GE Multilin
F60 Feeder Protection System
5-303
5 SETTINGS
5.8 INPUTS/OUTPUTS
5
GOOSE Analogs that represent current, voltage, power, frequency, angles, or power factor can be used in a FlexEle-
ment. The following text must be used in the UNITS setting, to represent these types of analogs: A, V, W, var, VA, Hz,
deg, and no text (blank setting) for power factor.
GOOSE Analogs can be compared to other GOOSE Analogs with any character string or no string.
•
GOOSE ANALOG 1 PU
: This setting specifies the per-unit base factor when using the GOOSE analog input FlexAna-
log values in other F60 features, such as FlexElements. The base factor is applied to the GOOSE analog input FlexAn-
alog quantity to normalize it to a per-unit quantity. The base units are described in the following table.
The per-unit base setting represents thousands, not single units. For example, a PU base of 1.000 is actually 1000 and
a PU base of 0.001 is 1.
When using GOOSE Analogs and PU base in FlexElements, the largest value that can be displayed in the FlexEle-
ment actual values is 2,140,000.000.
The GOOSE analog input FlexAnalog values are available for use in other F60 functions that use FlexAnalog values.
5.8.13 IEC 61850 GOOSE INTEGERS
PATH: SETTINGS
INPUTS/OUTPUTS
IEC 61850 GOOSE UINTEGERS
GOOSE UINTEGER INPUT 1(16)
The IEC 61850 GOOSE uinteger inputs feature allows the transmission of FlexInteger values between any two UR-series
devices. The following settings are available for each GOOSE uinteger input.
•
UINTEGER 1 DEFAULT
: This setting specifies the value of the GOOSE uinteger input when the sending device is
offline and the
UINTEGER 1 DEFAULT MODE
is set to “Default Value”.This setting is stored as a 32-bit unsigned integer
number.
Table 5–39: GOOSE ANALOG INPUT BASE UNITS
ELEMENT
BASE UNITS
BREAKER ARCING AMPS
(Brk X Arc Amp A, B, and C)
BASE = 2000 kA
2
×
cycle
dcmA
BASE = maximum value of the
DCMA INPUT MAX
setting for the two transducers configured
under the +IN and –IN inputs.
FREQUENCY
f
BASE
= 1 Hz
FREQUENCY RATE OF CHANGE
df/dt
BASE
= 1 Hz/s
PHASE ANGLE
ϕ
BASE
= 360 degrees (see the UR angle referencing convention)
POWER FACTOR
PF
BASE
= 1.00
RTDs
BASE = 100°C
SENSITIVE DIR POWER
(Sns Dir Power)
P
BASE
= maximum value of 3
×
V
BASE
×
I
BASE
for the +IN and –IN inputs of the sources
configured for the sensitive power directional element(s).
SOURCE CURRENT
I
BASE
= maximum nominal primary RMS value of the +IN and –IN inputs
SOURCE ENERGY
(Positive and Negative Watthours,
Positive and Negative Varhours)
E
BASE
= 10000 MWh or MVAh, respectively
SOURCE POWER
P
BASE
= maximum value of V
BASE
×
I
BASE
for the +IN and –IN inputs
SOURCE THD & HARMONICS
BASE = 1%
SOURCE VOLTAGE
V
BASE
= maximum nominal primary RMS value of the +IN and –IN inputs
SYNCHROCHECK
(Max Delta Volts)
V
BASE
= maximum primary RMS value of all the sources related to the +IN and –IN inputs
GOOSE UINTEGER
INPUT 1
UINTEGER 1
DEFAULT:
1000
Range: 0 to 429496295 in steps of 1
MESSAGE
UINTEGER 1
DEFAULT
MODE: Default Value
Range: Default Value, Last Known
Содержание F60
Страница 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Страница 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Страница 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Страница 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Страница 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Страница 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Страница 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Страница 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Страница 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Страница 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Страница 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Страница 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...