5-242
F60 Feeder Protection System
GE Multilin
5.7 CONTROL ELEMENTS
5 SETTINGS
5
5.7.8 SYNCHROCHECK (ANSI 25)
PATH: SETTINGS
CONTROL ELEMENTS
SYNCHROCHECK
SYNCHROCHECK 1(4)
There are four identical synchrocheck elements available, numbered 1 to 4.
The synchronism check function is intended for supervising the paralleling of two parts of a system which are to be joined
by the closure of a circuit breaker. The synchrocheck elements are typically used at locations where the two parts of the
system are interconnected through at least one other point in the system.
Synchrocheck verifies that the voltages (V1 and V2) on the two sides of the supervised circuit breaker are within set limits
of magnitude, angle and frequency differences. The time that the two voltages remain within the admissible angle differ-
ence is determined by the setting of the phase angle difference
ΔΦ
and the frequency difference
Δ
F (slip frequency). It can
be defined as the time it would take the voltage phasor V1 or V2 to traverse an angle equal to 2
×
ΔΦ
at a frequency equal
to the frequency difference
Δ
F. This time can be calculated by:
(EQ 5.31)
where:
ΔΦ
= phase angle difference in degrees;
Δ
F = frequency difference in Hz.
SYNCHROCHECK 1
SYNCHK1 FUNCTION:
Disabled
Range: Disabled, Enabled
MESSAGE
SYNCHK1 BLOCK:
Off
Range: FlexLogic operand
MESSAGE
SYNCHK1 V1 SOURCE:
SRC 1
Range: SRC 1, SRC 2, SRC 3, SRC 4
MESSAGE
SYNCHK1 V2 SOURCE:
SRC 2
Range: SRC 1, SRC 2, SRC 3, SRC 4
MESSAGE
SYNCHK1 MAX VOLT
DIFF: 10000 V
Range: 0 to 400000 V in steps of 1
MESSAGE
SYNCHK1 MAX ANGLE
DIFF: 30°
Range: 0 to 100° in steps of 1
MESSAGE
SYNCHK1 MAX FREQ
DIFF: 1.00 Hz
Range: 0.00 to 2.00 Hz in steps of 0.01
MESSAGE
SYNCHK1 MAX FREQ
HYSTERESIS: 0.06 Hz
Range: 0.00 to 0.10 Hz in steps of 0.01
MESSAGE
SYNCHK1 DEAD SOURCE
SELECT: LV1 and DV2
Range: None, LV1 and DV2, DV1 and LV2, DV1 or DV2,
DV1 Xor DV2, DV1 and DV2
MESSAGE
SYNCHK1 DEAD V1
MAX VOLT: 0.30 pu
Range: 0.00 to 1.25 pu in steps of 0.01
MESSAGE
SYNCHK1 DEAD V2
MAX VOLT: 0.30 pu
Range: 0.00 to 1.25 pu in steps of 0.01
MESSAGE
SYNCHK1 LIVE V1
MIN VOLT: 0.70 pu
Range: 0.00 to 1.25 pu in steps of 0.01
MESSAGE
SYNCHK1 LIVE V2
MIN VOLT: 0.70 pu
Range: 0.00 to 1.25 pu in steps of 0.01
MESSAGE
SYNCHK1 TARGET:
Self-reset
Range: Self-reset, Latched, Disabled
MESSAGE
SYNCHK1 EVENTS:
Disabled
Range: Disabled, Enabled
T
1
360
°
2
ΔΦ
×
------------------
Δ
F
×
--------------------------------
=
Содержание F60
Страница 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Страница 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Страница 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Страница 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Страница 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Страница 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Страница 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Страница 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Страница 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Страница 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Страница 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Страница 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...