GE Multilin
F60 Feeder Protection System
5-255
5 SETTINGS
5.7 CONTROL ELEMENTS
5
5.7.11 DIGITAL COUNTERS
PATH: SETTINGS
CONTROL ELEMENTS
DIGITAL COUNTERS
COUNTER 1(8)
There are 8 identical digital counters, numbered from 1 to 8. A digital counter counts the number of state transitions from
Logic 0 to Logic 1. The counter is used to count operations such as the pickups of an element, the changes of state of an
external contact (e.g. breaker auxiliary switch), or pulses from a watt-hour meter.
•
COUNTER 1 UNITS:
Assigns a label to identify the unit of measure pertaining to the digital transitions to be counted.
The units label will appear in the corresponding actual values status.
•
COUNTER 1 PRESET:
Sets the count to a required preset value before counting operations begin, as in the case
where a substitute relay is to be installed in place of an in-service relay, or while the counter is running.
•
COUNTER 1 COMPARE:
Sets the value to which the accumulated count value is compared. Three FlexLogic output
operands are provided to indicate if the present value is ‘more than (HI)’, ‘equal to (EQL)’, or ‘less than (LO)’ the set
value.
•
COUNTER 1 UP:
Selects the FlexLogic operand for incrementing the counter. If an enabled UP input is received when
the accumulated value is at the limit of +2,147,483,647 counts, the counter will rollover to –2,147,483,648.
•
COUNTER 1 DOWN:
Selects the FlexLogic operand for decrementing the counter. If an enabled DOWN input is
received when the accumulated value is at the limit of –2,147,483,648 counts, the counter will rollover to
+2,147,483,647.
•
COUNTER 1 BLOCK:
Selects the FlexLogic operand for blocking the counting operation. All counter operands are
blocked.
COUNTER 1
COUNTER 1
FUNCTION: Disabled
Range: Disabled, Enabled
MESSAGE
COUNTER 1 NAME:
Counter 1
Range: 12 alphanumeric
characters
MESSAGE
COUNTER 1 UNITS:
Range: 6 alphanumeric characters
MESSAGE
COUNTER 1 PRESET:
0
Range: –2,147,483,648 to +2,147,483,647
MESSAGE
COUNTER 1 COMPARE:
0
Range: –2,147,483,648 to +2,147,483,647
MESSAGE
COUNTER 1 UP:
Off
Range: FlexLogic operand
MESSAGE
COUNTER 1 DOWN:
Off
Range: FlexLogic operand
MESSAGE
COUNTER 1 BLOCK:
Off
Range: FlexLogic operand
MESSAGE
CNT1 SET TO PRESET:
Off
Range: FlexLogic operand
MESSAGE
COUNTER 1 RESET:
Off
Range: FlexLogic operand
MESSAGE
COUNT1 FREEZE/RESET:
Off
Range: FlexLogic operand
MESSAGE
COUNT1 FREEZE/COUNT:
Off
Range: FlexLogic operand
Содержание F60
Страница 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Страница 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Страница 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Страница 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Страница 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Страница 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Страница 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Страница 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Страница 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Страница 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Страница 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Страница 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...