F35 Multiple Feeder Protection System
GE Multilin
5.6 CONTROL ELEMENTS
5 SETTINGS
5
Figure 5–71: ARCING CURRENT MEASUREMENT
Figure 5–72: BREAKER ARCING CURRENT SCHEME LOGIC
Initiate
Breaker
Contacts
Part
Arc
Extinguished
100 ms
Programmable
Start Delay
Start
Integration
Stop
Integration
Total Area =
Breaker
Arcing
Current
(kA·cycle)
SETTING
SETTING
SETTINGS
SETTING
COMMAND
ACTUAL VALUE
FLEXLOGIC OPERANDS
SETTING
BREAKER 1 ARCING
AMP FUNCTION:
BREAKER 1 ARCING
AMP BLOCK:
BREAKER 1 ARCING
AMP INIT-A:
BREAKER 1 ARCING
AMP INIT-B:
BREAKER 1 ARCING
AMP INIT-C:
BREAKER 1 ARCING
AMP LIMIT:
CLEAR BREAKER 1
ARCING AMPS:
BKR 1 ARCING AMP A
BKR 1 OPERATING TIME A
BKR 1 OPERATING TIME B
BKR 1 OPERATING TIME C
BKR 1 OPERATING TIME
BKR 1 ARCING AMP B
BKR 1 ARCING AMP C
BKR1 ARC OP
BKR1 ARC DPO
BREAKER 1 ARCING
AMP SOURCE:
I
A
I
B
I
C
Off=0
Off=0
Off=0
Off=0
NO=0
YES=1
Enabled=1
Disabled=0
AND
AND
AND
AND
AND
OR
OR
827071A3.CDR
KA Cycle Limit
2
*
SETTING
BREAKER 1 ARCING
AMP DELAY:
100 ms
0
0
Set All To Zero
Add to
Accumulator
Integrate
Integrate
Integrate
Select
Highest
Value
RUN
RUN
RUN
I
B -Cycle
I
A -Cycle
I
C -Cycle
2
2
2
Summary of Contents for F35
Page 2: ......
Page 4: ......
Page 296: ...5 174 F35 Multiple Feeder Protection System GE Multilin 5 9 TESTING 5 SETTINGS 5 ...
Page 328: ...7 8 F35 Multiple Feeder Protection System GE Multilin 7 2 TARGETS 7 COMMANDS AND TARGETS 7 ...
Page 350: ...A 16 F35 Multiple Feeder Protection System GE Multilin A 1 PARAMETER LIST APPENDIXA A ...
Page 422: ...B 72 F35 Multiple Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIXB B ...
Page 472: ...E 12 F35 Multiple Feeder Protection System GE Multilin E 2 DNP POINT LISTS APPENDIXE E ...