GE Multilin
F35 Multiple Feeder Protection System
1-19
1 GETTING STARTED
1.5 USING THE RELAY
1
1.5.7 COMMISSIONING
The F35 requires a minimum amount of maintenance when it is commissioned into service. Since the F35 is a microproces-
sor-based relay, its characteristics do not change over time. As such, no further functional tests are required.
Furthermore, the F35 performs a number of continual self-tests and takes the necessary action in case of any major errors
(see the
Relay Self-tests
section in chapter 7 for details). However, it is recommended that F35 maintenance be scheduled
with other system maintenance. This maintenance may involve the in-service, out-of-service, or unscheduled maintenance.
In-service maintenance:
1.
Visual verification of the analog values integrity such as voltage and current (in comparison to other devices on the cor-
responding system).
2.
Visual verification of active alarms, relay display messages, and LED indications.
3.
LED test.
4.
Visual inspection for any damage, corrosion, dust, or loose wires.
5.
Event recorder file download with further events analysis.
Out-of-service maintenance:
1.
Check wiring connections for firmness.
2.
Analog values (currents, voltages, RTDs, analog inputs) injection test and metering accuracy verification. Calibrated
test equipment is required.
3.
Protection elements setting verification (analog values injection or visual verification of setting file entries against relay
settings schedule).
4.
Contact inputs and outputs verification. This test can be conducted by direct change of state forcing or as part of the
system functional testing.
5.
Visual inspection for any damage, corrosion, or dust.
6.
Event recorder file download with further events analysis.
7.
LED Test and pushbutton continuity check.
Unscheduled maintenance such as during a disturbance causing system interruption:
1.
View the event recorder and oscillography or fault report for correct operation of inputs, outputs, and elements.
If it is concluded that the relay or one of its modules is of concern, contact GE Multilin for prompt service.
Summary of Contents for F35
Page 2: ......
Page 4: ......
Page 296: ...5 174 F35 Multiple Feeder Protection System GE Multilin 5 9 TESTING 5 SETTINGS 5 ...
Page 328: ...7 8 F35 Multiple Feeder Protection System GE Multilin 7 2 TARGETS 7 COMMANDS AND TARGETS 7 ...
Page 350: ...A 16 F35 Multiple Feeder Protection System GE Multilin A 1 PARAMETER LIST APPENDIXA A ...
Page 422: ...B 72 F35 Multiple Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIXB B ...
Page 472: ...E 12 F35 Multiple Feeder Protection System GE Multilin E 2 DNP POINT LISTS APPENDIXE E ...