GE Multilin
F35 Multiple Feeder Protection System
6-17
6 ACTUAL VALUES
6.3 METERING
6
The metered values for current and power demand are displayed in this menu. The "SRC 1" text will be replaced by what-
ever name was programmed by the user for the associated source (see
SETTINGS
ÖØ
SYSTEM SETUP
ÖØ
SIGNAL
SOURCES
).
The relay measures (absolute values only) the source demand on each phase and average three phase demand for real,
reactive, and apparent power. These parameters can be monitored to reduce supplier demand penalties or for statistical
metering purposes. Demand calculations are based on the measurement type selected in the
SETTINGS
Ö
PRODUCT SETUP
ÖØ
DEMAND
menu. For each quantity, the relay displays the demand over the most recent demand time interval, the maxi-
mum demand since the last maximum demand reset, and the time and date stamp of this maximum demand value. Maxi-
mum demand quantities can be reset to zero with the
CLEAR RECORDS
ÖØ
CLEAR DEMAND RECORDS
command.
i) FREQUENCY METERING
PATH: ACTUAL VALUES
ÖØ
METERING
Ö
SOURCE SRC 1
ÖØ
FREQUENCY
The metered frequency values are displayed in this menu. The "SRC 1" text will be replaced by whatever name was pro-
grammed by the user for the associated source (see
SETTINGS
ÖØ
SYSTEM SETUP
ÖØ
SIGNAL SOURCES
).
SOURCE FREQUENCY
is measured via software-implemented zero-crossing detection of an AC signal. The signal is either a
Clarke transformation of three-phase voltages or currents, auxiliary voltage, or ground current as per source configuration
(see the
SYSTEM SETUP
ÖØ
POWER SYSTEM
settings). The signal used for frequency estimation is low-pass filtered. The
final frequency measurement is passed through a validation filter that eliminates false readings due to signal distortions and
transients.
MESSAGE
SRC 1 DMD IC:
0.000 A
MESSAGE
SRC 1 DMD IC MAX:
0.000 A
MESSAGE
SRC 1 DMD IC DATE:
2001/07/31 16:30:07
MESSAGE
SRC 1 DMD W:
0.000 W
MESSAGE
SRC 1 DMD W MAX:
0.000 W
MESSAGE
SRC 1 DMD W DATE:
2001/07/31 16:30:07
MESSAGE
SRC 1 DMD VAR:
0.000 var
MESSAGE
SRC 1 DMD VAR MAX:
0.000 var
MESSAGE
SRC 1 DMD VAR DATE:
2001/07/31 16:30:07
MESSAGE
SRC 1 DMD VA:
0.000 VA
MESSAGE
SRC 1 DMD VA MAX:
0.000 VA
MESSAGE
SRC 1 DMD VA DATE:
2001/07/31 16:30:07
FREQUENCY
SRC 1
SRC 1 FREQUENCY:
0.00 Hz
Содержание F35
Страница 2: ......
Страница 4: ......
Страница 30: ...1 20 F35 Multiple Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Страница 122: ...4 30 F35 Multiple Feeder Protection System GE Multilin 4 3 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Страница 296: ...5 174 F35 Multiple Feeder Protection System GE Multilin 5 9 TESTING 5 SETTINGS 5 ...
Страница 328: ...7 8 F35 Multiple Feeder Protection System GE Multilin 7 2 TARGETS 7 COMMANDS AND TARGETS 7 ...
Страница 332: ...8 4 F35 Multiple Feeder Protection System GE Multilin 8 1 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Страница 350: ...A 16 F35 Multiple Feeder Protection System GE Multilin A 1 PARAMETER LIST APPENDIXA A ...
Страница 422: ...B 72 F35 Multiple Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIXB B ...
Страница 460: ...D 10 F35 Multiple Feeder Protection System GE Multilin D 1 IEC 60870 5 104 PROTOCOL APPENDIXD D ...
Страница 472: ...E 12 F35 Multiple Feeder Protection System GE Multilin E 2 DNP POINT LISTS APPENDIXE E ...