Connect the ground lug to the ground terminal
You must provide these components to properly ground the chassis:
•
Crimping tool
•
Single ring ground terminal lug
•
One 12 AWG copper wire long enough to reach from the chassis to the common bonding network (CBN)
After the unit is installed in the rack and before you provide power to the system, you need to connect the
grounding hardware.
1.
Remove the M5 Keps nuts from the ground lug on the back of the chassis.
2.
Attach a ground ring terminal to the 12 AWG copper ground wire.
3.
Install the ground ring terminal onto the chassis ground terminal.
4.
Secure the ground ring terminal with the M5 Keps nuts.
Use 18 to 24 inch-pounds (2.0 to 2.7 Newton-meters) of torque on these Keps nuts.
5.
Connect the ground wire to a common bonding network (CBN).
Connect the cables and other hardware
After you have installed the unit into the rack, connect the cables and other hardware.
Important: In the event that network access is impaired or not yet configured, the serial console might be
the only way to access the unit. You should perform all installations and upgrades using the serial console,
as these procedures require reboots, in which network connectivity is lost temporarily.
1.
If you are using the default network configured on the management interface, connect an Ethernet cable
to the management port.
Note: For EMI compliance, shielded cables are required for the management port, and the shield must
be grounded at both ends.
2.
Connect the console port to a serial console server. Depending on which F5
®
system you have and the
console network to which you are attaching, you can use either the supplied RJ45 to DB9 console port
cable or the RJ45F to RJ45M rolled serial adapter to connect the system to a serial console.
•
Connect the RJ45 to DB9 console port cable to the console port on the system.
Note: The default baud rate and serial port configuration is 19200/8-N-1.
•
Connect the RJ45F to RJ45M rolled serial adapter to the console port if you are connecting the
system to a serial console server with a standard CAT5 cable, and then connect the CAT5 cable to
the adapter. The adapter provides the appropriate pinout connection to your equipment. For information
about cable and connector pinout specifications, see
F5 Platforms: Accessories
at
techdocs.f5.com/kb/en-us/products/big-ip_ltm/manuals/product/f5-plat-accessories.html
.
14
Platform Installation
Содержание i5000 Series
Страница 1: ...Setting Up the i5000 i7000 i10000 i11000 Series Platform MAN 0620 08...
Страница 2: ......
Страница 4: ...4 Table of Contents...
Страница 10: ......
Страница 20: ......
Страница 26: ......