GE Multilin
F60 Feeder Protection System
5-187
5 SETTINGS
5.6 GROUPED ELEMENTS
5
Figure 5–76: NEUTRAL DIRECTIONAL VOLTAGE-POLARIZED CHARACTERISTICS
•
NEUTRAL DIR OC1 POLARIZING:
This setting selects the polarizing mode for the directional unit.
– If “Voltage” polarizing is selected, the element uses the zero-sequence voltage angle for polarization. The user
can use either the zero-sequence voltage V_0 calculated from the phase voltages, or the zero-sequence voltage
supplied externally as the auxiliary voltage V_X, both from the
NEUTRAL DIR OC1 SOURCE
.
The calculated V_0 can be used as polarizing voltage only if the voltage transformers are connected in Wye. The
auxiliary voltage can be used as the polarizing voltage provided
SYSTEM SETUP
AC INPUTS
VOLTAGE BANK
AUXILIARY VT CONNECTION
is set to “Vn” and the auxiliary voltage is connected to a zero-sequence voltage
source (such as broken delta connected secondary of VTs).
The zero-sequence voltage must be greater than 0.02 pu to be validated for use as a polarizing signal. Addition-
ally, when offset impedance is applied and zero-sequence current is above 0.2 pu, compensated zero-sequence
voltage -V_0 + Z_offset x I_0 has to be above 0.02 pu in order to discriminate fault direction; otherwise when zero-
sequence current is less than 0.2 pu, -V_0 is then used as the polarizing signal. If the polarizing signal is invalid,
neither forward nor reverse indication is given.
–
If “Current” polarizing is selected, the element uses the ground current angle connected externally and configured
under
NEUTRAL OC1 SOURCE
for polarization. The ground CT must be connected between the ground and neutral
point of an adequate local source of ground current. The ground current must be greater than 0.05 pu to be vali-
dated as a polarizing signal. If the polarizing signal is not valid, neither forward nor reverse indication is given. In
addition, the zero-sequence current (I_0) must be greater than the
PRODUCT SETUP
DISPLAY PROPERTIES
CURRENT CUT-OFF LEVEL
setting value.
For a choice of current polarizing, it is recommended that the polarizing signal be analyzed to ensure that a known
direction is maintained irrespective of the fault location. For example, if using an autotransformer neutral current
as a polarizing source, it should be ensured that a reversal of the ground current does not occur for a high-side
fault. The low-side system impedance should be assumed minimal when checking for this condition. A similar sit-
uation arises for a wye/delta/wye transformer, where current in one transformer winding neutral may reverse when
faults on both sides of the transformer are considered.
–
If “Dual” polarizing is selected, the element performs both directional comparisons as described. A given direction
is confirmed if either voltage or current comparators indicate so. If a conflicting (simultaneous forward and
reverse) indication occurs, the forward direction overrides the reverse direction.
827805A1.CDR
VAG
(reference)
VBG
VCG
–3I_0 line
3I_0 line
ECA line
–ECA line
LA
LA
LA
LA
ECA
FWD LA
line
FWD Operating
Region
REV Operating
Region
FWD LA
line
REV LA
line
REV LA
line
–3V_0 line
3V_0 line
Содержание F60
Страница 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Страница 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Страница 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Страница 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Страница 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Страница 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Страница 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Страница 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Страница 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Страница 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Страница 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Страница 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...