GE Multilin
F60 Feeder Protection System
2-19
2 PRODUCT DESCRIPTION
2.4 SPECIFICATIONS
2
2.4SPECIFICATIONS
SPECIFICATIONS ARE SUBJECT TO CHANGE WITHOUT NOTICE
2.4.1 PROTECTION ELEMENTS
The operating times include the activation time of a trip rated form-A output contact unless otherwise indicated.
FlexLogic operands of a given element are 4 ms faster. Take this into account when using FlexLogic to interconnect
with other protection or control elements of the relay, building FlexLogic equations, or interfacing with other IEDs or
power system devices via communications or different output contacts. If not specified, the operate times given
here are for a 60 Hz system at nominal system frequency. Operate times for a 50 Hz system are 1.2 times longer.
RESTRICTED GROUND FAULT
Pickup:
0.005 to 30.000 pu in steps of 0.001
Dropout:
97 to 98% of pickup
Level accuracy:
0.1 to 2.0 x CT rating: ±0.5% of reading or ±1% of rated (which-
ever is greater)
>2.0 x CT rating
±1.5% of reading
Slope:
0 to 100% in steps of 1%
Pickup delay:
0 to 600.00 s in steps of 0.01
Dropout delay:
0 to 600.00 s in steps of 0.01
Operate time:
<1 power system cycle
PHASE/NEUTRAL/GROUND TOC
Current:
Phasor or RMS
Pickup level:
0.000 to 30.000 pu in steps of 0.001
Dropout level:
97% to 98% of pickup
Level accuracy:
0.1 to 2.0
×
CT:
±0.5% of reading or ±0.4% of rated
(whichever is greater)
> 2.0
×
CT:
±1.5% of reading > 2.0
×
CT rating
Curve shapes:
IEEE Moderately/Very/Extremely
Inverse; IEC (and BS) A/B/C and Short
Inverse; GE IAC Inverse, Short/Very/
Extremely Inverse; I
2
t; FlexCurves™
(programmable); Definite Time (0.01 s
base curve)
Curve multiplier:
Time Dial = 0.00 to 600.00 in steps of
0.01
Reset type:
Instantaneous/Timed (per IEEE)
Curve timing accuracy
at 1.03 to 20 x pickup:
±3.5% of operate time or ±½ cycle
(whichever is greater) from pickup to
operate
Voltage restraint:
modifies pickup current for voltage in the
range of 0.1<V<0.9 VT Nominal in a
fixed linear relationship
PHASE/NEUTRAL/GROUND IOC
Pickup level:
0.000 to 30.000 pu in steps of 0.001
Dropout level:
97 to 98% of pickup
Level accuracy:
0.1 to 2.0
×
CT rating: ±0.5% of reading or ±0.4% of rated
(whichever is greater)
> 2.0
×
CT rating
±1.5% of reading
Overreach:
<2%
Pickup delay:
0.00 to 600.00 s in steps of 0.01
Reset delay:
0.00 to 600.00 s in steps of 0.01
Operate time:
<16 ms at 3
×
pickup at 60 Hz
(Phase/Ground IOC)
<20 ms at 3
×
pickup at 60 Hz
(Neutral IOC)
Timer accuracy:
±3% of operate time or ±1/4 cycle
(whichever is greater)
NEGATIVE SEQUENCE TOC
Pickup level:
0.000 to 30.000 pu in steps of 0.001
Dropout level:
97% to 98% of pickup
Level accuracy:
±0.5% of reading or ±0.4% of rated
(whichever is greater)
from 0.1 to 2.0 x CT rating
±1.5% of reading > 2.0 x CT rating
Curve shapes:
IEEE Moderately/Very/Extremely
Inverse; IEC (and BS) A/B/C and Short
Inverse; GE IAC Inverse, Short/Very/
Extremely Inverse; I
2
t; FlexCurves™
(programmable); Definite Time (0.01 s
base curve)
Curve multiplier (Time dial): 0.00 to 600.00 in steps of 0.01
Reset type:
Instantaneous/Timed (per IEEE) and Lin-
ear
Curve timing accuracy
at 1.03 to 20 x pickup:
±3.5% of operate time or ±½ cycle
(whichever is greater) from pickup to
operate
NEGATIVE SEQUENCE IOC
Pickup level:
0.000 to 30.000 pu in steps of 0.001
Dropout level:
97 to 98% of pickup
Level accuracy:
0.1 to 2.0
×
CT rating: ±0.5% of reading
or ±0.4% of rated (whichever is greater);
>
2.0
×
CT rating: ±1.5% of reading
Overreach:
<
2%
Pickup delay:
0.00 to 600.00 s in steps of 0.01
Reset delay:
0.00 to 600.00 s in steps of 0.01
Operate time:
<20 ms at 3
×
pickup at 60 Hz
Timer accuracy:
±3% of operate time or ±1/4 cycle
(whichever is greater)
NOTE
Содержание F60
Страница 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Страница 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Страница 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Страница 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Страница 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Страница 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Страница 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Страница 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Страница 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Страница 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Страница 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Страница 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...