GE Multilin
F60 Feeder Protection System
5-99
5 SETTINGS
5.2 PRODUCT SETUP
5
5.2.19 INSTALLATION
PATH: SETTINGS
PRODUCT SETUP
INSTALLATION
To safeguard against the installation of a relay without any entered settings, the unit will not allow signaling of any output
relay until
RELAY SETTINGS
is set to "Programmed". This setting is defaulted to "Not Programmed" when at the factory. The
UNIT NOT PROGRAMMED
self-test error message is displayed until the relay is put into the "Programmed" state.
The
RELAY NAME
setting allows the user to uniquely identify a relay. This name will appear on generated reports.
INSTALLATION
RELAY SETTINGS:
Not Programmed
Range: Not Programmed, Programmed
MESSAGE
RELAY NAME:
Relay-1
Range: up to 20 alphanumeric characters
Содержание F60
Страница 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Страница 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Страница 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Страница 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Страница 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Страница 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Страница 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Страница 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Страница 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Страница 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Страница 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Страница 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...