7-8
F60 Feeder Protection System
GE Multilin
7.1 COMMANDS
7 COMMANDS AND TARGETS
7
MODULE FAILURE 07 — Event message reads SYSTEM INTEGRITRY RECOVERY 07 when a reboot was required
and otherwise MODULE FAILURE 07 when a failure was detected
MODULE FAILURE 08 — Event message reads SYSTEM INTEGRITRY RECOVERY 08 when a reboot was required
and otherwise MODULE FAILURE 08 when a failure was detected
MODULE FAILURE 11 — Event message reads SYSTEM INTEGRITRY RECOVERY 11 when a reboot was required
and otherwise MODULE FAILURE 11 when a failure was detected
•
How often the test is performed
: Module dependent.
•
What to do
: Contact the factory and supply the failure code noted in the display. The “xxx” text identifies the failed mod-
ule (for example, F8L).
c) MINOR SELF-TEST ERROR MESSAGES
Most of the minor self-test errors can be disabled. See the settings in the
User-programmable Self-tests
section in chapter
5.
•
Latched target message
: Yes.
•
Description of problem
: Module hardware failure detected. Module Failures 12 and 31 to 33 are minor.
•
How often the test is performed
: Module dependent.
•
What to do
: Contact the factory and supply the failure code noted in the display. The “xxx” text identifies the failed mod-
ule (for example, F8L).
For Module Failure 31, a new process card hardware is available. The process card hardware has been enhanced to
support new features, such as fast distance protection, Synchrophasors Frequency, and Rate of Change of Frequency
calculations to conform to C37.118 - 2005 standard. The new functionality leveraging the hardware is supported with
firmware revision 7.25 and above. When using an older revision of the process card with a new firmware revision
(7.25), Module Failure 31 indicates the limited functionality. If your application requires the new functionality, then new
process card hardware is required and otherwise you can continue using the existing hardware. To know the revision
of your hardware, contact the factory.
•
Latched target message
: No.
•
Description of problem
: A data item in a configurable GOOSE data set is not supported by the F60 order code.
•
How often the test is performed
: On power up
.
•
What to do
: Verify that all the items in the GOOSE data set are supported by the F60. The EnerVista UR Setup soft-
ware will list the valid items. An IEC61850 client will also show which nodes are available for the F60.
•
Latched target message
: No.
•
Description of problem
: A data item in a configurable report data set is not supported by the F60 order code.
•
How often the test is performed
: On power up
.
•
What to do
: Verify that all the items in the configurable report data set are supported by the F60. The EnerVista UR
Setup software will list the valid items. An IEC61850 client will also show which nodes are available for the F60.
•
Latched target message
: Yes.
MODULE FAILURE___:
Contact Factory (xxx)
IEC 61850 DATA SET:
LLN0 GOOSE# Error
IEC 61850 DATA SET:
LLN0 BR# Error
MAINTENANCE ALERT:
Replace Battery
Содержание F60
Страница 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Страница 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Страница 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Страница 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Страница 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Страница 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Страница 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Страница 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Страница 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Страница 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Страница 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Страница 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...