5-152
F60 Feeder Protection System
GE Multilin
5.5 FLEXLOGIC
5 SETTINGS
5
ELEMENT:
VTFF (Voltage
transformer fuse
failure)
SRC1 VT FF OP
SRC1 VT FF DPO
SRC1 VT FF VOL LOSS
Source 1 VT fuse failure detector has operated
Source 1 VT fuse failure detector has dropped out
Source 1 has lost voltage signals (V2 below 10% and V1 below 5%
of nominal)
SRC1 VT NEU WIRE OPEN
Source 1 VT neutral wire open detected.When the VT is connected in Delta,
this function should not be enabled because there is no neutral wire for Delta
connected VT.
SRC2 VT FUSE FAIL to SRC4
Same set of operands as shown for SRC1 VT FUSE FAIL
ELEMENT:
Disconnect switch
SWITCH 1 OFF CMD
SWITCH 1 ON CMD
SWITCH 1 CLOSED
SWITCH 1 OPEN
SWITCH 1 DISCREP
SWITCH 1 TROUBLE
SWITCH 1
Φ
A CLSD
SWITCH 1
Φ
A OPEN
SWITCH 1
Φ
A BAD ST
SWITCH 1
Φ
A INTERM
SWITCH 1
Φ
B CLSD
SWITCH 1
Φ
B OPEN
SWITCH 1
Φ
B BAD ST
SWITCH 1
Φ
B INTERM
SWITCH 1
Φ
C CLSD
SWITCH 1
Φ
C OPEN
SWITCH 1
Φ
C BAD ST
SWITCH 1
Φ
C INTERM
SWITCH 1 BAD STATUS
Disconnect switch 1 open command initiated
Disconnect switch 1 close command initiated
Disconnect switch 1 is closed
Disconnect switch 1 is open
Disconnect switch 1 has discrepancy
Disconnect switch 1 trouble alarm
Disconnect switch 1 phase A is closed
Disconnect switch 1 phase A is open
Disconnect switch 1 phase A bad status is detected (discrepancy between
the 89/a and 89/b contacts)
Disconnect switch 1 phase A intermediate status is detected (transition from
one position to another)
Disconnect switch 1 phase B is closed
Disconnect switch 1 phase B is open
Disconnect switch 1 phase B bad status is detected (discrepancy between
the 89/a and 89/b contacts)
Disconnect switch 1 phase B intermediate status is detected (transition from
one position to another)
Disconnect switch 1 phase C is closed
Disconnect switch 1 phase C is open
Disconnect switch 1 phase C bad status is detected (discrepancy between
the 89/a and 89/b contacts)
Disconnect switch 1 phase C intermediate status is detected (transition from
one position to another)
Disconnect switch 1 bad status is detected on any pole
SWITCH 2 to 16
Same set of operands as shown for SWITCH 1
ELEMENT:
Synchrocheck
SYNC1 DEAD S OP
SYNC1 DEAD S DPO
SYNC1 SYNC OP
SYNC1 SYNC DPO
SYNC1 CLS OP
SYNC1 CLS DPO
SYNC1 V1 ABOVE MIN
SYNC1 V1 BELOW MAX
SYNC1 V2 ABOVE MIN
SYNC1 V2 BELOW MAX
Synchrocheck 1 dead source has operated
Synchrocheck 1 dead source has dropped out
Synchrocheck 1 in synchronization has operated
Synchrocheck 1 in synchronization has dropped out
Synchrocheck 1 close has operated
Synchrocheck 1 close has dropped out
Synchrocheck 1 V1 is above the minimum live voltage
Synchrocheck 1 V1 is below the maximum dead voltage
Synchrocheck 1 V2 is above the minimum live voltage
Synchrocheck 1 V2 is below the maximum dead voltage
SYNC 2 to 4
Same set of operands as shown for SYNC 1
ELEMENT:
Teleprotection
channel tests
TELEPRO CH1 FAIL
TELEPRO CH2 FAIL
TELEPRO CH1 ID FAIL
TELEPRO CH2 ID FAIL
TELEPRO CH1 CRC FAIL
TELEPRO CH2 CRC FAIL
TELEPRO CH1 PKT LOST
TELEPRO CH2 PKT LOST
Channel 1 failed
Channel 2 failed
The ID check for a peer relay on channel 1 has failed
The ID check for a peer relay on channel 2 has failed
CRC detected packet corruption on channel 1
CRC detected packet corruption on channel 2
CRC detected lost packet on channel 1
CRC detected lost packet on channel 2
ELEMENT:
Teleprotection
inputs/outputs
TELEPRO INPUT 1-1 On
↓
TELEPRO INPUT 1-16 On
TELEPRO INPUT 2-1 On
↓
TELEPRO INPUT 2-16 On
Flag is set, Logic =1
↓
Flag is set, Logic =1
Flag is set, Logic =1
↓
Flag is set, Logic =1
ELEMENT:
Thermal overload
protection
THERMAL PROT 1 PKP
THERMAL PROT 1 OP
Thermal overload protection 1 picked up
Thermal overload protection 1 operated
THERMAL PROT 2
Same set of operands as shown for THERMAL PROT 1
ELEMENT
Trip bus
TRIP BUS 1 PKP
TRIP BUS 1 OP
Asserted when the trip bus 1 element picks up
Asserted when the trip bus 1 element operates
TRIP BUS 2 to 6
Same set of operands as shown for TRIP BUS 1
Table 5–18: F60 FLEXLOGIC OPERANDS (Sheet 6 of 8)
OPERAND TYPE
OPERAND SYNTAX
OPERAND DESCRIPTION
Содержание F60
Страница 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Страница 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Страница 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Страница 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Страница 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Страница 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Страница 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Страница 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Страница 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Страница 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Страница 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Страница 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...