name
Default Value
Step
Range
Physical Port
NONE
N/A
[COM1:COM2:NETWORK]
Address
255
1
[0 : 65534]
IP Addr Client1 Oct1
0
1
[0 : 255]
IP Addr Client1 Oct2
0
1
[0 : 255]
IP Addr Client1 Oct3
0
1
[0 : 255]
IP Addr Client1 Oct4
0
1
[0 : 255]
IP Addr Client2 Oct1
0
1
[0 : 255]
IP Addr Client2 Oct2
0
1
[0 : 255]
IP Addr Client2 Oct3
0
1
[0 : 255]
IP Addr Client2 Oct4
0
1
[0 : 255]
IP Addr Client3 Oct1
0
1
[0 : 255]
IP Addr Client3 Oct2
0
1
[0 : 255]
IP Addr Client3 Oct3
0
1
[0 : 255]
IP Addr Client3 Oct4
0
1
[0 : 255]
IP Addr Client4 Oct1
0
1
[0 : 255]
IP Addr Client4 Oct2
0
1
[0 : 255]
IP Addr Client4 Oct3
0
1
[0 : 255]
IP Addr Client4 Oct4
0
1
[0 : 255]
IP Addr Client5 Oct1
0
1
[0 : 255]
IP Addr Client5 Oct2
0
1
[0 : 255]
IP Addr Client5 Oct3
0
1
[0 : 255]
IP Addr Client5 Oct4
0
1
[0 : 255]
TCP/UDP Port
20000
1
[0 : 65535]
Unsol Resp Function
DISABLED
N/A
[DISABLED – ENABLED]
Unsol Resp TimeOut
5
1
[0 : 60]
Unsol Resp Max Ret
10
1
[0 : 255]
Unsol Resp Dest Adr
200
1
[0 : 65535]
Current Scale Factor
1
N/A
[0.00001-0.0001-0.001-0.01-0.1-1-10-
100-1000]
Содержание F650
Страница 68: ...2 32 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 2 6 EXTERNAL CONNECTIONS CHAPTER 2 PRODUCT DESCRIPTION ...
Страница 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Страница 660: ...7 254 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 7 3 IEC 61850 CONFIGURATOR CHAPTER 7 IEC 61850 PROTOCOL ...
Страница 734: ...12 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 12 4 RELAY CONFIGURATION CHAPTER 12 FREQUENTLY ASKED QUESTIONS ...
Страница 772: ...A 32 F650 DIGITAL BAY CONTROLLER GEK 106310 AF A 1 OPERANDS F650 MODEL FX GX APPENDIX A LOGIC OPERANDS ...
Страница 950: ...c 24 F650 DIGITAL BAY CONTROLLER GEK 106310 AF C 8 ANALOG INPUTS APPENDIX C DNP 3 0 PROTOCOL FOR F650 ...
Страница 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Страница 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Страница 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Страница 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 1044: ...I 40 F650 DIGITAL BAY CONTROLLER GEK 106310 AF I 2 FACTORY DEFAULT CONFIGURATION APPENDIX I FACTORY DEFAULT CONFIGURATION ...
Страница 1046: ...J 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF J 1 GE MULTILIN WARRANTY APPENDIX J MISCELLANEOUS ...