5 SETTINGS
5.8 INPUTS/OUTPUTS
5
•
Setting
REMOTE IN 1 DEFAULT STATE
to “On” value defaults the input to logic 1.
•
Setting
REMOTE IN 1 DEFAULT STATE
to “Off” value defaults the input to logic 0.
•
Setting
REMOTE IN 1 DEFAULT STATE
to “Latest/On” freezes the input in case of lost communications. If the latest state is
not known, such as after relay power-up but before the first communication exchange, the input will default to logic 1.
When communication resumes, the input becomes fully operational.
•
Setting
REMOTE IN 1 DEFAULT STATE
to “Latest/Off” freezes the input in case of lost communications. If the latest state is
not known, such as after relay power-up but before the first communication exchange, the input will default to logic 0.
When communication resumes, the input becomes fully operational.
For additional information on GSSE/GOOOSE messaging, see the
Remote Devices
section in this chapter.
5.8.7 REMOTE DOUBLE-POINT STATUS INPUTS
PATH: SETTINGS
INPUTS/OUTPUTS
REMOTE DPS INPUTS
REMOTE DPS INPUT 1(5)
Remote double-point status inputs are extracted from GOOSE messages originating in the remote device. Each remote
double point status input must be programmed to replicate the logic state of a specific signal from a specific remote device
for local use. This functionality is accomplished with the five remote double-point status input settings.
•
REM DPS IN 1 ID
: This setting assigns descriptive text to the remote double-point status input.
•
REM DPS IN 1 DEV
: This setting selects a remote device ID to indicate the origin of a GOOSE message. The range is
selected from the remote device IDs specified in the
Remote Devices
section.
•
REM DPS IN 1 ITEM
: This setting specifies the required bits of the GOOSE message.
The configurable GOOSE dataset items must be changed to accept a double-point status item from a GOOSE dataset
(changes are made in the
SETTINGS
COMMUNICATION
IEC 61850 PROTOCOL
GSSE/GOOSE CONFIGURATION
RECEPTION
CONFIGURABLE GOOSE
CONFIGURABLE GOOSE 1(16)
CONFIG GSE 1 DATASET ITEMS
menus). Dataset
items configured to receive any of “GGIO3.ST.IndPos1.stV” to “GGIO3.ST.IndPos5.stV” will accept double-point status
information that will be decoded by the remote double-point status inputs configured to this dataset item.
The remote double point status is recovered from the received IEC 61850 dataset and is available as through the
RemDPS
Ip 1 BAD
,
RemDPS Ip 1 INTERM
,
RemDPS Ip 1 OFF
, and
RemDPS Ip 1 ON
FlexLogic operands. These operands can then be
used in breaker or disconnect control schemes.
5.8.8 REMOTE OUTPUTS
a) DNA BIT PAIRS
PATH: SETTINGS
INPUTS/OUTPUTS
REMOTE OUTPUTS DNA BIT PAIRS
REMOTE OUTPUTS DNA- 1(32) BIT PAIR
REMOTE DPS INPUT 1
REM DPS IN 1 ID:
RemDPS Ip 1
Range: up to 12 alphanumeric characters
MESSAGE
REM DPS IN 1 DEV:
Remote Device 1
Range: Remote Device 1 to Remote device 16
MESSAGE
REM DPS IN 1 ITEM:
None
Range: None, Dataset Item 1 to Dataset Item 32
MESSAGE
REM DPS IN 1
EVENTS: Disabled
Range: Enabled, Disabled
REMOTE OUTPUTS
DNA- 1 BIT PAIR
DNA- 1 OPERAND:
Off
Range: FlexLogic operand
MESSAGE
DNA- 1 EVENTS:
Disabled
Range: Disabled, Enabled
NOTE
Содержание F60
Страница 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Страница 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Страница 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Страница 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Страница 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Страница 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Страница 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Страница 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Страница 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Страница 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Страница 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Страница 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...