GE Multilin
F35 Multiple Feeder Protection System
5-19
5 SETTINGS
5.2 PRODUCT SETUP
5
port paired control points, with each paired control point operating two virtual inputs. The
DNP NUMBER OF PAIRED CONTROL
POINTS
setting allows configuration of from 0 to 32 binary output paired controls. Points not configured as paired operate on
a one-to-one basis.
The
DNP ADDRESS
setting is the DNP slave address. This number identifies the F35 on a DNP communications link. Each
DNP slave should be assigned a unique address.
The
DNP TCP CONNECTION TIMEOUT
setting specifies a time delay for the detection of dead network TCP connections. If
there is no data traffic on a DNP TCP connection for greater than the time specified by this setting, the connection will be
aborted by the F35. This frees up the connection to be re-used by a client.
Relay power must be re-cycled after changing the
DNP TCP CONNECTION TIMEOUT
setting for the changes to take
effect.
f) DNP / IEC 60870-5-104 POINT LISTS
PATH: SETTINGS
Ö
PRODUCT SETUP
ÖØ
COMMUNICATIONS
ÖØ
DNP / IEC104 POINT LISTS
The binary and analog inputs points for the DNP protocol, or the MSP and MME points for IEC 60870-5-104 protocol, can
configured to a maximum of 256 points. The value for each point is user-programmable and can be configured by assigning
FlexLogic™ operands for binary inputs / MSP points or FlexAnalog parameters for analog inputs / MME points.
The menu for the binary input points (DNP) or MSP points (IEC 60870-5-104) is shown below.
PATH: SETTINGS
Ö
PRODUCT SETUP
ÖØ
COMMUNICATIONS
ÖØ
DNP / IEC104 POINT LISTS
Ö
BINARY INPUT / MSP POINTS
Up to 256 binary input points can be configured for the DNP or IEC 60870-5-104 protocols. The points are configured by
assigning an appropriate FlexLogic™ operand. Refer to the
Introduction to FlexLogic™
section in this chapter for the full
range of assignable operands.
The menu for the analog input points (DNP) or MME points (IEC 60870-5-104) is shown below.
PATH: SETTINGS
Ö
PRODUCT SETUP
ÖØ
COMMUNICATIONS
ÖØ
DNP / IEC104 POINT LISTS
ÖØ
ANALOG INPUT / MME POINTS
Up to 256 analog input points can be configured for the DNP or IEC 60870-5-104 protocols. The analog point list is config-
ured by assigning an appropriate FlexAnalog parameter to each point. Refer to Appendix A:
FlexAnalog Parameters
for the
full range of assignable parameters.
DNP / IEC104
POINT LISTS
BINARY INPUT / MSP
POINTS
Range: see sub-menu below
MESSAGE
ANALOG INPUT / MME
POINTS
Range: see sub-menu below
BINARY INPUT / MSP
POINTS
Point:
0
Off
Range: FlexLogic™ operand
MESSAGE
Point:
1
Off
Range: FlexLogic™ operand
↓
MESSAGE
Point:
255
Off
Range: FlexLogic™ operand
ANALOG INPUT / MME
POINTS
Point:
0
Off
Range: any FlexAnalog parameter
MESSAGE
Point:
1
Off
Range: any FlexAnalog parameter
↓
MESSAGE
Point:
255
Off
Range: any FlexAnalog parameter
NOTE
Содержание F35
Страница 2: ......
Страница 4: ......
Страница 30: ...1 20 F35 Multiple Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Страница 122: ...4 30 F35 Multiple Feeder Protection System GE Multilin 4 3 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Страница 296: ...5 174 F35 Multiple Feeder Protection System GE Multilin 5 9 TESTING 5 SETTINGS 5 ...
Страница 328: ...7 8 F35 Multiple Feeder Protection System GE Multilin 7 2 TARGETS 7 COMMANDS AND TARGETS 7 ...
Страница 332: ...8 4 F35 Multiple Feeder Protection System GE Multilin 8 1 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Страница 350: ...A 16 F35 Multiple Feeder Protection System GE Multilin A 1 PARAMETER LIST APPENDIXA A ...
Страница 422: ...B 72 F35 Multiple Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIXB B ...
Страница 460: ...D 10 F35 Multiple Feeder Protection System GE Multilin D 1 IEC 60870 5 104 PROTOCOL APPENDIXD D ...
Страница 472: ...E 12 F35 Multiple Feeder Protection System GE Multilin E 2 DNP POINT LISTS APPENDIXE E ...