background image

GE Multilin

F35 Multiple Feeder Protection System

5-131

5 SETTINGS

5.6 CONTROL ELEMENTS

5

The ‘Incomplete Sequence’ timer times out.

The recloser will be latched in the Lockout state until a ‘reset from lockout’ signal is asserted, either from a manual close of
the breaker or from a manual reset command (local or remote). The reset from lockout can be accomplished by operator
command, by manually closing the breaker, or whenever the breaker has been closed and stays closed for a preset time.

After the dead time elapses, the scheme issues the close signal. The close signal is latched until the breaker closes or the
scheme goes to Lockout.

A reset timer output resets the recloser following a successful reclosure sequence. The reset time is based on the breaker
‘reclaim time’ which is the minimum time required between successive reclose sequences.

SETTINGS:

AR1 INITIATE:

 Selects the FlexLogic™ operand that initiates the scheme, typically the trip signal from protection.

AR1 BLOCK:

 Selects the FlexLogic™ operand that blocks the autoreclosure initiate (it could be from the breaker fail-

ure, bus differential protection, etc.).

AR1 MAX NUMBER OF SHOTS:

 Specifies the number of reclosures that can be attempted before reclosure goes to

“Lockout” because the fault is permanent.

AR1 REDUCE MAX TO 1(3):

 Selects the FlexLogic™ operand that changes the maximum number of shots from the

initial setting to 1, 2, or 3, respectively.

AR1 MANUAL CLOSE:

 Selects the logic input set when the breaker is manually closed.

AR1 MNL RST FRM LO:

 Selects the FlexLogic™ operand that resets the autoreclosure from Lockout condition. Typi-

cally this is a manual reset from lockout, local or remote.

AR1 RESET LOCKOUT IF BREAKER CLOSED: 

This setting allows the autoreclose scheme to reset from Lockout if

the breaker has been manually closed and stays closed for a preset time. In order for this setting to be effective, the
next setting (

AR1 RESET LOCKOUT ON MANUAL CLOSE

) should be disabled.

AR1 RESET LOCKOUT ON MANUAL CLOSE: 

This setting allows the autoreclose scheme to reset from Lockout

when the breaker is manually closed regardless if the breaker remains closed or not. This setting overrides the previ-
ous setting (

AR1 RESET LOCKOUT IF BREAKER CLOSED

).

AR1 BLK TIME UPON MNL CLS:

 The autoreclose scheme can be disabled for a programmable time delay after the

associated circuit breaker is manually closed. This prevents reclosing onto a fault after a manual close. This delay
must be longer than the slowest expected trip from any protection not blocked after manual closing. If no overcurrent
trips occur after a manual close and this time expires, the autoreclose scheme is enabled. 

AR1 DEAD TIME 1 to AR1 DEAD TIME 4: 

These are the intentional delays before first, second, third, and fourth

breaker automatic reclosures (1st, 2nd, and 3rd shots), respectively, and should be set longer than the estimated
deionizing time following a three pole trip.

AR1 ADD DELAY 1:

 This setting selects the FlexLogic™ operand that introduces an additional delay (Delay 1) to the

initial set Dead Time (1 to 4). When this setting is “Off”, Delay 1 is by-passed.

AR1 DELAY 1:

 This setting establishes the extent of the additional dead time Delay 1.

AR1 ADD DELAY 2:

 This setting selects the FlexLogic™ operand that introduces an additional delay (Delay 2) to the

initial set Dead Time (1 to 4). When this setting is “Off”, Delay 2 is by-passed.

AR1 DELAY 2:

 This setting establishes the extent of the additional dead time Delay 2.

AR1 RESET LOCKOUT DELAY:

 This setting establishes how long the breaker should stay closed after a manual

close command, in order for the autorecloser to reset from Lockout.

AR1 RESET TIME

: A reset timer output resets the recloser following a successful reclosure sequence. The setting is

based on the breaker ‘reclaim time’ which is the minimum time required between successive reclose sequences.

AR1 INCOMPLETE SEQ TIME

: This timer defines the maximum time interval allowed for a single reclose shot. It is

started whenever a reclosure is initiated and is active when the scheme is in the ‘reclose-in-progress’ state. If all condi-
tions allowing a breaker closure are not satisfied when this time expires, the scheme goes to “Lockout”.

This timer must be set to a delay less than the reset timer

.

NOTE

Summary of Contents for F35

Page 1: ... UR Series Instruction Manual GE Multilin 215 Anderson Avenue Markham Ontario Canada L6E 1B3 Tel 905 294 6222 Fax 905 201 2098 Internet http www GEmultilin com Title Page IISO9001 2000 G E M ULTILI N R E GISTERE D GE Multilin s Quality Management System is registered to ISO9001 2000 QMI 005094 UL A3775 1601 0106 S5 LISTED 52TL IND CONT EQ E83849 ...

Page 2: ......

Page 3: ...colors are the same In the event that there is a mismatch between the CPU and CT VT module the relay will not function and a DSP ERROR or HARDWARE MISMATCH error will be displayed All other input output modules are compatible with the new hardware With respect to the firmware firmware versions 4 0x and higher are only compatible with the new CPU and CT VT mod ules Previous versions of the firmware...

Page 4: ......

Page 5: ...1 17 1 5 4 RELAY ACTIVATION 1 17 1 5 5 RELAY PASSWORDS 1 18 1 5 6 FLEXLOGIC CUSTOMIZATION 1 18 1 5 7 COMMISSIONING 1 19 2 PRODUCT DESCRIPTION 2 1 INTRODUCTION 2 1 1 OVERVIEW 2 1 2 1 2 ORDERING 2 2 2 1 3 REPLACEMENT MODULES 2 4 2 2 SPECIFICATIONS 2 2 1 PROTECTION ELEMENTS 2 7 2 2 2 USER PROGRAMMABLE ELEMENTS 2 8 2 2 3 MONITORING 2 9 2 2 4 METERING 2 9 2 2 5 INPUTS 2 10 2 2 6 POWER SUPPLY 2 11 2 2 7...

Page 6: ...1 1 INTRODUCTION 4 1 4 1 2 CREATING A SITE LIST 4 1 4 1 3 ENERVISTA UR SETUP OVERVIEW 4 1 4 1 4 ENERVISTA UR SETUP MAIN WINDOW 4 3 4 2 EXTENDED ENERVISTA UR SETUP FEATURES 4 2 1 SETTINGS TEMPLATES 4 4 4 2 2 SECURING AND LOCKING FLEXLOGIC EQUATIONS 4 8 4 2 3 SETTINGS FILE TRACEABILITY 4 10 4 3 FACEPLATE INTERFACE 4 3 1 FACEPLATE 4 13 4 3 2 LED INDICATORS 4 14 4 3 3 CUSTOM LABELING OF LEDS 4 17 4 3 ...

Page 7: ...CURRENT 5 103 5 5 4 NEUTRAL CURRENT 5 111 5 5 5 GROUND CURRENT 5 113 5 5 6 VOLTAGE ELEMENTS 5 115 5 6 CONTROL ELEMENTS 5 6 1 OVERVIEW 5 121 5 6 2 SETTING GROUPS 5 121 5 6 3 SELECTOR SWITCH 5 122 5 6 4 UNDERFREQUENCY 5 128 5 6 5 AUTORECLOSE 5 129 5 6 6 DIGITAL ELEMENTS 5 135 5 6 7 DIGITAL COUNTERS 5 138 5 6 8 8 BIT SWITCHES 5 140 5 6 9 MONITORING ELEMENTS 5 142 5 6 10 TRIP BUS 5 147 5 7 INPUTS OUTP...

Page 8: ...ET SWITCH 6 9 6 3 METERING 6 3 1 METERING CONVENTIONS 6 10 6 3 2 SOURCES 6 13 6 3 3 TRACKING FREQUENCY 6 18 6 3 4 FLEXELEMENTS 6 19 6 3 5 IEC 61580 GOOSE ANALOG VALUES 6 19 6 3 6 TRANSDUCER INPUTS OUTPUTS 6 20 6 4 RECORDS 6 4 1 FAULT REPORTS 6 21 6 4 2 EVENT RECORDS 6 21 6 4 3 OSCILLOGRAPHY 6 22 6 4 4 DATA LOGGER 6 22 6 4 5 BREAKER MAINTENANCE 6 23 6 5 PRODUCT INFORMATION 6 5 1 MODEL INFORMATION 6...

Page 9: ... C 2 1 OVERVIEW C 2 C 2 2 GGIO1 DIGITAL STATUS VALUES C 2 C 2 3 GGIO2 DIGITAL CONTROL VALUES C 2 C 2 4 GGIO3 DIGITAL STATUS AND ANALOG VALUES FROM RECEIVED GOOSE DATAC 2 C 2 5 GGIO4 GENERIC ANALOG MEASURED VALUES C 2 C 2 6 MMXU ANALOG MEASURED VALUES C 3 C 2 7 PROTECTION AND OTHER LOGICAL NODES C 3 C 3 SERVER FEATURES AND CONFIGURATION C 3 1 BUFFERED UNBUFFERED REPORTING C 5 C 3 2 FILE TRANSFER C ...

Page 10: ...0 5 104 COMMS D 1 IEC 60870 5 104 PROTOCOL D 1 1 INTEROPERABILITY DOCUMENT D 1 D 1 2 POINTS LIST D 9 E DNP COMMUNICATIONS E 1 DEVICE PROFILE DOCUMENT E 1 1 DNP V3 00 DEVICE PROFILE E 1 E 1 2 IMPLEMENTATION TABLE E 4 E 2 DNP POINT LISTS E 2 1 BINARY INPUT POINTS E 8 E 2 2 BINARY AND CONTROL RELAY OUTPUT E 9 E 2 3 COUNTERS E 10 E 2 4 ANALOG INPUTS E 11 F MISCELLANEOUS F 1 CHANGE NOTES F 1 1 REVISION...

Page 11: ...nstruction manual updates and the latest software updates please visit the GE Multilin web site at http www GEmultilin com If there is any noticeable physical damage or any of the contents listed are missing please contact GE Multilin immediately GE MULTILIN CONTACT INFORMATION AND CALL CENTER FOR PRODUCT SUPPORT GE Multilin 215 Anderson Avenue Markham Ontario Canada L6E 1B3 TELEPHONE 905 294 6222...

Page 12: ... of cabling and auxiliary equipment installed in stations can be even further reduced to 20 to 70 of the levels common in 1990 to achieve large cost reductions This requires placing even more functions within the IEDs Users of power equipment are also interested in reducing cost by improving power quality and personnel productivity and as always in increasing system reliability and efficiency Thes...

Page 13: ...e the device Virtual outputs can also serve as virtual inputs to FlexLogic equations The analog inputs and outputs are signals that are associated with transducers such as Resistance Temperature Detec tors RTDs The CT and VT inputs refer to analog current transformer and voltage transformer signals used to monitor AC power lines The UR series relays support 1 A and 5 A CTs The remote inputs and ou...

Page 14: ...or metering input output control hmi communications or any functional entity in the system Employing OOD OOP in the software architecture of the F35 achieves the same features as the hardware architecture modularity scalability and flexibility The application software for any UR series device for example feeder protection transformer protection distance protection is constructed by combining objec...

Page 15: ...ble of displaying 800 x 600 or higher in high color mode 16 bit color RS232 and or Ethernet port for communications to the relay The following qualified modems have been tested to be compliant with the F35 and the EnerVista UR Setup software US Robotics external 56K FaxModem 5686 US Robotics external Sportster 56K X2 PCTEL 2304WT V 92 MDC internal modem 1 3 2 INSTALLATION After ensuring the minimu...

Page 16: ...allation The files will be installed in the directory indicated and the installation program will automatically create icons and add EnerVista UR Setup to the Windows start menu 9 Click Finish to end the installation The UR series device will be added to the list of installed IEDs in the EnerVista Launchpad window as shown below 1 3 3 CONFIGURING THE F35 FOR SOFTWARE ACCESS a OVERVIEW The user can...

Page 17: ...ll be required Refer to the F485 instruction manual for additional details 1 Verify that the latest version of the EnerVista UR Setup software is installed available from the GE EnerVista CD or online from http www GEmultilin com See the Software Installation section for installation details 2 Select the UR device from the EnerVista Launchpad to start EnerVista UR Setup 3 Click the Device Setup bu...

Page 18: ...will be necessary to define a Site then add the relay as a Device at that site 1 Verify that the latest version of the EnerVista UR Setup software is installed available from the GE EnerVista CD or online from http www GEmultilin com See the Software Installation section for installation details 2 Select the UR device from the EnerVista Launchpad to start EnerVista UR Setup 3 Click the Device Setu...

Page 19: ...he latest version of the EnerVista UR Setup software is installed available from the GE EnerVista CD or online from http www GEmultilin com See the Software Installation section for installation details 2 Select the UR device from the EnerVista Launchpad to start EnerVista UR Setup 3 Click the Quick Connect button to open the Quick Connect dialog box 4 Select the Serial interface and the correct C...

Page 20: ...p computer an IP address compatible with the relay s IP address 1 From the Windows desktop right click the My Network Places icon and select Properties to open the network con nections window 2 Right click the Local Area Connection icon and select Properties 842799A1 CDR END 1 END 2 Pin Wire color Diagram Pin Wire color Diagram 1 White orange 1 White green 2 Orange 2 Green 3 White green 3 White or...

Page 21: ... 1 Open a Windows console window by selecting Start Run from the Windows Start menu and typing cmd 2 Type the following command C WINNT ping 1 1 1 1 3 If the connection is successful the system will return four replies as follows Pinging 1 1 1 1 with 32 bytes of data Reply from 1 1 1 1 bytes 32 time 10ms TTL 255 Reply from 1 1 1 1 bytes 32 time 10ms TTL 255 Reply from 1 1 1 1 bytes 32 time 10ms TT...

Page 22: ...es of data Verify the physical connection between the F35 and the laptop computer and double check the programmed IP address in the PRODUCT SETUP ÖØ COMMUNICATIONS ÖØ NETWORK Ö IP ADDRESS setting then repeat step 2 in the above procedure If the following sequence of messages appears when entering the C WINNT ping 1 1 1 1 command Pinging 1 1 1 1 with 32 bytes of data Destination host unreachable De...

Page 23: ...ct the UR device from the EnerVista Launchpad to start EnerVista UR Setup 4 Click the Quick Connect button to open the Quick Connect dialog box 5 Select the Ethernet interface and enter the IP address assigned to the F35 then click Connect 6 The EnerVista UR Setup software will create a site named Quick Connect with a corresponding device also named Quick Connect and display them on the upper left...

Page 24: ...e EnerVista UR Setup software can automatically discover and communicate to all UR series IEDs located on an Ether net network Using the Quick Connect feature a single click of the mouse will trigger the software to automatically detect any UR series relays located on the network The EnerVista UR Setup software will then proceed to configure all settings and order code options in the Device Setup ...

Page 25: ...edited printed or changed according to user specifications Refer to chapter 4 in this manual and the EnerVista UR Setup Help File for more information about the using the EnerVista UR Setup software interface QUICK ACTION HOT LINKS The EnerVista UR Setup software has several new quick action buttons that provide users with instant access to several functions that are often performed when using F35...

Page 26: ...rt the GE Multilin RS232 RS485 converter box is required This device catalog number F485 connects to the computer using a straight through serial cable A shielded twisted pair 20 22 or 24 AWG connects the F485 converter to the F35 rear communications port The converter termi nals GND are connected to the F35 communication module COM terminals Refer to the CPU communica tions ports section in chapt...

Page 27: ...led 1 5 3 MENU HIERARCHY The setting and actual value messages are arranged hierarchically The header display pages are indicated by double scroll bar characters while sub header pages are indicated by single scroll bar characters The header display pages represent the highest level of the hierarchy and the sub header display pages fall below this level The MESSAGE UP and DOWN keys move within a g...

Page 28: ...pecific personnel There are two user password security access levels COMMAND and SETTING 1 COMMAND The COMMAND access level restricts the user from making any settings changes but allows the user to perform the fol lowing operations change state of virtual inputs clear event records clear oscillography records operate user programmable pushbuttons 2 SETTING The SETTING access level allows the user...

Page 29: ...ges and LED indications 3 LED test 4 Visual inspection for any damage corrosion dust or loose wires 5 Event recorder file download with further events analysis Out of service maintenance 1 Check wiring connections for firmness 2 Analog values currents voltages RTDs analog inputs injection test and metering accuracy verification Calibrated test equipment is required 3 Protection elements setting ve...

Page 30: ...1 20 F35 Multiple Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...

Page 31: ...eport generation in the event of a system fault A faceplate RS232 port may be used to connect to a PC for the programming of settings and the monitoring of actual val ues A variety of communications modules are available Two rear RS485 ports allow independent access by operating and engineering staff All serial ports use the Modbus RTU protocol The RS485 ports may be connected to system computers ...

Page 32: ...OTHER DEVICE FUNCTIONS FUNCTION FUNCTION FUNCTION Breaker arcing current I2 t Ethernet Global Data protocol optional Oscillography Breaker control Event recorder Setting groups 6 Contact inputs up to 96 Fault detector and fault report Teleprotection inputs and outputs Contact outputs up to 64 FlexElements 16 Time synchronization over SNTP Control pushbuttons FlexLogic equations Transducer inputs a...

Page 33: ...inputs 6B 6B 6B 6B 6B 2 Form A voltage with optional current and 4 Form C outputs 4 digital inputs 6C 6C 6C 6C 6C 8 Form C outputs 6D 6D 6D 6D 6D 16 digital inputs 6E 6E 6E 6E 6E 4 Form C outputs 8 digital inputs 6F 6F 6F 6F 6F 8 Fast Form C outputs 6G 6G 6G 6G 6G 4 Form A voltage with optional current outputs 8 digital inputs 6H 6H 6H 6H 6H 6 Form A voltage with optional current outputs 4 digital...

Page 34: ...orm A voltage with optional current and 2 Form C outputs 8 digital inputs 6B 6B 6B 2 Form A voltage with optional current and 4 Form C outputs 4 digital inputs 6C 6C 6C 8 Form C outputs 6D 6D 6D 16 digital inputs 6E 6E 6E 4 Form C outputs 8 digital inputs 6F 6F 6F 8 Fast Form C outputs 6G 6G 6G 4 Form A voltage with optional current outputs 8 digital inputs 6H 6H 6H 6 Form A voltage with optional ...

Page 35: ...Form C outputs 8 digital inputs 6B 2 Form A voltage with optional current and 4 Form C outputs 4 digital inputs 6C 8 Form C outputs 6D 16 digital inputs 6E 4 Form C outputs 8 digital inputs 6F 8 Fast Form C outputs 6G 4 Form A voltage with optional current outputs 8 digital inputs 6H 6 Form A voltage with optional current outputs 4 digital inputs 6K 4 Form C and 4 Fast Form C outputs 6L 2 Form A c...

Page 36: ...m A voltage with optional current outputs 4 digital inputs 6K 4 Form C and 4 Fast Form C outputs 6L 2 Form A current with optional voltage and 2 Form C outputs 8 digital inputs 6M 2 Form A current with optional voltage and 4 Form C outputs 4 digital inputs 6N 4 Form A current with optional voltage outputs 8 digital inputs 6P 6 Form A current with optional voltage outputs 4 digital inputs 6R 2 Form...

Page 37: ...to 103 of pickup Level accuracy 0 5 of reading from 10 to 208 V Curve shapes GE IAV Inverse Definite Time 0 1s base curve Curve multiplier Time dial 0 00 to 600 00 in steps of 0 01 Timing accuracy Operate at 0 90 pickup 3 5 of operate time or 4 ms which ever is greater AUXILIARY UNDERVOLTAGE Pickup level 0 000 to 3 000 pu in steps of 0 001 Dropout level 102 to 103 of pickup Level accuracy 0 5 of r...

Page 38: ...ferential mode Operating signal mode signed or absolute value Operating mode level delta Comparator direction over under Pickup Level 90 000 to 90 000 pu in steps of 0 001 Hysteresis 0 1 to 50 0 in steps of 0 1 Delta dt 20 ms to 60 days Pickup dropout delay 0 000 to 65 535 s in steps of 0 001 NON VOLATILE LATCHES Type set dominant or reset dominant Number 16 individually programmed Output stored i...

Page 39: ...teps of 1 Trigger any FlexLogic operand Mode continuous or triggered Storage capacity NN is dependent on memory 1 second rate 01 channel for NN days 16 channels for NN days 60 minute rate 01 channel for NN days 16 channels for NN days FAULT LOCATOR Number of independent fault locators 1 per CT bank to a maxi mum of 5 Method single ended Voltage source wye connected VTs delta connected VTs and neut...

Page 40: ...ent to external CT AC VOLTAGE VT rated secondary 50 0 to 240 0 V VT ratio 1 00 to 24000 00 Nominal frequency 20 to 65 Hz Relay burden 0 25 VA at 120 V Conversion range 1 to 275 V Voltage withstand continuous at 260 V to neutral 1 min hr at 420 V to neutral CONTACT INPUTS Dry contacts 1000 Ω maximum Wet contacts 300 V DC maximum Selectable thresholds 17 V 33 V 84 V 166 V Tolerance 10 Contacts per c...

Page 41: ...ge 88 265 V at 25 to 100 Hz Voltage loss hold up 200 ms duration at nominal ALL RANGES Volt withstand 2 Highest Nominal Voltage for 10 ms Power consumption typical 15 to 20 W VA maximum 50 W VA contact factory for exact order code con sumption INTERNAL FUSE RATINGS Low range power supply 8 A 250 V High range power supply 4 A 250 V INTERRUPTING CAPACITY AC 100 000 A RMS symmetrical DC 10 000 A 2 2 ...

Page 42: ...solation 1 5 kV Driving signal any FlexAnalog quantity Upper and lower limit for the driving signal 90 to 90 pu in steps of 0 001 ETHERNET SWITCH HIGH VOLTAGE TYPE 2S Nominal DC voltage 110 to 240 V DC Minimum DC voltage 88 V DC Maximum DC voltage 300 V DC Input Current 0 9 A DC maximum Nominal AC voltage 100 to 240 V AC 0 26 to 0 16 A 26 to 39 VA at 50 60 Hz Minimum AC voltage 85 V AC 0 31 A 22 V...

Page 43: ...optical power budget between two type 2T or 2S modules using a single fiber cable is To calculate the maximum fiber length divide the worst case opti cal power budget by the cable attenuation per unit distance speci fied in the manufacturer data sheets For example typical attenuation for 62 5 125 μm glass fiber optic cable is approxi mately 2 8 dB per km In our example this would result in the fol...

Page 44: ...on degree II Overvoltage category II Ingress protection IP40 front IP20 back INTERFACE TYPE TYPICAL DISTANCE RS422 1200 m G 703 100 m EMITTER FIBER TYPE TRANSMIT POWER RECEIVED SENSITIVITY POWER BUDGET 820 nm LED Multimode 20 dBm 30 dBm 10 dB 1300 nm LED Multimode 21 dBm 30 dBm 9 dB 1300 nm ELED Singlemode 23 dBm 32 dBm 9 dB 1300 nm Laser Singlemode 1 dBm 30 dBm 29 dB 1550 nm Laser Singlemode 5 dB...

Page 45: ...pple 200 ms interrupts Radiated and conducted emissions CISPR11 CISPR22 IEC60255 25 Class A Sinusoidal vibration IEC60255 21 1 Class 1 Shock and bump IEC60255 21 2 Class 1 Seismic IEC60255 21 3 Class 1 Power magnetic immunity IEC61000 4 8 Level 5 Pulse magnetic immunity IEC61000 4 9 Level 4 Damped magnetic immunity IEC61000 4 10 Level 4 Voltage dip and interruption IEC61000 4 11 0 40 70 80 dips 25...

Page 46: ... inch pounds 2 inch pounds of torque CLEANING Normally cleaning is not required but for situations where dust has accumulated on the faceplate display a dry cloth can be used Units that are stored in a de energized state should be powered up once per year for one hour continuously to avoid deterioration of electrolytic capacitors COMPLIANCE APPLICABLE COUNCIL DIRECTIVE ACCORDING TO CE compliance L...

Page 47: ... with limited rear depth There is also a removable dust cover that fits over the faceplate which must be removed when attempting to access the keypad or RS232 communications port The case dimensions are shown below along with panel cutout details for panel mounting When planning the location of your panel cutout ensure that provision is made for the faceplate to swing open without interference to ...

Page 48: ...d rear depth There is also a removable dust cover that fits over the faceplate which must be removed when attempting to access the keypad or RS232 communications port The case dimensions are shown below along with panel cutout details for panel mounting When planning the location of your panel cutout ensure that provision is made for the faceplate to swing open without interference to or from adja...

Page 49: ...GE Multilin F35 Multiple Feeder Protection System 3 3 3 HARDWARE 3 1 DESCRIPTION 3 Figure 3 4 F35 VERTICAL MOUNTING AND DIMENSIONS e UR SERIES UR SERIES ...

Page 50: ...3 4 F35 Multiple Feeder Protection System GE Multilin 3 1 DESCRIPTION 3 HARDWARE 3 Figure 3 5 F35 VERTICAL SIDE MOUNTING INSTALLATION ...

Page 51: ...r electrostatic discharge protection for example a static strap must be used when coming in con tact with modules while the relay is energized The relay being modular in design allows for the withdrawal and insertion of modules Modules must only be replaced with like modules in their original factory configured slots The enhanced faceplate can be opened to the left once the thumb screw has been re...

Page 52: ...tion of the module to ensure that the same or replacement module is inserted into the correct slot Modules with current input provide automatic shorting of external CT circuits To properly insert a module ensure that the correct module type is inserted into the correct slot position The ejector inserter clips located at the top and at the bottom of each module must be in the disengaged position as...

Page 53: ...mber assignments which are three characters long assigned in order by module slot position row number and column letter Two slot wide modules take their slot designation from the first slot position nearest to CPU module which is indicated by an arrow marker on the terminal block See the following figure for an example of rear terminal assignments NOTE X W V U T S P N M L K J H D G F B R 8 4 7 3 6...

Page 54: ...3 8 F35 Multiple Feeder Protection System GE Multilin 3 1 DESCRIPTION 3 HARDWARE 3 Figure 3 10 EXAMPLE OF MODULES IN F AND H SLOTS ...

Page 55: ... INPUT W8a CONTACT INPUT W6c CONTACT INPUT W8c COMMON W5b COMMON W7b SURGE W6a W8a W5b W7b W8b W5a W7a W6c W8c W5c W7c W1 W2 W3 W4 I V I V I V I V DIGITAL INPUTS OUTPUTS 6G U1c U4a U3c U5a U5c U7c CIRCUIT U CURRENT INPUTS U6a U7a U6c U2c VA VB VC U4c U1a U4b U1b U2a U3a U2b U3b CIRCUIT U VOLTAGE INPUTS 8F 8G VA VB VC IA IB IC IG IA5 IA1 IB5 IC5 IG5 IB1 IC1 IG1 F7c F8c F8b F8a F5c F5a F5b F7b F3c F...

Page 56: ...dry contact input connections The power supply module provides 48 V DC power for dry contact input connections and a critical failure relay see the Typical wiring diagram earlier The critical failure relay is a form C device that will be energized once control power is applied and the relay has successfully booted up with no critical self test failures If on going self test diagnostic checks detec...

Page 57: ...s an isolating transformer and an automatic shorting mechanism that shorts the input when the module is withdrawn from the chassis There are no internal ground connections on the current inputs Current transformers with 1 to 50000 A primaries and 1 A or 5 A secondaries may be used CT VT modules with a sensitive ground input are also available The ground CT input of the sensitive ground modules is ...

Page 58: ...NG Ground connection to neutral must be on the source side UNSHIELDED CABLE LOAD A B C N G Ground outside CT Source LOAD SHIELDED CABLE 996630A5 A B C Source To ground must be on load side Stress cone shields NOTE 1a 1b 1c 2a 2b 2c 3a 4a 5a 6a 7a 8a 3b 4b 5c 6c 7c 8c 3c 4c Current inputs 8F 8G 8L and 8M modules 4 CTs and 4 VTs Voltage inputs VA VB VC VX VA VB VC VX IA IC IB IG IA5 IC5 IB5 IG5 IA1 ...

Page 59: ...per row these names are assigned by module slot position row number and column position Some form A solid state relay outputs include circuits to monitor the DC voltage across the output contact when it is open and the DC current through the output contact when it is closed Each of the monitors contains a level detector whose out put is set to logic On 1 when the current in the circuit is above th...

Page 60: ...d and subsequently opened when measured as an impedance The solution to this problem is to use the voltage measuring trigger input of the relay test set and connect the form A contact through a voltage dropping resistor to a DC voltage source If the 48 V DC output of the power supply is used as a source a 500 Ω 10 W resistor is appropriate In this configuration the voltage across either the form A...

Page 61: ...A 6a 6c 2 Inputs 6 Fast Form C 6a 6c 2 Inputs 6 Form A 7a 7c 2 Inputs 7 Fast Form C 7a 7c 2 Inputs 7a 7c 2 Inputs 8a 8c 2 Inputs 8 Fast Form C 8a 8c 2 Inputs 8a 8c 2 Inputs 6K MODULE 6L MODULE 6M MODULE 6N MODULE TERMINAL ASSIGNMENT OUTPUT TERMINAL ASSIGNMENT OUTPUT OR INPUT TERMINAL ASSIGNMENT OUTPUT OR INPUT TERMINAL ASSIGNMENT OUTPUT OR INPUT 1 Form C 1 Form A 1 Form A 1 Form A 2 Form C 2 Form ...

Page 62: ...5 Form A 5 Form A 5 Not Used 5 Not Used 6 Form A 6 Form A 6 Solid State 6 Solid State 7a 7c 2 Inputs 7 Form A 7 Not Used 7 Not Used 8a 8c 2 Inputs 8 Form A 8 Solid State 8 Solid State 4C MODULE 4D MODULE 4L MODULE TERMINAL ASSIGNMENT OUTPUT TERMINAL ASSIGNMENT OUTPUT TERMINAL ASSIGNMENT OUTPUT 1 Not Used 1a 1c 2 Inputs 1 2 Outputs 2 Solid State 2a 2c 2 Inputs 2 2 Outputs 3 Not Used 3a 3c 2 Inputs ...

Page 63: ...GE Multilin F35 Multiple Feeder Protection System 3 17 3 HARDWARE 3 2 WIRING 3 Figure 3 17 DIGITAL INPUT OUTPUT MODULE WIRING 1 of 2 842762A2 CDR ...

Page 64: ...tection System GE Multilin 3 2 WIRING 3 HARDWARE 3 Figure 3 18 DIGITAL INPUT OUTPUT MODULE WIRING 2 of 2 CORRECT POLARITY MUST BE OBSERVED FOR ALL CONTACT INPUT AND SOLID STATE OUTPUT CON NECTIONS FOR PROPER FUNCTIONALITY CAUTION ...

Page 65: ...ources 33 V DC for 48 V sources 84 V DC for 110 to 125 V sources and 166 V DC for 250 V sources Figure 3 19 DRY AND WET CONTACT INPUT CONNECTIONS Wherever a tilde symbol appears substitute with the slot position of the module Contact outputs may be ordered as form a or form C The form A contacts may be connected for external circuit supervi sion These contacts are provided with voltage and current...

Page 66: ...e change of state was sensed Then within 25 to 50 ms this current is slowly reduced to 3 mA as indicated above The 50 to 70 mA peak current burns any film on the con tacts allowing for proper sensing of state changes If the external device contact is bouncing the auto burnishing starts when external device contact bouncing is over Another important difference between the auto burnishing input modu...

Page 67: ...onnections These connections are arranged as three ter minals per row with a total of eight rows A given row may be used for either inputs or outputs with terminals in column a having positive polarity and terminals in column c having negative polarity Since an entire row is used for a single input output channel the name of the channel is assigned using the module slot position and row number Eac...

Page 68: ... 23 RS232 FACEPLATE PORT CONNECTION 3 2 8 CPU COMMUNICATION PORTS a OPTIONS In addition to the faceplate RS232 port the F35 provides two additional communication ports or a managed six port Ether net switch depending on the installed CPU module The CPU modules do not require a surge ground connection Table 3 3 CPU MODULE COMMUNICATIONS CPU TYPE COM1 COM2 9E RS485 RS485 9G 10Base F and 10Base T RS4...

Page 69: ...0Base F COMMON D1a D2a D3a D4b D4a BNC BNC IRIG B output IRIG B input CPU 9M Co axial cable Co axial cable Shielded twisted pairs SM fiber optic cable Ground at remote device RS485 COM2 COMMON D1a D2a D3a D4b D4a BNC BNC IRIG B output IRIG B input CPU 9E RS485 COM2 COMMON D1b D2b D3b RS485 COM1 Ground at remote device Co axial cable Co axial cable Shielded twisted pairs NORMAL ALTERNATE COM1 100Ba...

Page 70: ...point only Each relay should also be daisy chained to the next one in the link A maximum of 32 relays can be connected in this manner without exceeding driver capability For larger systems additional serial channels must be added It is also possible to use commercially available repeaters to increase the number of relays on a single channel to more than 32 Star or stub connections should be avoide...

Page 71: ...e The 10 Mbps rate is available for CPU modules 9G and 9H 100Mbps is available for modules 9H 9J 9K 9L 9M 9N 9P and 9R The 9H 9K 9M and 9R modules have a second pair of identical optical fiber transmitter and receiver for redundancy The optical fiber sizes supported include 50 125 µm 62 5 125 µm and 100 140 µm for 10 Mbps The fiber optic port is designed such that the response times will not vary ...

Page 72: ...aphic locations can also be synchronized Figure 3 26 IRIG B CONNECTION The IRIG B repeater provides an amplified DC shift IRIG B signal to other equipment By using one IRIG B serial connec tion several UR series relays can be synchronized The IRIG B repeater has a bypass function to maintain the time signal even when a relay in the series is powered down Figure 3 27 IRIG B REPEATER Using an amplit...

Page 73: ...s relays can be connected in a single ring Figure 3 28 DIRECT INPUT AND OUTPUT SINGLE CHANNEL CONNECTION The interconnection for dual channel Type 7 communications modules is shown below Two channel modules allow for a redundant ring configuration That is two rings can be created to provide an additional independent data path The required connections are UR1 Tx1 to UR2 Rx1 UR2 Tx1 to UR3 Rx1 UR3 T...

Page 74: ...IEEE C37 94 820 nm 128 kbps multi mode LED 2 channels 2S Six port managed Ethernet switch with high voltage power supply 2T Six port managed Ethernet switch with low voltage power supply 72 1550 nm single mode laser 1 channel 73 1550 nm single mode laser 2 channels 74 Channel 1 RS422 channel 2 1550 nm single mode laser 75 Channel 1 G 703 channel 2 1550 nm single mode laser 76 IEEE C37 94 820 nm 64...

Page 75: ... Interface attenuators may be necessary to ensure that you do not exceed the maxi mum optical input power to the receiver 7N Channel 1 RS422 channel 2 1300 nm single mode ELED 7P Channel 1 RS422 channel 2 1300 nm single mode laser 7Q Channel 1 G 703 channel 2 1300 nm single mode laser 7R G 703 1 channel 7S G 703 2 channels 7T RS422 1 channel 7V RS422 2 channels 2 clock inputs 7W RS422 2 channels T...

Page 76: ... manufacturer to another Therefore it is not uncommon to see pin outs numbered TxA TxB RxA and RxB In such cases it can be assumed that A is equivalent to and B is equivalent to b G 703 SELECTION SWITCH PROCEDURES 1 Remove the G 703 module 7R or 7S The ejector inserter clips located at the top and at the bottom of each module must be pulled simultaneously in order to release the module for removal...

Page 77: ...should be disabled off d G 703 TIMING MODES There are two timing modes for the G 703 module internal timing mode and loop timing mode default Internal Timing Mode The system clock is generated internally Therefore the G 703 timing selection should be in the internal timing mode for back to back UR to UR connections For back to back connections set for octet timing S1 OFF and timing mode to interna...

Page 78: ...UM REMOTE LOOPBACK MODE In dual loopback mode the multiplexers are active and the functions of the circuit are divided into two with each receiver transmitter pair linked together to deconstruct and then reconstruct their respective signals Differential Manchester data enters the Differential Manchester receiver module and then is returned to the differential Manchester transmitter module Likewise...

Page 79: ...end timing ST connections However when used in two channel applications certain criteria must be followed since there is one clock input for the two RS422 channels The system will function cor rectly if the following connections are observed and your data module has a terminal timing feature Terminal timing is a common feature to most synchronous data units that allows the module to accept timing ...

Page 80: ...edge of the Tx clock in the center of the Tx data bit Figure 3 41 CLOCK AND DATA TRANSITIONS d RECEIVE TIMING The RS422 interface utilizes NRZI MARK modulation code and therefore does not rely on an Rx clock to recapture data NRZI MARK is an edge type invertible self clocking code Data module 1 Data module 2 Signal name Signal name SD A Send data TT A Terminal timing TT B Terminal timing SD B Send...

Page 81: ...ceed maximum optical input power to the receiver Figure 3 42 RS422 AND FIBER INTERFACE CONNECTION Connections shown above are for multiplexers configured as DCE data communications equipment units 3 3 7 G 703 AND FIBER INTERFACE The figure below shows the combined G 703 plus fiber interface configuration at 64 kbps The 7E 7F 7G 7Q and 75 mod ules are used in configurations where channel 1 is emplo...

Page 82: ...and is repeated at a frame rate of 8000 Hz with a resultant bit rate of 2048 kbps The specifications for the module are as follows IEEE standard C37 94 for 1 64 kbps optical fiber interface for 2G and 2H modules or C37 94 for 2 64 kbps optical fiber interface for 76 and 77 modules Fiber optic cable type 50 mm or 62 5 mm core diameter optical fiber Fiber optic mode multi mode Fiber optic cable leng...

Page 83: ...removal Before performing this action control power must be removed from the relay The original location of the module should be recorded to help ensure that the same or replacement module is inserted into the correct slot 2 Remove the module cover screw 3 Remove the top cover by sliding it towards the rear and then lift it upwards 4 Set the timing selection switches channel 1 channel 2 to the des...

Page 84: ... rate of 2048 kbps The specifications for the module are as follows Emulated IEEE standard emulates C37 94 for 1 64 kbps optical fiber interface modules set to n 1 or 64 kbps Fiber optic cable type 9 125 μm core diameter optical fiber Fiber optic mode single mode ELED compatible with HP HFBR 1315T transmitter and HP HFBR 2316T receiver Fiber optic cable length up to 10 km Fiber optic connector typ...

Page 85: ...le should be recorded to help ensure that the same or replacement module is inserted into the correct slot 2 Remove the module cover screw 3 Remove the top cover by sliding it towards the rear and then lift it upwards 4 Set the timing selection switches channel 1 channel 2 to the desired timing modes see description above 5 Replace the top cover and the cover screw 6 Re insert the C37 94SM module ...

Page 86: ...CODE XXX self test warning will be issued 3 4 2 MANAGED ETHERNET SWITCH MODULE HARDWARE The type 2S and 2T managed Ethernet switch modules provide two 10 100Base T and four multimode ST 100Base FX external Ethernet ports accessible through the rear of the module In addition a serial console port is accessible from the front of the module requires the front panel faceplate to be open The pin assign...

Page 87: ...lt your net work administrator to determine if the default IP address subnet mask or default gateway needs to be modified Do not connect to network while configuring the switch module a CONFIGURING THE SWITCH MODULE IP SETTINGS In our example configuration of both the Switch s IP address and subnet mask must be changed to 3 94 247 229 and 255 255 252 0 respectively The IP address subnet mask and d...

Page 88: ... switch module 1 Select the desired device from site tree in the online window 2 Select the Settings Product Setup Communications Ethernet Switch Ethernet Switch Settings File Retreive Settings File item from the device settings tree The system will request the name and destination path for the settings file 3 Enter an appropriate folder and file name and click Save All settings files will be save...

Page 89: ... firmware on a switch module Using the EnerVista UR Setup software Serially using the F35 switch module console port Using FTP or TFTP through the F35 switch module console port It is highly recommended to use the EnerVista UR Setup software to upgrade firmware on a F35 switch module Firmware upgrades using the serial port TFTP and FTP are described in detail in the switch module manual b SELECTIN...

Page 90: ...cations Ethernet Switch Firmware Upload menu item The following popup screen will appear warning that the settings will be lost when the firmware is upgraded It is highly recommended that you save the switch settings before upgrading the firmware 3 After saving the settings file proceed with the firmware upload by selecting Yes to the above warning Another window will open asking you to point to t...

Page 91: ...ion The following window will pop up indicating that the firmware file transfer is in progress If the firmware load was successful the following window will appear Note The switch will automatically reboot after a successful firmware file transfer 5 Once the firmware has been successfully uploaded to the switch module load the settings file using the procedure described earlier NOTE ...

Page 92: ...ling attempts Loss of switch power IP gateway subnet Incompatibility between the CPU and the switch module UR port port 7 configured incorrectly or blocked Switch IP address assigned to another device in the same network PORT 1 EVENTS to PORT 6 EVENTS ETHERNET PORT 1 OFFLINE to ETHERNET PORT 6 OFFLINE An active Ethernet port has returned a FAILED status Ethernet connection broken An inactive port ...

Page 93: ...ce definition must first be created See the EnerV ista UR Setup Help File or refer to the Connecting EnerVista UR Setup with the F35 section in Chapter 1 for details 4 1 3 ENERVISTA UR SETUP OVERVIEW a ENGAGING A DEVICE The EnerVista UR Setup software may be used in on line mode relay connected to directly communicate with the F35 relay Communicating relays are organized and grouped by communicati...

Page 94: ...nsion which had been removed from the Settings List tree menu it will be added back to the Settings List tree menu Drag and Drop The Site List and Settings List control bar windows are each mutually a drag source and a drop target for device order code compatible files or individual menu items Also the Settings List control bar window and any Windows Explorer directory folder are each mutually a f...

Page 95: ...onents 1 Title bar which shows the pathname of the active data view 2 Main window menu bar 3 Main window tool bar 4 Site list control bar window 5 Settings list control bar window 6 Device data view windows with common tool bar 7 Settings file data view windows with common tool bar 8 Workspace area with data view tabs 9 Status bar 10 Quick action hot links Figure 4 1 ENERVISTA UR SETUP SOFTWARE MA...

Page 96: ...e template feature is disabled by default The following procedure describes how to enable the settings tem plate for UR series settings files 1 Select a settings file from the offline window of the EnerVista UR Setup main screen 2 Right click on the selected device or settings file and select the Template Mode Create Template option The settings file template is now enabled and the file tree displ...

Page 97: ...able by clicking on them The setting available to view will be displayed against a yellow background as shown below Figure 4 3 SETTINGS TEMPLATE VIEW TWO SETTINGS SPECIFIED AS EDITABLE 6 Click on Save to save changes to the settings template 7 Proceed through the settings tree to specify all viewable settings c ADDING PASSWORD PROTECTION TO A TEMPLATE It is highly recommended that templates be sav...

Page 98: ...nly those settings available for editing Display all settings with settings not available for editing greyed out Use the following procedure to only display settings available for editing 1 Select an installed device or a settings file from the tree menu on the left of the EnerVista UR Setup main screen 2 Apply the template by selecting the Template Mode View In Template Mode option 3 Enter the te...

Page 99: ...pecified by the template but all settings will be shown The effect of applying the template to the phase time overcurrent settings is shown below Figure 4 6 APPLYING TEMPLATES VIA THE VIEW ALL SETTINGS COMMAND e REMOVING THE SETTINGS TEMPLATE It may be necessary at some point to remove a settings template Once a template is removed it cannot be reapplied and it will be necessary to define a new se...

Page 100: ...ION ENTRIES The following procedure describes how to lock individual entries of a FlexLogic equation 1 Right click the settings file or online device and select the Template Mode Create Template item to enable the set tings template feature 2 Select the FlexLogic FlexLogic Equation Editor settings menu item By default all FlexLogic entries are specified as viewable and displayed against a yellow b...

Page 101: ...own below and on the front panel display Figure 4 9 SECURED FLEXLOGIC IN GRAPHICAL VIEW b LOCKING FLEXLOGIC EQUATIONS TO A SERIAL NUMBER A settings file and associated FlexLogic equations can also be locked to a specific UR serial number Once the desired FlexLogic entries in a settings file have been secured use the following procedure to lock the settings file to a specific serial number 1 Select...

Page 102: ...s infor mation can be compared with the F35 actual values at any later date to determine if security has been compromised The traceability information is only included in the settings file if a complete settings file is either transferred to the F35 device or obtained from the F35 device Any partial settings transfers by way of drag and drop do not add the traceability information to the settings ...

Page 103: ...he relay configuration since the settings file was saved a SETTINGS FILE TRACEABILITY INFORMATION The serial number and file transfer date are saved in the settings files when they sent to an F35 device The F35 serial number and file transfer date are included in the settings file device definition within the EnerVista UR Setup offline window as shown in the example below Figure 4 12 DEVICE DEFINI...

Page 104: ...EL INFORMATION ÖØ SERIAL NUMBER ACTUAL VALUES ÖØ PRODUCT INFO Ö MODEL INFORMATION ÖØ LAST SETTING CHANGE c ADDITIONAL TRACEABILITY RULES The following additional rules apply for the traceability feature If the user changes any settings within the settings file in the offline window then the traceability information is removed from the settings file If the user creates a new settings file then no t...

Page 105: ...her interface being EnerVista UR Setup software The front panel interface consists of LED panels an RS232 port keypad LCD display control pushbuttons and optional user programmable pushbuttons The faceplate is hinged to allow easy access to the removable modules There is also a removable dust cover that fits over the faceplate which must be removed in order to access the keypad panel The following...

Page 106: ...ondition has been cleared these latched conditions can also be reset via the SETTINGS ÖØ INPUT OUTPUTS ÖØ RESETTING menu The RS232 port is intended for connection to a portable PC The USER keys are not used in this unit Figure 4 18 TYPICAL LED INDICATOR PANEL FOR ENHANCED FACEPLATE The status indicators in the first column are described below IN SERVICE This LED indicates that control power is app...

Page 107: ...EDs consist of 48 amber LED indicators in four columns The operation of these LEDs is user defined Support for applying a customized label beside every LED is provided Default labels are shipped in the label pack age of every F35 together with custom templates The default labels can be replaced by user printed labels User customization of LED operation is of maximum benefit in installations where ...

Page 108: ...DICATORS The second and third provide 48 amber LED indicators whose operation is controlled by the user Support for applying a customized label beside every LED is provided User customization of LED operation is of maximum benefit in installations where languages other than English are used to communicate with operators Refer to the User programmable LEDs section in chapter 5 for the settings used...

Page 109: ...lowing procedure requires the pre requisites listed below EnerVista UR Setup software is installed and operational The F35 settings have been saved to a settings file The F35 front panel label cutout sheet GE Multilin part number 1006 0047 has been downloaded from http www GEindustrial com multilin support ur and printed Small bladed knife This procedure describes how to create custom LED labels f...

Page 110: ...ted side containing the GE part number facing the user The label package shipped with every F35 contains the three default labels shown below the custom label template sheet and the label removal tool If the default labels are suitable for your application insert them in the appropriate slots and program the LEDs to match them If you require custom labels follow the procedures below to remove the ...

Page 111: ...e knife to lift the LED label and slide the label tool underneath Make sure the bent tabs are pointing away from the relay 2 Slide the label tool under the LED label until the tabs snap out as shown below This will attach the label tool to the LED label 3 Remove the tool and attached LED label as shown below ...

Page 112: ...emove the user programmable pushbutton labels from the F35 enhanced front panel and insert the custom labels 1 Use the knife to lift the pushbutton label and slide the tail of the label tool underneath as shown below Make sure the bent tab is pointing away from the relay 2 Slide the label tool under the user programmable pushbutton label until the tabs snap out as shown below This will attach the ...

Page 113: ... STANDARD FACEPLATE Custom labeling of an LED only panel is facilitated through a Microsoft Word file available from the following URL http www GEindustrial com multilin support ur This file provides templates and instructions for creating appropriate labeling for the LED panel The following procedures are contained in the downloadable file The panel templates provide relative LED locations and lo...

Page 114: ...ocal PC for future use 3 Print the template s to a local printer 4 From the printout cut out the Background Template from the three windows using the cropmarks as a guide 5 Put the Background Template on top of the custom display module GE Multilin Part Number 1513 0069 and snap the clear custom module cover GE Multilin Part Number 1502 0015 over it and the templates 4 3 4 DISPLAY All messages are...

Page 115: ...wing discussion it is assumed the SETTINGS ÖØ SYSTEM SETUP ÖØ BREAKERS Ö BREAKER 1 2 Ö BREAKER FUNCTION setting is Enabled for each breaker b CONTROL MODE SELECTION AND MONITORING Installations may require that a breaker is operated in the three pole only mode 3 pole or in the one and three pole 1 pole mode selected by setting If the mode is selected as three pole a single input tracks the breaker...

Page 116: ...ge will be maintained for 30 seconds or until the USER 1 key is pressed again BKR1 Name SELECTED USER 2 CLS USER 3 OP This message is displayed after the USER 1 key is pressed for the second time Three possible actions can be performed from this state within 30 seconds as per items 1 2 and 3 below 1 USER 2 OFF ON To Close BKR1 Name If the USER 2 key is pressed this message appears for 20 seconds I...

Page 117: ...actual value headers Ø SETTINGS PRODUCT SETUP Press the MENU key until the header for the first page of Settings appears This page contains settings to configure the relay Ø SETTINGS SYSTEM SETUP Press the MESSAGE DOWN key to move to the next Settings page This page con tains settings for System Setup Repeatedly press the MESSAGE UP and DOWN keys to display the other setting headers and then back ...

Page 118: ...DOWN key displays the previous selection c ENTERING ALPHANUMERIC TEXT Text settings have data values which are fixed in length but user defined in character They may be comprised of upper case letters lower case letters numerals and a selection of special characters FLASH MESSAGE TIME 1 0 s For example select the SETTINGS Ö PRODUCT SETUP ÖØ DISPLAY PROPERTIES Ö FLASH MESSAGE TIME setting Ø MINIMUM...

Page 119: ...ssage appears on the display 2 Press the MESSAGE RIGHT key until the PASSWORD SECURITY message appears on the display 3 Press the MESSAGE DOWN key until the INSTALLATION message appears on the display 4 Press the MESSAGE RIGHT key until the RELAY SETTINGS Not Programmed message is displayed 5 After the RELAY SETTINGS Not Programmed message appears on the display press the VALUE keys change the sel...

Page 120: ...WORD 7 Type in a numerical password up to 10 characters and press the ENTER key 8 When the VERIFY NEW PASSWORD is displayed re type in the same password and press ENTER 9 When the NEW PASSWORD HAS BEEN STORED message appears your new Setting or Command Password will be active f CHANGING EXISTING PASSWORD To change an existing password follow the instructions in the previous section with the follow...

Page 121: ...be set to Off after the expiration of the ten minute timeout In the event that an incorrect Command or Setting password has been entered via the any external communications inter face three times within a three minute time span the REMOTE ACCESS DENIED FlexLogic operand will be set to On and the F35 will not allow Settings or Command access via the any external communications interface for the nex...

Page 122: ...4 30 F35 Multiple Feeder Protection System GE Multilin 4 3 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...

Page 123: ... CLOCK See page 5 33 FAULT REPORTS See page 5 34 OSCILLOGRAPHY See page 5 36 DATA LOGGER See page 5 38 DEMAND See page 5 40 USER PROGRAMMABLE LEDS See page 5 41 USER PROGRAMMABLE SELF TESTS See page 5 44 CONTROL PUSHBUTTONS See page 5 45 USER PROGRAMMABLE PUSHBUTTONS See page 5 46 FLEX STATE PARAMETERS See page 5 51 USER DEFINABLE DISPLAYS See page 5 52 DIRECT I O See page 5 54 TELEPROTECTION See ...

Page 124: ...RS See page 5 96 FLEXELEMENTS See page 5 98 NON VOLATILE LATCHES See page 5 102 SETTINGS GROUPED ELEMENTS SETTING GROUP 1 See page 5 103 SETTING GROUP 2 SETTING GROUP 3 SETTING GROUP 4 SETTING GROUP 5 SETTING GROUP 6 SETTINGS CONTROL ELEMENTS SETTING GROUPS See page 5 121 SELECTOR SWITCH See page 5 122 UNDERFREQUENCY See page 5 128 AUTORECLOSE See page 5 129 DIGITAL ELEMENTS See page 5 135 DIGITAL...

Page 125: ...56 REMOTE INPUTS See page 5 157 REMOTE OUTPUTS DNA BIT PAIRS See page 5 158 REMOTE OUTPUTS UserSt BIT PAIRS See page 5 158 RESETTING See page 5 159 DIRECT INPUTS See page 5 159 DIRECT OUTPUTS See page 5 160 TELEPROTECTION See page 5 163 IEC 61850 GOOSE ANALOGS See page 5 165 SETTINGS TRANSDUCER I O DCMA INPUTS See page 5 166 RTD INPUTS See page 5 167 DCMA OUTPUTS See page 5 169 SETTINGS TESTING TE...

Page 126: ...For current elements the base quantity is the nominal secondary or primary current of the CT Where the current source is the sum of two CTs with different ratios the base quantity will be the common secondary or primary current to which the sum is scaled that is normalized to the larger of the two rated CT inputs For example if CT1 300 5 A and CT2 100 5 A then in order to sum these CT2 is scaled t...

Page 127: ...ing functions For a three winding transformer application it may be required to calculate watts and vars for each of three windings using voltage from different sets of VTs These requirements can be satisfied with a single UR equipped with sufficient CT and VT input channels by selecting the parameter to measure A mechanism is provided to specify the AC parameter or group of parameters used as the...

Page 128: ... use For example in the scheme shown in the above diagram the configures one Source to be the sum of CT1 and CT2 and can name this Source as Wdg 1 Current Once the sources have been configured the user has them available as selections for the choice of input signal for the pro tection elements and as metered quantities b CT VT MODULE CONFIGURATION CT and VT input channels are contained in CT VT mo...

Page 129: ...f the set of three channels Upon startup the CPU configures the settings required to characterize the current and voltage inputs and will display them in the appropriate section in the sequence of the banks as described above as follows for a maximum configuration F1 F5 M1 M5 U1 and U5 The above section explains how the input channels are identified and configured to the specific application instr...

Page 130: ...e F35 supports password entry from a local or remote connection Local access is defined as any access to settings or commands via the faceplate interface This includes both keypad entry and the through the faceplate RS232 port Remote access is defined as any access to settings or commands via any rear communications port This includes both Ethernet and RS485 connections Any changes to the local or...

Page 131: ...y with the corresponding ENCRYPTED PASSWORD If the setting and command passwords are identical then this one password allows access to both com mands and settings c REMOTE PASSWORDS The remote password settings are only visible from a remote connection via the EnerVista UR Setup software Select the Settings Product Setup Password Security menu item to open the remote password settings window Figur...

Page 132: ...lockout password access after the number of invalid password entries specified by the INVALID ATTEMPS BEFORE LOCKOUT setting has occurred The F35 provides a means to raise an alarm upon failed password entry Should password verification fail while accessing a password protected level of the relay either settings or commands the UNAUTHORIZED ACCESS FlexLogic operand is asserted The operand can be p...

Page 133: ...tivity time is modified via this setting to ensure messages remain on the screen long enough during programming or reading of actual values DEFAULT MESSAGE INTENSITY To extend phosphor life in the vacuum fluorescent display the brightness can be attenuated during default message display During keypad interrogation the display always operates at full brightness SCREEN SAVER FEATURE and SCREEN SAVER...

Page 134: ...he cut off operation applies to quantities used for metering protection and control as well as those used by communications protocols Raw samples of the voltages available via oscillography are not subject cut off The CURRENT CUT OFF LEVEL and the VOLTAGE CUT OFF LEVEL are used to determine the metered power cut off levels The power cut off level is calculated as shown below For Delta connections ...

Page 135: ...ords the following settings should be applied 1 Assign the clear demand function to Pushbutton 1 by making the following change in the SETTINGS Ö PRODUCT SETUP ÖØ CLEAR RELAY RECORDS menu CLEAR DEMAND PUSHBUTTON 1 ON 2 Set the properties for User Programmable Pushbutton 1 by making the following changes in the SETTINGS Ö PRODUCT SETUP ÖØ USER PROGRAMMABLE PUSHBUTTONS Ö USER PUSHBUTTON 1 menu PUSHB...

Page 136: ...L See page 5 16 MESSAGE DNP IEC104 POINT LISTS See page 5 19 MESSAGE IEC 61850 PROTOCOL See page 5 20 MESSAGE WEB SERVER HTTP PROTOCOL See page 5 29 MESSAGE TFTP PROTOCOL See page 5 29 MESSAGE IEC 60870 5 104 PROTOCOL See page 5 29 MESSAGE SNTP PROTOCOL See page 5 30 MESSAGE EGD PROTOCOL See page 5 30 MESSAGE ETHERNET SWITCH See page 5 32 SERIAL PORTS RS485 COM1 BAUD RATE 19200 Range 300 1200 2400...

Page 137: ...hen used with DNP is changed it will not become active until power to the relay has been cycled off on Do not set more than one protocol to the same TCP UDP PORT NUMBER as this will result in unreliable opera tion of those protocols d MODBUS PROTOCOL PATH SETTINGS Ö PRODUCT SETUP ÖØ COMMUNICATIONS ÖØ MODBUS PROTOCOL The serial communication ports utilize the Modbus protocol unless configured for D...

Page 138: ...0 10000 100000 MESSAGE DNP VOLTAGE SCALE FACTOR 1 Range 0 001 0 01 0 1 1 10 100 1000 10000 100000 MESSAGE DNP POWER SCALE FACTOR 1 Range 0 001 0 01 0 1 1 10 100 1000 10000 100000 MESSAGE DNP ENERGY SCALE FACTOR 1 Range 0 001 0 01 0 1 1 10 100 1000 10000 100000 MESSAGE DNP PF SCALE FACTOR 1 Range 0 001 0 01 0 1 1 10 100 1000 10000 100000 MESSAGE DNP OTHER SCALE FACTOR 1 Range 0 001 0 01 0 1 1 10 10...

Page 139: ... on channels 1 or 2 When this value is set to Network UDP the DNP protocol can be used over UDP IP on chan nel 1 only Refer to Appendix E for additional information on the DNP protocol Changes to the DNP CHANNEL 1 PORT and DNP CHANNEL 2 PORT settings will take effect only after power has been cycled to the relay The DNP NETWORK CLIENT ADDRESS settings can force the F35 to respond to a maximum of f...

Page 140: ...d to change dead band values from the default for each individual DNP analog input point Whenever power is removed and re applied to the F35 the default deadbands will be in effect The DNP TIME SYNC IIN PERIOD setting determines how often the Need Time Internal Indication IIN bit is set by the F35 Changing this time allows the DNP master to send time synchronization commands more or less often as ...

Page 141: ...gning FlexLogic operands for binary inputs MSP points or FlexAnalog parameters for analog inputs MME points The menu for the binary input points DNP or MSP points IEC 60870 5 104 is shown below PATH SETTINGS Ö PRODUCT SETUP ÖØ COMMUNICATIONS ÖØ DNP IEC104 POINT LISTS Ö BINARY INPUT MSP POINTS Up to 256 binary input points can be configured for the DNP or IEC 60870 5 104 protocols The points are co...

Page 142: ...ures are not available if CPU type E is ordered The F35 supports the Manufacturing Message Specification MMS protocol as specified by IEC 61850 MMS is supported over two protocol stacks TCP IP over ethernet and TP4 CLNP OSI over ethernet The F35 operates as an IEC 61850 server The Remote inputs and outputs section in this chapter describe the peer to peer GSSE GOOSE message scheme The GSSE GOOSE c...

Page 143: ...abled GSSE messages are not transmitted The GSSE ID setting represents the IEC 61850 GSSE application ID name string sent as part of each GSSE message This string identifies the GSSE message to the receiving device In F35 releases previous to 5 0x this name string was repre sented by the RELAY NAME setting The fixed GOOSE settings are shown below PATH SETTINGS Ö PRODUCT ÖØ COMMUNICATIONS ÖØ IEC 61...

Page 144: ...he F35 The F35 supports the configuration of eight 8 transmission and reception datasets allowing for the optimization of data transfer between devices Items programmed for dataset 1 will have changes in their status transmitted as soon as the change is detected Dataset 1 should be used for high speed transmission of data that is required for applications such as transfer tripping blocking and bre...

Page 145: ...figure the transmission dataset 2 Configure the GOOSE service settings 3 Configure the data The general steps required for reception configuration are 1 Configure the reception dataset 2 Configure the GOOSE service settings 3 Configure the data This example shows how to configure the transmission and reception of three IEC 61850 data items a single point status value its associated quality flags a...

Page 146: ... changes in the INPUTS OUTPUTS ÖØ REMOTE INPUTS ÖØ REMOTE INPUT 1 settings menu Set REMOTE IN 1 DEVICE to GOOSEOut_1 Set REMOTE IN 1 ITEM to Dataset Item 2 This assigns the value of the GGIO3 ST Ind1 stVal single point status item to remote input 1 Remote input 1 can now be used in FlexLogic equations or other settings The F35 must be rebooted control power removed and re applied before these sett...

Page 147: ... SETUP ÖØ COMMUNICATIONS ÖØ IEC 61850 PROTOCOL ÖØ SERVER CONFIGURATION The IED NAME and LD INST settings represent the MMS domain name IEC 61850 logical device where all IEC MMS logical nodes are located Valid characters for these values are upper and lowercase letters numbers and the underscore _ character and the first character in the string must be a letter This conforms to the IEC 61850 stand...

Page 148: ...Ø MMXU DEADBANDS The MMXU deadband settings represent the deadband values used to determine when the update the MMXU mag and cVal values from the associated instmag and instcVal values The mag and cVal values are used for the IEC 61850 buffered and unbuffered reports These settings correspond to the associated db data items in the CF functional con straint of the MMXU logical node as per the IEC 6...

Page 149: ... security The GGIO2 control points are used to control the F35 virtual inputs The GGIO4 analog configuration points are shown below PATH SETTINGS Ö PRODUCT SETUP ÖØ COMMUNICATIONS ÖØ IEC 61850 ÖØ GGIO4 ANALOG CONFIGURATION The NUMBER OF ANALOG POINTS setting determines how many analog data points will exist in GGIO4 When this value is changed the F35 must be rebooted in order to allow the GGIO4 lo...

Page 150: ...ANALOG IN 1 MAX settings are stored as IEEE 754 IEC 60559 floating point numbers Because of the large range of these settings not all values can be stored Some values may be rounded to the closest possible floating point number The report control configuration settings are shown below PATH SETTINGS Ö PRODUCT SETUP ÖØ COMMUNICATIONS ÖØ IEC 61850 ÖØ REPORT Ö REPORT 1 6 CONFIGURATION Changes to the r...

Page 151: ...TP client software is available from various sources including Microsoft Windows NT The dir txt file obtained from the F35 contains a list and description of all available files event records oscillography etc j IEC 60870 5 104 PROTOCOL PATH SETTINGS Ö PRODUCT SETUP ÖØ COMMUNICATIONS ÖØ IEC 60870 5 104 PROTOCOL WEB SERVER HTTP PROTOCOL HTTP TCP PORT NUMBER 80 Range 1 to 65535 in steps of 1 TFTP PR...

Page 152: ...er to provide an accurate time Both unicast and broadcast SNTP are supported If SNTP functionality is enabled at the same time as IRIG B the IRIG B signal provides the time value to the F35 clock for as long as a valid signal is present If the IRIG B signal is removed the time obtained from the SNTP server is used If either SNTP or IRIG B is enabled the F35 clock value cannot be changed using the ...

Page 153: ...w PATH SETTINGS Ö PRODUCT SETUP ÖØ COMMUNICATIONS ÖØ EGD PROTOCOL Ö SLOW PROD EXCH 1 2 CONFIGURATION Slow EGD exchanges 500 to 1000 ms are generally used for the transfer and display of data items The settings for the fast and slow exchanges are described below EXCH 1 DESTINATION This setting specifies the destination IP address of the produced EGD exchange This is usu ally unicast or broadcast EX...

Page 154: ...us TCP port number for the Ethernet switch module are specified in this menu These settings are used in advanced network configurations Please consult the network administrator before making changes to these settings The client software EnerVista UR Setup for example is the preferred interface to configure these settings The PORT 1 EVENTS through PORT 6 EVENTS settings allow Ethernet switch module...

Page 155: ...ht savings time DST settings can be used to allow the F35 clock can follow the DST rules of the local time zone Note that when IRIG B time synchronization is active the DST settings are ignored The DST settings are used when the F35 is synchronized with SNTP or when neither SNTP nor IRIG B is used Only timestamps in the event recorder and communications protocols are affected by the daylight savin...

Page 156: ... with fault report source or the trigger operate Fault current and voltage phasors one cycle after the trigger Elements operated at the time of triggering Events 9 before trigger and 7 after trigger only available via the relay webpage Fault duration times for each breaker created by the breaker arcing current feature FAULT REPORT 1 FAULT REPORT 1 SOURCE SRC 1 Range SRC 1 SRC 2 SRC 3 SRC 4 SRC 5 S...

Page 157: ... of trigger the fault type the distance location of the fault and the reclose shot number The FAULT REPORT 1 SOURCE setting selects the source for input currents and voltages and disturbance detection The FAULT 1 REPORT TRIG setting assigns the FlexLogic operand representing the protection element elements requiring operational fault location calculations The distance to fault calculations are ini...

Page 158: ...ffer size for example 10 50 75 etc A trigger position of 25 consists of 25 pre and 75 post trigger data The TRIGGER SOURCE is always captured in oscillography and may be any FlexLogic parameter element state contact input virtual output etc The relay sampling rate is 64 samples per cycle The AC INPUT WAVEFORMS setting determines the sampling rate at which AC input signals that is current and volta...

Page 159: ...ng actual value parameters is presented in Appendix A FlexAnalog parameters The parameter index number shown in any of the tables is used to expedite the selection of the parameter on the relay display It can be quite time consuming to scan through the list of parameters via the relay keypad and display entering this number via the relay keypad will cause the corresponding parameter to be displaye...

Page 160: ...a fixed sampling rate the data logger can be configured with a few channels over a long period or a larger number of channels for a shorter period The relay automatically partitions the available memory between the channels in use Exam ple storage capacities for a system frequency of 60 Hz are shown in the following table DATA LOGGER DATA LOGGER MODE Continuous Range Continuous Trigger MESSAGE DAT...

Page 161: ...de is set to Trigger DATA LOGGER RATE This setting selects the time interval at which the actual value data will be recorded DATA LOGGER CHNL 1 16 This setting selects the metering actual value that is to be recorded in Channel 1 16 of the data log The parameters available in a given relay are dependent on the type of relay the type and number of CT VT hardware modules installed and the type and n...

Page 162: ...acteristic of 15 minutes is illustrated below A setpoint establishes the time to reach 90 of a steady state value just as the response time of an analog instrument A steady state value applied for twice the response time will indicate 99 of the value Figure 5 3 THERMAL DEMAND CHARACTERISTIC CALCULATION METHOD 2 BLOCK INTERVAL This method calculates a linear average of the quantity RMS current real...

Page 163: ...is a quick test to verify if any of the LEDs is burned This stage lasts as long as the control input is on up to a maximum of 1 minute After 1 minute the test will end 2 All the LEDs are turned off and then one LED at a time turns on for 1 second then back off The test routine starts at the top left panel moving from the top to bottom of each LED column This test checks for hardware failures that ...

Page 164: ...t to recognize user programmable pushbutton 1 by making the following entries in the SETTINGS Ö PRODUCT SETUP ÖØ USER PROGRAMMABLE LEDS Ö LED TEST menu LED TEST FUNCTION Enabled LED TEST CONTROL PUSHBUTTON 1 ON The test will be initiated when the user programmable pushbutton 1 is pressed The pushbutton should remain pressed for as long as the LEDs are being visually inspected When finished the pus...

Page 165: ... is in the logic 1 state For the standard faceplate the LEDs are located as follows LED Panel 2 user programmable LEDs 1 through 24 LED Panel 3 user programmable LEDs 25 through 48 For the enhanced faceplate the LEDs are located as follows LED column 2 user programmable LEDs 1 through 12 LED column 3 user programmable LEDs 13 through 24 LED column 4 user programmable LEDs 25 through 36 LED column ...

Page 166: ...and BREAKER 2 CLOSED LED 4 operand SETTING GROUP ACT 4 LED 16 operand BREAKER 2 TROUBLE LED 5 operand SETTING GROUP ACT 5 LED 17 operand SYNC 1 SYNC OP LED 6 operand SETTING GROUP ACT 6 LED 18 operand SYNC 2 SYNC OP LED 7 operand Off LED 19 operand Off LED 8 operand Off LED 20 operand Off LED 9 operand BREAKER 1 OPEN LED 21 operand AR ENABLED LED 10 operand BREAKER 1 CLOSED LED 22 operand AR DISAB...

Page 167: ... or disable control pushbuttons for security reasons Each control pushbutton asserts its own FlexLogic operand These operands should be configured appropriately to per form the desired function The operand remains asserted as long as the pushbutton is pressed and resets when the push button is released A dropout delay of 100 ms is incorporated to ensure fast pushbutton manipulation will be recogni...

Page 168: ...AGE PUSHBTN 1 RESET Off Range FlexLogic operand MESSAGE PUSHBTN 1 AUTORST Disabled Range Disabled Enabled MESSAGE PUSHBTN 1 AUTORST DELAY 1 0 s Range 0 2 to 600 0 s in steps of 0 1 MESSAGE PUSHBTN 1 REMOTE Off Range FlexLogic operand MESSAGE PUSHBTN 1 LOCAL Off Range FlexLogic operand MESSAGE PUSHBTN 1 DROP OUT TIME 0 00 s Range 0 to 60 00 s in steps of 0 05 MESSAGE PUSHBTN 1 LED CTL Off Range Fle...

Page 169: ...d are used to program specific actions If any pushbutton is active the ANY PB ON operand will be asserted Each pushbutton has an associated LED indicator By default this indicator displays the present status of the correspond ing pushbutton on or off However each LED indicator can be assigned to any FlexLogic operand through the PUSHBTN 1 LED CTL setting The pushbuttons can be automatically contro...

Page 170: ...ting selects the characteristic of the pushbutton If set to Disabled the push button is not active and the corresponding FlexLogic operands both On and Off are de asserted If set to Self Reset the control logic is activated by the pulse longer than 100 ms issued when the pushbutton is being physically pressed or virtually pressed via a FlexLogic operand assigned to the PUSHBTN 1 SET setting When i...

Page 171: ...and remains on has no effect on the pulse duration This setting is required to set the duration of the pushbutton operating pulse PUSHBTN 1 LED CTL This setting assigns the FlexLogic operand serving to drive pushbutton LED If this setting is Off then LED operation is directly linked to PUSHBUTTON 1 ON operand PUSHBTN 1 MESSAGE If pushbutton message is set to High Priority the message programmed in...

Page 172: ...f 0 PUSHBTN 1 LOCAL SETTING Off 0 PUSHBTN 1 SET SETTING Off 0 PUSHBTN 1 RESET SETTING Enabled Disabled PUSHBTN 1 AUTORST FLEXLOGIC OPERAND PUSHBUTTON 1 ON FLEXLOGIC OPERAND PUSHBUTTON 1 OFF TIMER 200 ms 0 AND AND AND AND AND TIMER 50 ms 0 TIMER 50 ms 0 SETTING PUSHBTN 1 AUTORST DELAY TPKP 0 TIMER 200 ms 0 AND AND SETTING PUSHBTN 1 DROP OUT DELAY TRST 0 PUSHBUTTON ON To user programmable pushbutton...

Page 173: ...SSAGE PARAMETER 256 Off Range FlexLogic operand Pushbutton 1 LED Instantaneous reset OR 1 If pushbutton 1 LED control is set to off 2 If pushbutton 1 LED control is not set to off PUSHBUTTON 1 LED LOGIC OR AND AND SETTING Disabled High Priority PUSHBUTTON 1 MESSAGE Normal FLEXLOGIC OPERAND PUSHBUTTON 1 ON Pushbutton 1 LED SETTING any FlexLogic operand PUSHBTN 1 LED CTL AND SETTING FLASH MESSAGE TI...

Page 174: ...by the PRODUCT SETUP ÖØ DISPLAY PROPER TIES ÖØ DEFAULT MESSAGE TIMEOUT setting USER PROGRAMMABLE CONTROL INPUT The user definable displays also respond to the INVOKE AND SCROLL setting Any FlexLogic operand in particular the user programmable pushbutton operands can be used to navi gate the programmed displays On the rising edge of the configured operand such as when the pushbutton is pressed the ...

Page 175: ...o scroll through the characters A space is selected like a character 4 Press the decimal key to advance the cursor to the next position 5 Repeat step 3 and continue entering characters until the desired text is displayed 6 The HELP key may be pressed at any time for context sensitive help information 7 Press the ENTER key to store the new settings To enter a numerical value for any of the five ite...

Page 176: ...s decimal form of user selected Modbus Register Address corresponding to first Tilde marker MESSAGE DISP 1 ITEM 2 6357 Shows decimal form of user selected Modbus Register Address corresponding to 2nd Tilde marker MESSAGE DISP 1 ITEM 3 0 This item is not being used there is no corresponding Tilde marker in Top or Bottom lines MESSAGE DISP 1 ITEM 4 0 This item is not being used there is no correspon...

Page 177: ... device are not being received Direct input and output settings are similar to remote input and output settings The equivalent of the remote device name strings for direct inputs and outputs is the DIRECT OUTPUT DEVICE ID The DIRECT OUTPUT DEVICE ID setting identifies the relay in all direct output messages All UR series IEDs in a ring should have unique numbers assigned The IED ID is used to iden...

Page 178: ...gic operands flags bits to be exchanged Table 5 4 DIRECT INPUT AND OUTPUT DATA RATES MODULE CHANNEL SUPPORTED DATA RATES 74 Channel 1 64 kbps Channel 2 64 kbps 7L Channel 1 64 kbps 128 kbps Channel 2 64 kbps 128 kbps 7M Channel 1 64 kbps 128 kbps Channel 2 64 kbps 128 kbps 7P Channel 1 64 kbps 128 kbps Channel 2 64 kbps 128 kbps 7T Channel 1 64 kbps 128 kbps 7W Channel 1 64 kbps 128 kbps Channel 2...

Page 179: ... ID 1 DIRECT I O CH1 RING CONFIGURATION Yes DIRECT I O DATA RATE 128 kbps For UR series IED 2 DIRECT OUTPUT DEVICE ID 2 DIRECT I O CH1 RING CONFIGURATION Yes DIRECT I O DATA RATE 128 kbps The message delivery time is about 0 2 of power cycle in both ways at 128 kbps that is from device 1 to device 2 and from device 2 to device 1 Different communications cards can be selected by the user for this b...

Page 180: ... both rings are healthy IED 1 to IED 2 0 2 of power system cycle IED 1 to IED 3 0 4 of power system cycle IED 1 to IED 4 0 2 of power system cycle IED 2 to IED 3 0 2 of power system cycle IED 2 to IED 4 0 4 of power system cycle IED 3 to IED 4 0 2 of power system cycle If one ring is broken say TX2 RX2 the delivery times are as follows IED 1 to IED 2 0 2 of power system cycle IED 1 to IED 3 0 4 of...

Page 181: ... OUTPUT DEVICE ID 1 DIRECT I O CH1 RING CONFIGURATION Yes DIRECT I O CH2 RING CONFIGURATION Yes For UR series IED 3 DIRECT OUTPUT DEVICE ID 1 DIRECT I O CH1 RING CONFIGURATION Yes DIRECT I O CH2 RING CONFIGURATION Yes In this configuration the following delivery times are expected at 128 kbps IED 1 to IED 2 0 2 of power system cycle IED 1 to IED 3 0 5 of power system cycle IED 2 to IED 3 0 2 of po...

Page 182: ...CH1 2 PATH SETTINGS Ö PRODUCT SETUP ÖØ DIRECT I O ÖØ CRC ALARM CH1 2 The F35 checks integrity of the incoming direct input and output messages using a 32 bit CRC The CRC alarm function is available for monitoring the communication medium noise by tracking the rate of messages failing the CRC check The monitoring function counts all incoming messages including messages that failed the CRC check A s...

Page 183: ...uming the best case of only 1 bit error in a failed packet having 1 failed packet for every 63 received is about equal to a BER of 10 4 c UNRETURNED MESSAGES ALARM CH1 2 PATH SETTINGS Ö PRODUCT SETUP ÖØ DIRECT I O ÖØ UNRETURNED MESSAGES ALARM CH1 2 The F35 checks integrity of the direct input and output communication ring by counting unreturned messages In the ring configuration all messages origi...

Page 184: ...INAL 2 RELAY ID NUMBER In installa tions that use multiplexers or modems it is desirable to ensure that the data used by the relays protecting a given line is from the correct relays The teleprotection function performs this check by reading the message ID sent by transmit ting relays and comparing it to the programmed ID in the receiving relay This check is also used to block inputs if inad verte...

Page 185: ...is setting is defaulted to Not Programmed when at the factory The UNIT NOT PROGRAMMED self test error message is displayed until the relay is put into the Programmed state The RELAY NAME setting allows the user to uniquely identify a relay This name will appear on generated reports This name is also used to identify specific devices which are engaged in automatically sending receiving data over th...

Page 186: ...ion the ground CT primary rating must be entered To detect low level ground fault currents the sensitive ground input may be used In this case the sensitive ground CT primary rating must be entered Refer to chapter 3 for more details on CT connections Enter the rated CT primary current values For both 1000 5 and 1000 1 CTs the entry would be 1000 For correct opera tion the CT secondary rating must...

Page 187: ... 120 volt VT in a delta connec tion the secondary voltage would be 115 that is 13800 14400 120 For a wye connection the voltage value entered must be the phase to neutral voltage which would be 115 66 4 On a 14 4 kV system with a delta connection and a VT primary to secondary turns ratio of 14400 120 the voltage value entered would be 120 that is 14400 120 If the PHASE VT F5 CONNECTION is set to D...

Page 188: ... reference signal is not measurable at a given time the phase angles are not referenced The phase angle referencing is done via a phase locked loop which can synchronize independent UR series relays if they have the same AC signal reference These results in very precise correlation of time tagging in the event recorder between different UR series relays provided the relays have an IRIG B connectio...

Page 189: ...sturbance detector that detects any disturbance on the protected system The 50DD function is intended for use in conjunction with measuring elements blocking of current based elements to prevent maloperation as a result of the wrong settings and starting oscillography data capture A dis turbance detector is provided for each source The 50DD function responds to the changes in magnitude of the sequ...

Page 190: ... breaker and a half sys tem The following figure shows the arrangement of sources used to provide the functions required in this application and the CT VT inputs that are used to provide the data Figure 5 19 EXAMPLE USE OF SOURCES F 5 F 1 DSP Bank U 1 M 1 M 1 M 5 51BF 1 51BF 2 Source 4 87T 51P UR Relay A V V A W W Var Var Amps Source 1 Source 3 Volts Amps Amps Volts Amps Source 2 ...

Page 191: ...E Off Range FlexLogic operand MESSAGE BREAKER 1 ΦA 3P CLSD Off Range FlexLogic operand MESSAGE BREAKER 1 ΦA 3P OPND Off Range FlexLogic operand MESSAGE BREAKER 1 ΦB CLOSED Off Range FlexLogic operand MESSAGE BREAKER 1 ΦB OPENED Off Range FlexLogic operand MESSAGE BREAKER 1 ΦC CLOSED Off Range FlexLogic operand MESSAGE BREAKER 1 ΦC OPENED Off Range FlexLogic operand MESSAGE BREAKER 1 Toperate 0 070...

Page 192: ...r and used to track the breaker open or closed position If the mode is selected as 1 Pole the input mentioned above is used to track phase A and the BREAKER 1 ΦB and BREAKER 1 ΦC settings select operands to track phases B and C respectively BREAKER 1 ΦA 3P OPND This setting selects an operand usually a contact input that should be a normally closed 52 b status input to create a logic 1 when the br...

Page 193: ...NG Off 0 BREAKER 1 BLOCK OPEN FLEXLOGIC OPERANDS TRIP PHASE A TRIP PHASE B TRIP PHASE C TRIP 3 POLE SETTING Off 0 BREAKER 1 OPEN SETTING Enabled BREAKER 1 PUSHBUTTON CONTROL USER 2 OFF ON To open BRK1 Name SETTING Off 0 BREAKER 1 CLOSE FLEXLOGIC OPERAND AR CLOSE BKR 1 SETTING Off 0 BREAKER 1 BLOCK CLOSE SETTING MANUAL CLOSE RECAL1 TIME 0 FLEXLOGIC OPERAND BREAKER 1 MNL CLS FLEXLOGIC OPERAND BREAKE...

Page 194: ...Φ SETTING Off BREAKER 1 OPENED ΦB SETTING Off BREAKER 1 OPENED ΦC SETTING Off BREAKER 1 OUT OF SV SETTING BREAKER 1 Toperate 0 SETTING BREAKER 1 Toperate 0 SETTING BREAKER 1 Toperate 0 from breaker control logic sheet 1 827061AR BKR ENABLED FLEXLOGIC OPERAND BREAKER 1 CLOSED FLEXLOGIC OPERAND BREAKER 1 OPEN FLEXLOGIC OPERAND BREAKER 1 DISCREP FLEXLOGIC OPERAND BREAKER 1 TROUBLE FLEXLOGIC OPERAND B...

Page 195: ...sconnect switch 1 SWITCH 1 MODE This setting selects 3 pole mode where all disconnect switch poles are operated simultaneously or 1 pole mode where all disconnect switch poles are operated either independently or simultaneously SWITCH 1 SWITCH 1 FUNCTION Disabled Range Disabled Enabled MESSAGE SWITCH 1 NAME SW 1 Range up to 6 alphanumeric characters MESSAGE SWITCH 1 MODE 3 Pole Range 3 Pole 1 Pole...

Page 196: ...put that should be a normally closed 52 b status input to create a logic 1 when the disconnect switch is open If a separate 52 b contact input is not avail able then the inverted SWITCH 1 CLOSED status signal can be used SWITCH 1 ΦB CLOSED If the mode is selected as three pole this setting has no function If the mode is selected as single pole this input is used to track the disconnect switch phas...

Page 197: ...XLOGIC OPERAND SWITCH 1 CLOSED FLEXLOGIC OPERAND SWITCH 1 OPEN FLEXLOGIC OPERAND SWITCH 1 DISCREP FLEXLOGIC OPERAND SWITCH 1 TROUBLE FLEXLOGIC OPERAND SWITCH 1 BAD STATUS FLEXLOGIC OPERANDS SWITCH 1 ΦA BAD ST SWITCH 1 ΦA CLSD SWITCH 1 ΦA OPEN SWITCH 1 ΦA INTERM FLEXLOGIC OPERANDS SWITCH 1 Φ BAD ST B SWITCH 1 B Φ CLSD SWITCH 1 B Φ OPEN SWITCH 1 B Φ INTERM FLEXLOGIC OPERANDS SWITCH Φ BAD ST 1 C SWIT...

Page 198: ...e multiple of pickup of 1 that is 0 98 pu and 1 03 pu It is recommended to set the two times to a similar value otherwise the lin ear approximation may result in undesired behavior for the operating quantity that is close to 1 00 pu FLEXCURVE A FLEXCURVE A TIME AT 0 00 xPKP 0 ms Range 0 to 65535 ms in steps of 1 Table 5 5 FLEXCURVE TABLE RESET TIME MS RESET TIME MS OPERATE TIME MS OPERATE TIME MS ...

Page 199: ...ally at higher currents and where upstream and downstream pro tective devices have different operating characteristics The recloser curve configuration window shown below appears when the Initialize From EnerVista UR Setup setting is set to Recloser Curve and the Initialize FlexCurve button is clicked Figure 5 23 RECLOSER CURVE INITIALIZATION The multiplier and adder settings only affect the curve...

Page 200: ...00 ms see below Figure 5 24 COMPOSITE RECLOSER CURVE WITH HCT DISABLED With the HCT feature enabled the operating time reduces to 30 ms for pickup multiples exceeding 8 times pickup Figure 5 25 COMPOSITE RECLOSER CURVE WITH HCT ENABLED Configuring a composite curve with an increase in operating time at increased pickup multiples is not allowed If this is attempted the EnerVista UR Setup software g...

Page 201: ...LOSER CURVES GE113 GE120 GE138 AND GE142 GE104 1 1 2 1 5 2 2 5 3 4 5 6 7 8 9 10 12 15 20 0 01 0 02 0 05 0 1 0 2 0 5 1 2 CURRENT multiple of pickup TIME sec GE101 GE102 GE103 GE106 GE105 842723A1 CDR 1 1 2 1 5 2 2 5 3 4 5 6 7 8 9 10 12 15 20 0 05 0 1 0 2 0 5 1 2 5 10 20 50 CURRENT multiple of pickup TIME sec GE113 GE142 GE138 GE120 842725A1 CDR ...

Page 202: ...51 AND GE201 Figure 5 29 RECLOSER CURVES GE131 GE141 GE152 AND GE200 1 1 2 1 5 2 2 5 3 4 5 6 7 8 9 10 12 15 20 0 5 1 2 5 10 20 50 CURRENT multiple of pickup TIME sec GE134 GE151 GE140 GE137 GE201 842730A1 CDR 1 1 2 1 5 2 2 5 3 4 5 6 7 8 9 10 12 15 20 2 5 10 20 50 CURRENT multiple of pickup TIME sec GE131 GE200 GE152 GE141 842728A1 CDR ...

Page 203: ...VES GE116 GE117 GE118 GE132 GE136 AND GE139 842729A1 CDR 1 1 2 1 5 2 2 5 3 4 5 6 7 8 9 10 12 15 20 0 01 0 02 0 05 0 1 0 2 0 5 1 2 5 10 20 50 CURRENT multiple of pickup TIME sec GE133 GE163 GE162 GE161 GE165 GE164 842726A1 CDR 1 1 2 1 5 2 2 5 3 4 5 6 7 8 9 10 12 15 20 0 01 0 02 0 05 0 1 0 2 0 5 1 2 5 10 20 CURRENT multiple of pickup TIME sec GE116 GE132 GE118 GE117 GE139 GE136 ...

Page 204: ...122 Figure 5 33 RECLOSER CURVES GE119 GE135 AND GE202 842724A1 CDR 1 1 2 1 5 2 2 5 3 4 5 6 7 8 9 10 12 15 20 0 01 0 02 0 05 0 1 0 2 0 5 1 2 5 10 20 CURRENT multiple of pickup TIME sec GE121 GE114 GE112 GE122 GE107 GE115 GE111 842727A1 CDR 1 1 2 1 5 2 2 5 3 4 5 6 7 8 9 10 12 15 20 0 2 0 5 1 2 5 10 20 50 CURRENT multiple of pickup TIME sec GE119 GE202 GE135 ...

Page 205: ... contact output The state of the contact input can be displayed locally or viewed remotely via the communications facilities provided If a simple scheme where a contact input is used to block an element is desired this selection is made when programming the ele ment This capability also applies to the other features that set flags elements virtual inputs remote inputs schemes and human operators I...

Page 206: ... On Voltage is presently applied to the input external contact closed Off Cont Ip Off Voltage is presently not applied to the input external contact open Contact Output type Form A contact only Voltage On Cont Op 1 VOn Voltage exists across the contact Voltage Off Cont Op 1 VOff Voltage does not exists across the contact Current On Cont Op 1 IOn Current is flowing through the contact Current Off C...

Page 207: ... level on channel 1 or 2 ring configurations only ELEMENT Eight bit switch 8BIT SWITCH 1 BIT 0 8BIT SWITCH 1 BIT 1 8BIT SWITCH 1 BIT 2 8BIT SWITCH 1 BIT 3 8BIT SWITCH 1 BIT 4 8BIT SWITCH 1 BIT 5 8BIT SWITCH 1 BIT 6 8BIT SWITCH 1 BIT 7 Bit 0 of eight bit switch 1 asserted the least significant bit Bit 1 of eight bit switch 1 asserted Bit 2 of eight bit switch 1 asserted Bit 3 of eight bit switch 1 ...

Page 208: ...mparison value Counter 2 to Counter 8 Same set of operands as shown for Counter 1 ELEMENT Digital elements Dig Element 1 PKP Dig Element 1 OP Dig Element 1 DPO Digital Element 1 is picked up Digital Element 1 is operated Digital Element 1 is dropped out Dig Element 2 to Dig Element 48 Same set of operands as shown for Dig Element 1 ELEMENT FlexElements FxE 1 PKP FxE 1 OP FxE 1 DPO FlexElement 1 ha...

Page 209: ...ase B of phase time overcurrent 1 has picked up Phase C of phase time overcurrent 1 has picked up Phase A of phase time overcurrent 1 has operated Phase B of phase time overcurrent 1 has operated Phase C of phase time overcurrent 1 has operated Phase A of phase time overcurrent 1 has dropped out Phase B of phase time overcurrent 1 has dropped out Phase C of phase time overcurrent 1 has dropped out...

Page 210: ...nnect switch 1 is open Disconnect switch 1 has discrepancy Disconnect switch 1 trouble alarm SWITCH 2 Same set of operands as shown for SWITCH 1 ELEMENT Teleprotection channel tests TELEPRO CH1 FAIL TELEPRO CH2 FAIL TELEPRO CH1 ID FAIL TELEPRO CH2 ID FAIL TELEPRO CH1 CRC FAIL TELEPRO CH2 CRC FAIL TELEPRO CH1 PKT LOST TELEPRO CH2 PKT LOST Channel 1 failed Channel 2 failed The ID check for a peer re...

Page 211: ...ED is on Asserted when the front panel ALARM LED is on Asserted when the front panel PICKUP LED is on Asserted when the front panel VOLTAGE LED is on Asserted when the front panel CURRENT LED is on Asserted when the front panel FREQUENCY LED is on Asserted when the front panel OTHER LED is on Asserted when the front panel PHASE A LED is on Asserted when the front panel PHASE B LED is on Asserted w...

Page 212: ...e description in Chapter 7 Commands and targets See description in Chapter 7 Commands and targets See description in Chapter 7 Commands and targets See description in Chapter 7 Commands and targets See description in Chapter 7 Commands and targets See description in Chapter 7 Commands and targets See description in Chapter 7 Commands and targets See description in Chapter 7 Commands and targets Se...

Page 213: ...ifies the last entry in the list of processed FlexLogic parameters One shot POSITIVE ONE SHOT One shot that responds to a positive going edge A one shot refers to a single input gate that generates a pulse in response to an edge on the input The output from a one shot is True positive for only one pass through the FlexLogic equation There is a maximum of 64 one shots NEGATIVE ONE SHOT One shot tha...

Page 214: ...ND 16 17 through 25 to AND 9 and the outputs from these two gates to AND 2 Inspect each operator between the initial operands and final virtual outputs to determine if the output from the operator is used as an input to more than one following operator If so the operator output must be assigned as a virtual output For the example shown above the output of the AND gate is used as an input to both O...

Page 215: ...sier to start at the output end of the equation and work back towards the input as shown in the following steps It is also recommended to list operator inputs from bottom to top For demonstration the final output will be arbitrarily identified as parameter 99 and each preceding parameter decremented by one in turn Until accustomed to using FlexLogic it is suggested that a worksheet with a series o...

Page 216: ...he set of parame ters into a logic diagram The result of this process is shown below which is compared to the logic for virtual output 3 dia gram as a check Figure 5 40 FLEXLOGIC EQUATION FOR VIRTUAL OUTPUT 3 6 Repeating the process described for virtual output 3 select the FlexLogic parameters for Virtual Output 4 99 The final output of the equation is virtual output 4 which is parameter Virt Op ...

Page 217: ... cases where a lot of processing is required to perform logic this may be difficult to achieve but in most cases will not cause problems as all logic is calculated at least four times per power frequency cycle The possibility of a problem caused by sequential processing emphasizes the necessity to test the performance of FlexLogic before it is placed in service In the following equation virtual ou...

Page 218: ...QUATION EDITOR PATH SETTINGS ÖØ FLEXLOGIC Ö FLEXLOGIC EQUATION EDITOR There are 512 FlexLogic entries available numbered from 1 to 512 with default END entry settings If a Disabled Ele ment is selected as a FlexLogic entry the associated state flag will never be set to 1 The key may be used when editing FlexLogic equations from the keypad to quickly scan through the major parameter types 5 4 6 FLE...

Page 219: ...GE Multilin F35 Multiple Feeder Protection System 5 97 5 SETTINGS 5 4 FLEXLOGIC 5 TIMER 1 DROPOUT DELAY Sets the time delay to dropout If a dropout delay is not required set this function to 0 ...

Page 220: ...MENT 1 NAME FxE1 Range up to 6 alphanumeric characters MESSAGE FLEXELEMENT 1 IN Off Range Off any analog actual value parameter MESSAGE FLEXELEMENT 1 IN Off Range Off any analog actual value parameter MESSAGE FLEXELEMENT 1 INPUT MODE Signed Range Signed Absolute MESSAGE FLEXELEMENT 1 COMP MODE Level Range Level Delta MESSAGE FLEXELEMENT 1 DIRECTION Over Range Over Under MESSAGE FLEXELEMENT 1 PICKU...

Page 221: ...ple applications for the Absolute setting include monitoring the angular difference between two phasors with a symmetrical limit angle in both directions monitoring power regardless of its direction or monitoring a trend regardless of whether the signal increases of decreases The element responds directly to its operating signal as defined by the FLEXELEMENT 1 IN FLEXELEMENT 1 IN and FLEX ELEMENT ...

Page 222: ...NT 1 PKP FLEXELEMENT DIRECTION Over PICKUP HYSTERESIS of PICKUP FlexElement 1 OpSig FLEXELEMENT 1 PKP FLEXELEMENT DIRECTION Under PICKUP HYSTERESIS of PICKUP 842705A1 CDR 842706A2 CDR FlexElement 1 OpSig FLEXELEMENT 1 PKP FLEXELEMENT DIRECTION Over FLEXELEMENT INPUT MODE Signed FlexElement 1 OpSig FLEXELEMENT 1 PKP FLEXELEMENT DIRECTION Over FLEXELEMENT INPUT MODE Absolute FlexElement 1 OpSig FLEX...

Page 223: ...alue as shown in the FlexElement direction pickup and hysteresis dia gram The FLEXELEMENT 1 DT UNIT setting specifies the time unit for the setting FLEXELEMENT 1 dt This setting is applicable only if FLEXELEMENT 1 COMP MODE is set to Delta The FLEXELEMENT 1 DT setting specifies duration of the time interval for the rate of change mode of operation This setting is applicable only if FLEXELEMENT 1 C...

Page 224: ...erted the specified FlexLogic operand resets Latch 1 Figure 5 45 NON VOLATILE LATCH OPERATION TABLE N 1 to 16 AND LOGIC LATCH 1 LATCH 1 FUNCTION Disabled Range Disabled Enabled MESSAGE LATCH 1 TYPE Reset Dominant Range Reset Dominant Set Dominant MESSAGE LATCH 1 SET Off Range FlexLogic operand MESSAGE LATCH 1 RESET Off Range FlexLogic operand MESSAGE LATCH 1 TARGET Self reset Range Self reset Latc...

Page 225: ...l multiplier setting allows selection of a multiple of the base curve shape where the time dial multiplier 1 with the curve shape CURVE setting Unlike the electromechanical time dial equivalent operate times are directly proportional to the time multiplier TD MULTIPLIER setting value For example all times for a multiplier of 10 are 10 times the multiplier 1 or base curve values Setting the multipl...

Page 226: ...87 14 587 8 007 5 187 3 710 2 837 2 277 1 897 1 626 6 0 136 090 57 130 21 880 12 010 7 780 5 564 4 255 3 416 2 845 2 439 8 0 181 454 76 174 29 174 16 014 10 374 7 419 5 674 4 555 3 794 3 252 10 0 226 817 95 217 36 467 20 017 12 967 9 274 7 092 5 693 4 742 4 065 IEEE VERY INVERSE 0 5 8 090 3 514 1 471 0 899 0 654 0 526 0 450 0 401 0 368 0 345 1 0 16 179 7 028 2 942 1 798 1 308 1 051 0 900 0 802 0 7...

Page 227: ...80 4 280 3 837 3 528 3 297 3 116 2 971 IEC CURVE B 0 05 1 350 0 675 0 338 0 225 0 169 0 135 0 113 0 096 0 084 0 075 0 10 2 700 1 350 0 675 0 450 0 338 0 270 0 225 0 193 0 169 0 150 0 20 5 400 2 700 1 350 0 900 0 675 0 540 0 450 0 386 0 338 0 300 0 40 10 800 5 400 2 700 1 800 1 350 1 080 0 900 0 771 0 675 0 600 0 60 16 200 8 100 4 050 2 700 2 025 1 620 1 350 1 157 1 013 0 900 0 80 21 600 10 800 5 4...

Page 228: ... 1 488 1 239 1 060 0 926 IAC VERY INVERSE 0 5 1 451 0 656 0 269 0 172 0 133 0 113 0 101 0 093 0 087 0 083 1 0 2 901 1 312 0 537 0 343 0 266 0 227 0 202 0 186 0 174 0 165 2 0 5 802 2 624 1 075 0 687 0 533 0 453 0 405 0 372 0 349 0 331 4 0 11 605 5 248 2 150 1 374 1 065 0 906 0 810 0 745 0 698 0 662 6 0 17 407 7 872 3 225 2 061 1 598 1 359 1 215 1 117 1 046 0 992 8 0 23 209 10 497 4 299 2 747 2 131 ...

Page 229: ...om instanta neous to 600 00 seconds in steps of 10 ms EQ 5 14 EQ 5 15 where T Operate Time sec TDM Multiplier setting I Input Current Ipickup Pickup Current setting TRESET Reset Time in seconds assuming energy capacity is 100 and RESET Timed RECLOSER CURVES The F35 uses the FlexCurve feature to facilitate programming of 41 recloser curves Please refer to the FlexCurve sec tion in this chapter for ...

Page 230: ...reduced by a voltage restraint feature when enabled This is accom plished via the multipliers Mvr corresponding to the phase phase voltages of the voltage restraint characteristic curve see the figure below the pickup level is calculated as Mvr times the PHASE TOC1 PICKUP setting If the voltage restraint feature is disabled the pickup level always remains at the setting value PHASE TOC1 PHASE TOC1...

Page 231: ...OCK C PHASE TOC1 BLOCK B PHASE TOC1 VOLT RESTRAINT PHASE TOC1 A PKP PHASE TOC1 A DPO PHASE TOC1 A OP PHASE TOC1 B PKP PHASE TOC1 B DPO PHASE TOC1 B OP PHASE TOC1 C PKP PHASE TOC1 C DPO PHASE TOC1 C OP PHASE TOC1 PKP PHASE TOC1 OP PHASE TOC1 SOURCE PHASE TOC1 RESET PHASE TOC1 CURVE PHASE TOC1 PICKUP PHASE TOC1 INPUT IA Seq ABC Seq ACB Set Multiplier Set Multiplier Set Multiplier Set Pickup Multipli...

Page 232: ...s of 0 01 MESSAGE PHASE IOC1 RESET DELAY 0 00 s Range 0 00 to 600 00 s in steps of 0 01 MESSAGE PHASE IOC1 BLOCK A Off Range FlexLogic operand MESSAGE PHASE IOC1 BLOCK B Off Range FlexLogic operand MESSAGE PHASE IOC1 BLOCK C Off Range FlexLogic operand MESSAGE PHASE IOC1 TARGET Self reset Range Self reset Latched Disabled MESSAGE PHASE IOC1 EVENTS Disabled Range Disabled Enabled IA PICKUP SETTING ...

Page 233: ...nstan taneous and the element is blocked the time accumulator will be cleared immediately Figure 5 49 NEUTRAL TIME OVERCURRENT 1 SCHEME LOGIC NEUTRAL TOC1 NEUTRAL TOC1 FUNCTION Disabled Range Disabled Enabled MESSAGE NEUTRAL TOC1 SIGNAL SOURCE SRC 1 Range SRC 1 SRC 2 SRC 3 SRC 4 SRC 5 SRC 6 MESSAGE NEUTRAL TOC1 INPUT Phasor Range Phasor RMS MESSAGE NEUTRAL TOC1 PICKUP 1 000 pu Range 0 000 to 30 00...

Page 234: ...phase faults The positive sequence restraint must be considered when testing for pickup accuracy and response time multiple of pickup The operating quantity depends on how test currents are injected into the relay single phase injection three phase pure zero sequence injection Figure 5 50 NEUTRAL IOC1 SCHEME LOGIC NEUTRAL IOC1 NEUTRAL IOC1 FUNCTION Disabled Range Disabled Enabled MESSAGE NEUTRAL I...

Page 235: ...l is from 0 02 to 46 times the CT rating This channel may be also equipped with a sensitive input The conversion range of a sensitive channel is from 0 002 to 4 6 times the CT rating Figure 5 51 GROUND TOC1 SCHEME LOGIC GROUND TOC1 GROUND TOC1 FUNCTION Disabled Range Disabled Enabled MESSAGE GROUND TOC1 SIGNAL SOURCE SRC 1 Range SRC 1 SRC 2 SRC 3 SRC 4 SRC 5 SRC 6 MESSAGE GROUND TOC1 INPUT Phasor ...

Page 236: ... is from 0 002 to 4 6 times the CT rating Figure 5 52 GROUND IOC1 SCHEME LOGIC GROUND IOC1 GROUND IOC1 FUNCTION Disabled Range Disabled Enabled MESSAGE GROUND IOC1 SIGNAL SOURCE SRC 1 Range SRC 1 SRC 2 SRC 3 SRC 4 SRC 5 SRC 6 MESSAGE GROUND IOC1 PICKUP 1 000 pu Range 0 000 to 30 000 pu in steps of 0 001 MESSAGE GROUND IOC1 PICKUP DELAY 0 00 s Range 0 00 to 600 00 s in steps of 0 01 MESSAGE GROUND ...

Page 237: ...e used to block the functioning of other elements through the block feature of those elements Source Transfer Schemes In the event of an undervoltage a transfer signal may be generated to transfer a load from its normal source to a standby or emergency power source The undervoltage elements can be programmed to have a definite time delay characteristic The definite time curve oper ates when the vo...

Page 238: ...s shown below EQ 5 17 where T operating time D undervoltage delay setting D 0 00 operates instantaneously V secondary voltage applied to the relay Vpickup pickup level Figure 5 53 INVERSE TIME UNDERVOLTAGE CURVES At 0 of pickup the operating time equals the UNDERVOLTAGE DELAY setting T D 1 V Vpickup 842788A1 CDR of voltage pickup Time seconds NOTE ...

Page 239: ... Ground Phase to Phase MESSAGE PHASE UV1 PICKUP 1 000 pu Range 0 000 to 3 000 pu in steps of 0 001 MESSAGE PHASE UV1 CURVE Definite Time Range Definite Time Inverse Time MESSAGE PHASE UV1 DELAY 1 00 s Range 0 00 to 600 00 s in steps of 0 01 MESSAGE PHASE UV1 MINIMUM VOLTAGE 0 100 pu Range 0 000 to 3 000 pu in steps of 0 001 MESSAGE PHASE UV1 BLOCK Off Range FlexLogic operand MESSAGE PHASE UV1 TARG...

Page 240: ... A B or C or be used as a definite time element The NEUTRAL OV1 PICKUP DELAY setting applies only if the NEUTRAL OV1 CURVE setting is Definite time The source assigned to this element must be configured for a phase VT VT errors and normal voltage unbalance must be considered when setting this element This function requires the VTs to be wye connected Figure 5 55 NEUTRAL OVERVOLTAGE1 SCHEME LOGIC N...

Page 241: ...istics The operating characteristics and equations for both definite and inverse time delay are as for the phase undervoltage element The element resets instantaneously The minimum voltage setting selects the operating voltage below which the element is blocked Figure 5 56 AUXILIARY UNDERVOLTAGE SCHEME LOGIC AUXILIARY UV1 AUX UV1 FUNCTION Disabled Range Disabled Enabled MESSAGE AUX UV1 SIGNAL SOUR...

Page 242: ... AUXILIARY OV1 AUX OV1 FUNCTION Disabled Range Disabled Enabled MESSAGE AUX OV1 SIGNAL SOURCE SRC 1 Range SRC 1 SRC 2 SRC 3 SRC 4 SRC 5 SRC 6 MESSAGE AUX OV1 PICKUP 0 300 pu Range 0 000 to 3 000 pu in steps of 0 001 MESSAGE AUX OV1 PICKUP DELAY 1 00 s Range 0 00 to 600 00 s in steps of 0 01 MESSAGE AUX OV1 RESET DELAY 1 00 s Range 0 00 to 600 00 s in steps of 0 01 MESSAGE AUX OV1 BLOCK Off Range F...

Page 243: ... for group 1 the default active group because group 1 automatically becomes active if no other group is active The SETTING GROUP 1 NAME to SETTING GROUP 6 NAME settings allows to user to assign a name to each of the six settings groups Once programmed this name will appear on the second line of the GROUPED ELEMENTS Ö SETTING GROUP 1 6 menu display The relay can be set up via a FlexLogic equation t...

Page 244: ...out Range Time out Acknowledge MESSAGE SELECTOR 1 ACK Off Range FlexLogic operand MESSAGE SELECTOR 1 3BIT A0 Off Range FlexLogic operand MESSAGE SELECTOR 1 3BIT A1 Off Range FlexLogic operand MESSAGE SELECTOR 1 3BIT A2 Off Range FlexLogic operand MESSAGE SELECTOR 1 3BIT MODE Time out Range Time out Acknowledge MESSAGE SELECTOR 1 3BIT ACK Off Range FlexLogic operand MESSAGE SELECTOR 1 POWER UP MODE...

Page 245: ...ll not take place and an alarm will be set SELECTOR 1 STEP UP This setting specifies a control input for the selector switch The switch is shifted to a new position at each rising edge of this signal The position changes incrementally wrapping up from the last SELECTOR 1 FULL RANGE to the first position 1 Consecutive pulses of this control operand must not occur faster than every 50 ms After each ...

Page 246: ...the SELEC TOR TIME OUT setting after the last activity of the three bit control inputs Note that the stepping up control input and three bit control input have independent acknowledging signals SELECTOR 1 ACK and SELECTOR 1 3BIT ACK accord ingly SELECTOR 1 POWER UP MODE This setting specifies the element behavior on power up of the relay When set to Restore the last position of the selector stored...

Page 247: ...n these diagrams T represents a time out setting Figure 5 59 TIME OUT MODE 842737A1 CDR STEP UP 3BIT A0 3BIT A1 3BIT A2 POS 1 POS 2 POS 3 POS 4 POS 5 POS 6 POS 7 BIT 0 BIT 1 BIT 2 pre existing position 2 changed to 4 with a pushbutton changed to 1 with a 3 bit input changed to 2 with a pushbutton T T T T changed to 7 with a 3 bit input STP ALARM BIT ALARM ALARM ...

Page 248: ...should synchronize the setting group to the three bit control input Make the following changes to setting group control in the SETTINGS ÖØ CONTROL ELEMENTS Ö SETTING GROUPS menu SETTING GROUPS FUNCTION Enabled GROUP 4 ACTIVATE ON SELECTOR 1 POS 4 SETTING GROUPS BLK Off GROUP 5 ACTIVATE ON Off GROUP 2 ACTIVATE ON SELECTOR 1 POS 2 GROUP 6 ACTIVATE ON Off GROUP 3 ACTIVATE ON SELECTOR 1 POS 3 Make the...

Page 249: ...ollowing changes in the SETTINGS Ö PRODUCT SETUP ÖØ USER PROGRAMMABLE PUSHBUTTONS Ö USER PUSHBUTTON 1 menu PUSHBUTTON 1 FUNCTION Self reset PUSHBUTTON 1 DROP OUT TIME 0 10 s The logic for the selector switch is shown below Figure 5 61 SELECTOR SWITCH LOGIC 842012A2 CDR step up acknowledge 3 bit position out ON FLEXLOGIC OPERANDS SELECTOR 1 POS 1 SELECTOR 1 POS 2 SELECTOR 1 POS 3 SELECTOR 1 POS 4 S...

Page 250: ...r below the minimum voltage current setting The UNDERFREQ 1 MIN VOLT AMP setting selects the minimum per unit voltage or current level required to allow the underfre quency element to operate This threshold is used to prevent an incorrect operation because there is no signal to measure This UNDERFREQ 1 PICKUP setting is used to select the level at which the underfrequency element is to pickup For ...

Page 251: ...R1 MNL RST FRM LO Off Range FlexLogic operand MESSAGE AR1 RESET LOCKOUT IF BREAKER CLOSED Off Range Off On MESSAGE AR1 RESET LOCKOUT ON MANUAL CLOSE Off Range Off On MESSAGE AR1 BKR CLOSED Off Range FlexLogic operand MESSAGE AR1 BKR OPEN Off Range FlexLogic operand MESSAGE AR1 BLK TIME UPON MNL CLS 10 000 s Range 0 00 to 655 35 s in steps of 0 01 MESSAGE AR1 DEAD TIME 1 1 000 s Range 0 00 to 655 3...

Page 252: ...scheme is initiated provided the circuit breaker is in the closed state before protection operation The reclose in progress RIP is set when a reclosing cycle begins following a reclose initiate signal Once the cycle is suc cessfully initiated the RIP signal will seal in and the scheme will continue through its sequence until one of the following conditions is satisfied The close signal is issued w...

Page 253: ... scheme to reset from Lockout when the breaker is manually closed regardless if the breaker remains closed or not This setting overrides the previ ous setting AR1 RESET LOCKOUT IF BREAKER CLOSED AR1 BLK TIME UPON MNL CLS The autoreclose scheme can be disabled for a programmable time delay after the associated circuit breaker is manually closed This prevents reclosing onto a fault after a manual cl...

Page 254: ...0 On 1 On 1 Off 0 Off 0 Off 0 Disable 0 AR1 ENABLED AR1 DISABLED AR1 BLK FROM MAN CLS Enabled Default Disabled Default AR1 RIP AR1 LO LO AND AND AND AND OR O O O O O O O O Off 0 Off 0 SETTING SETTING SETTING SETTING SETTING SETTING SETTING SETTING SETTING SETTING SETTING AR1 BLK TIME UPON MNL CLOSE AR1 RESET LOCKOUT DELAY AR1 DEAD TIME 4 AR1 DELAY 1 AR1 DELAY 2 AR1 ADD DELAY 1 AR1 ADD DELAY 2 Shot...

Page 255: ... CNT 3 AR1 SHOT CNT 1 AR1 SHOT CNT 0 Increment shot counter Shot cnt 2 Shot cnt 1 Shot cnt 0 Reset shot counter Shot cnt 3 AUTORECLOSE 1 SHOT COUNT 0 1 2 3 4 AR1 CLOSE AND AND AND AND AND AND AND AND 100 ms AND OR OR OR OR OR OR OR OR SETTING SETTING SETTING SETTING SETTING AR1 RESET TIME AR1 MAX NUMBER OF SHOTS AR1 REDUCE MAX TO 1 AR1 REDUCE MAX TO 2 AR1 REDUCE MAX TO 3 MAX 1 Off 0 Off 0 Off 0 MA...

Page 256: ... SEPARATE OPENING TIME CLOSING TIME PROT TIME OPENING TIME PROT TIME ARC EXTINGUISHES ARC EXTINGUISHES CLOSE COMMAND CLOSED COMMAND BKR CLOSED AR INITIATE AR GOES TO LOCKOUT SHOT COUNT MAX RESET FROM LOCKOUT AR ENABLED LOCKOUT RIP INCOMPL SEQ TIMING RESET TIMER IS TIMING INCOMPLETE SEQUENCE IS TIMING DEAD TIME RECLOSE IN PROGRESS CONTACTS CLOSE TRIP COMMAND CONTACTS SEPARATE BKR OPEN AR ENABLED AU...

Page 257: ...6 DIGITAL ELEMENT SCHEME LOGIC CIRCUIT MONITORING APPLICATIONS Some versions of the digital input modules include an active voltage monitor circuit connected across form A contacts The voltage monitor circuit limits the trickle current through the output circuit see technical specifications for form A DIGITAL ELEMENT 1 DIGITAL ELEMENT 1 FUNCTION Disabled Range Disabled Enabled MESSAGE DIG ELEM 1 N...

Page 258: ...ent of the breaker trip coil If the circuit presents a high resis tance the trickle current will fall below the monitor threshold and an alarm would be declared In most breaker control circuits the trip coil is connected in series with a breaker auxiliary contact which is open when the breaker is open see diagram below To prevent unwanted alarms in this situation the trip circuit monitoring logic ...

Page 259: ...chieved by connecting a suitable resistor see figure below across the auxiliary contact in the trip circuit In this case it is not required to supervise the monitoring circuit with the breaker position the BLOCK setting is selected to Off In this case the settings are as follows EnerVista UR Setup example shown Figure 5 68 TRIP CIRCUIT EXAMPLE 2 Trip Coil 52a V I H1a H1c H1b UR Relay Form A V Volt...

Page 260: ... equal to EQL or less than LO the set value COUNTER 1 UP Selects the FlexLogic operand for incrementing the counter If an enabled UP input is received when the accumulated value is at the limit of 2 147 483 647 counts the counter will rollover to 2 147 483 648 COUNTER 1 DOWN Selects the FlexLogic operand for decrementing the counter If an enabled DOWN input is received when the accumulated value i...

Page 261: ...rand for capturing freezing the accumulated count value into a separate register with the date and time of the operation and resetting the count to 0 COUNTER 1 FREEZE COUNT Selects the FlexLogic operand for capturing freezing the accumulated count value into a separate register with the date and time of the operation and continuing counting The present accumulated value and captured frozen value w...

Page 262: ...ttings specify FlexLogic operands that constitute the second B input of the switch These operands are routed to the output operands if the control input is in the On position 8BIT SW 1 CONTROL This setting specifies FlexLogic operands to control the routing between the A and B inputs of the switch If the control operand is in the Off state the first A input is switched to the output If the control...

Page 263: ...W 1 ARG B3 Off 0 8BIT SW 1 ARG A4 Off 0 8BIT SW 1 ARG B4 Off 0 8BIT SW 1 ARG A5 Off 0 8BIT SW 1 ARG B5 Off 0 8BIT SW 1 ARG A6 Off 0 8BIT SW 1 ARG B6 Off 0 8BIT SW 1 ARG A7 Off 0 8BIT SW 1 ARG B7 Off 0 FLEXLOGIC OPERAND 8BIT SWITCH 1 BIT 1 FLEXLOGIC OPERAND 8BIT SWITCH 1 BIT 2 FLEXLOGIC OPERAND 8BIT SWITCH 1 BIT 3 FLEXLOGIC OPERAND 8BIT SWITCH 1 BIT 4 FLEXLOGIC OPERAND 8BIT SWITCH 1 BIT 5 FLEXLOGIC...

Page 264: ...RCING CURRENT See page 5 143 MESSAGE BREAKER 3 ARCING CURRENT See page 5 143 MESSAGE BREAKER 4 ARCING CURRENT See page 5 143 MESSAGE BREAKER 5 ARCING CURRENT See page 5 143 MESSAGE BREAKER 6 ARCING CURRENT See page 5 143 MESSAGE INCIPIENT FAULT 1 See page 5 145 MESSAGE INCIPIENT FAULT 2 See page 5 145 MESSAGE INCIPIENT FAULT 3 See page 5 145 MESSAGE INCIPIENT FAULT 4 See page 5 145 MESSAGE INCIPIE...

Page 265: ...t duration is defined as a time between operation of the disturbance detector occurring before initiation of this feature and reset of an internal low set overcurrent function Cor rection is implemented to account for a non zero reset time of the overcurrent function Breaker arcing currents and fault duration values are available under the ACTUAL VALUES ÖØ RECORDS ÖØ MAINTENANCE Ö BREAKER 1 6 menu...

Page 266: ...1 ARCING AMP BLOCK BREAKER 1 ARCING AMP INIT A BREAKER 1 ARCING AMP INIT B BREAKER 1 ARCING AMP INIT C BREAKER 1 ARCING AMP LIMIT CLEAR BREAKER 1 ARCING AMPS BKR 1 ARCING AMP A BKR 1 OPERATING TIME A BKR 1 OPERATING TIME B BKR 1 OPERATING TIME C BKR 1 OPERATING TIME BKR 1 ARCING AMP B BKR 1 ARCING AMP C BKR1 ARC OP BKR1 ARC DPO BREAKER 1 ARCING AMP SOURCE IA IB IC Off 0 Off 0 Off 0 Off 0 NO 0 YES ...

Page 267: ... cycles later when the incip ient fault pattern is confirmed and therefore detected The following figure illustrates a recorded field case of an incipient phase B fault The top portion of the figure shows the raw A B and C currents The bottom portion shows the neutral current blue and reveals the fault period from under the load and the superimposed phase B current red The superimposed current sho...

Page 268: ...minal current INCIPNT FLT 1 MODE There are two modes of operation available for the incipient cable fault detector element In the Number of counts mode a trip will be initiated only after the selected number of faults is detected In the Counts per window mode a trip will be initiated only after the selected number of faults is detected within the time specified by the INCIPNT FLT 1 DETECT WINDOW s...

Page 269: ...RIP BUS 1 RESET Off Range FlexLogic operand MESSAGE TRIP BUS 1 TARGET Self reset Range Self reset Latched Disabled MESSAGE TRIP BUS 1 EVENTS Disabled Range Enabled Disabled Detection logic SETTING Enabled Disabled INCIPIENT FAULT 1 FUNCTION SETTING OFF INCIPIENT FAULT 1 BLOCK SETTING IA IB INCIPIENT FAULT 1 SOURCE IC IN AND SETTING INCIPIENT FAULT 1 PICKUP RUN PICKUP where is 2 cycles old Imag I I...

Page 270: ... TRIP BUS FIELDS IN THE PROTECTION SUMMARY The following settings are available TRIP BUS 1 BLOCK The trip bus output is blocked when the operand assigned to this setting is asserted TRIP BUS 1 PICKUP DELAY This setting specifies a time delay to produce an output depending on how output is used TRIP BUS 1 RESET DELAY This setting specifies a time delay to reset an output command The time delay shou...

Page 271: ...NPUT 1 Off TRIP BUS 1 INPUT 16 OR SETTINGS Enabled TRIP BUS 1 FUNCTION Off TRIP BUS 1 BLOCK AND AND Latch S R Non volatile set dominant SETTINGS Enabled TRIP BUS 1 LATCHING Off TRIP BUS 1 RESET FLEXLOGIC OPERAND TRIP BUS 1 PKP OR SETTINGS TRIP BUS 1 PICKUP DELAY TRIP BUS 1 RESET DELAY TPKP TRST FLEXLOGIC OPERAND RESET OP FLEXLOGIC OPERAND TRIP BUS 1 OP 842023A1 CDR ...

Page 272: ...r a user settable debounce time in order for the F35 to validate the new contact state In the figure below the debounce time is set at 2 5 ms thus the 6th sample in a row validates the change of state mark no 1 in the diagram Once validated de bounced the contact input asserts a corresponding FlexLogic operand and logs an event as per user setting A time stamp of the first sample in the sequence t...

Page 273: ...to filter the LOW HIGH marks no 1 2 3 and 4 in the figure below and HIGH LOW marks no 5 6 7 and 8 below transitions Figure 5 77 INPUT CONTACT DEBOUNCING MECHANISM AND TIME STAMPING SAMPLE TIMING Contact inputs are isolated in groups of four to allow connection of wet contacts from different voltage sources for each group The CONTACT INPUT THRESHOLDS determine the minimum voltage required to detect...

Page 274: ...tput operand will be set to on for only one evaluation of the FlexLogic equations and then return to off If set to Latched the virtual input sets the state of the output operand to the same state as the most recent received input The self reset operating mode generates the output operand for a single evaluation of the FlexLogic equations If the operand is to be used anywhere other than internally ...

Page 275: ...ed to prevent damage to the less robust initiating contact This can be done by monitoring an auxiliary contact on the breaker which opens when the breaker has tripped but this scheme is subject to incorrect oper ation caused by differences in timing between breaker auxiliary contact change of state and interruption of current in the trip circuit The most dependable protection of the initiating con...

Page 276: ... the contact response under conflicting control inputs that is when both the OPERATE and RESET signals are applied With both control inputs applied simultaneously the contact will close if set to Operate dominant and will open if set to Reset dominant Application Example 1 A latching output contact H1a is to be controlled from two user programmable pushbuttons buttons number 1 and 2 The following ...

Page 277: ...ista UR Setup example shown Program the Latching Outputs by making the following changes in the SETTINGS ÖØ INPUTS OUTPUTS ÖØ CONTACT OUT PUTS Ö CONTACT OUTPUT H1a menu assuming an H4L module OUTPUT H1a OPERATE VO1 OUTPUT H1a RESET VO2 5 7 4 VIRTUAL OUTPUTS PATH SETTINGS ÖØ INPUTS OUTPUTS ÖØ VIRTUAL OUTPUTS Ö VIRTUAL OUTPUT 1 96 There are 96 virtual outputs that may be assigned via FlexLogic If no...

Page 278: ...on provides 32 of the 96 available UserSt bit pairs The IEC 61850 specification includes features that are used to cope with the loss of communication between transmitting and receiving devices Each transmitting device will send a GSSE GOOSE message upon a successful power up when the state of any included point changes or after a specified interval the default update time if a change of state has...

Page 279: ...hrough DNA 32 and UserSt 1 through UserSt 32 The function of DNA inputs is defined in the IEC 61850 specification and is presented in the IEC 61850 DNA Assignments table in the Remote outputs section The function of UserSt inputs is defined by the user selection of the FlexLogic operand whose state is represented in the GSSE GOOSE message A user must program a DNA point from the appropriate FlexLo...

Page 280: ...y the state of a specific FlexLogic oper and The above operand setting represents a specific DNA function as shown in the following table to be transmitted b USERST BIT PAIRS PATH SETTINGS ÖØ INPUTS OUTPUTS ÖØ REMOTE OUTPUTS UserSt BIT PAIRS Ö REMOTE OUTPUTS UserSt 1 32 BIT PAIR Remote outputs 1 to 32 originate as GSSE GOOSE messages to be transmitted to remote devices Each digital point in the me...

Page 281: ...e DIRECT INPUT 1 DEVICE ID represents the source of direct input 1 The specified direct input is driven by the device identified here The DIRECT INPUT 1 BIT NUMBER is the bit number to extract the state for direct input 1 Direct Input 1 is driven by the bit identified as DIRECT INPUT 1 BIT NUMBER This corresponds to the direct output number of the sending device The DIRECT INPUT 1 DEFAULT STATE re...

Page 282: ...gic requirements The two IEDs are connected via single channel digital communication cards as shown below Figure 5 79 INPUT AND OUTPUT EXTENSION VIA DIRECT INPUTS AND OUTPUTS Assume contact input 1 from UR IED 2 is to be used by UR IED 1 The following settings should be applied Direct Input 5 and bit number 12 are used as an example The Cont Ip 1 On operand of UR IED 2 is now available in UR IED 1...

Page 283: ...R 3 DIRECT INPUT 8 DEFAULT STATE select On for security select Off for dependability DIRECT INPUT 9 DEVICE ID 4 DIRECT INPUT 9 BIT NUMBER 3 DIRECT INPUT 9 DEFAULT STATE select On for security select Off for dependability Now the three blocking signals are available in UR IED 1 as DIRECT INPUT 7 ON DIRECT INPUT 8 ON and DIRECT INPUT 9 ON Upon losing communications or a device the scheme is inclined...

Page 284: ...PUT 5 DEVICE ID 1 DIRECT INPUT 5 BIT NUMBER 2 DIRECT INPUT 6 DEVICE ID 3 DIRECT INPUT 6 BIT NUMBER 2 DIRECT OUT 2 OPERAND HYB POTT TX1 DIRECT OUT 3 OPERAND DIRECT INPUT 5 forward a message from 1 to 3 DIRECT OUT 4 OPERAND DIRECT INPUT 6 forward a message from 3 to 1 Signal flow between the three IEDs is shown in the figure below Figure 5 83 SIGNAL FLOW FOR DIRECT INPUT AND OUTPUT EXAMPLE 3 In thre...

Page 285: ...lity The teleprotection function must be enabled to utilize the inputs b TELEPROTECTION INPUTS PATH SETTINGS ÖØ INPUTS OUTPUTS ÖØ TELEPROTECTION Ö TELEPROT INPUTS Setting the TELEPROT INPUT DEFAULT setting to On defaults the input to logic 1 when the channel fails A value of Off defaults the input to logic 0 when the channel fails The Latest On and Latest Off values freeze the input in case of los...

Page 286: ... TELEPROT OUTPUT 2 1 Off Range FlexLogic operand MESSAGE TELEPROT OUTPUT 2 2 Off Range FlexLogic operand MESSAGE TELEPROT OUTPUT 2 16 Off Range FlexLogic operand 842750A2 CDR TELEPROT OUTPUT 1 1 same for 1 2 1 16 TELEPROT INPUT 1 1 DEFAULT same for 1 2 1 16 Off Flexlogic Operand TELEPRO INPUT 1 1 On same for 1 2 1 16 UR 1 Teleprotection I O Enabled Communication channel 1 On Off ACTUAL VALUES CHAN...

Page 287: ...ing GOOSE analog input value GOOSE ANALOG 1 PU This setting specifies the per unit base factor when using the GOOSE analog input FlexAna log values in other F35 features such as FlexElements The base factor is applied to the GOOSE analog input FlexAnalog quantity to normalize it to a per unit quantity The base units are described in the following table The GOOSE analog input FlexAnalog values are ...

Page 288: ...s are automatically generated for every channel available in the specific relay as shown above for the first channel of a type 5F transducer module installed in slot H The function of the channel may be either Enabled or Disabled If Disabled no actual values are created for the chan nel An alphanumeric ID is assigned to each channel this ID will be included in the channel actual value along with t...

Page 289: ...gs are automatically generated for every channel available in the specific relay as shown above for the first channel of a type 5C transducer module installed in the first available slot The function of the channel may be either Enabled or Disabled If Disabled there will not be an actual value created for the channel An alphanumeric ID is assigned to the channel this ID will be included in the cha...

Page 290: ...50 122 119 39 157 74 131 45 10 97 60 140 123 24 165 90 138 25 11 35 70 158 127 07 174 25 145 20 11 74 80 176 130 89 182 84 152 37 12 12 90 194 134 70 191 64 159 70 12 51 100 212 138 50 200 64 167 20 12 90 110 230 142 29 209 85 174 87 13 28 120 248 146 06 219 29 182 75 13 67 130 266 149 82 228 96 190 80 14 06 140 284 153 58 238 85 199 04 14 44 150 302 157 32 248 95 207 45 14 83 160 320 161 04 259 3...

Page 291: ...ngs menu an exam ple for channel M5 is shown The relay checks the driving signal x in equations below for the minimum and maximum limits and subsequently re scales so the limits defined as MIN VAL and MAX VAL match the output range of the hardware defined as RANGE The follow ing equation is applied EQ 5 18 where x is a driving signal specified by the SOURCE setting Imin and Imax are defined by the...

Page 292: ...ystem measured via UR series relay source 1 is to be monitored by the dcmA H1 output of the range of 1 to 1 mA The following settings are applied on the relay CT ratio 1200 5 VT secondary 115 VT connection is delta and VT ratio 120 The nominal current is 800 A primary and the nominal power factor is 0 90 The power is to be monitored in both importing and exporting directions and allow for 20 overl...

Page 293: ...are EQ 5 27 The base unit for voltage refer to the FlexElements section in this chapter for additional details is EQ 5 28 The minimum and maximum voltage values to be monitored in pu are EQ 5 29 The following settings should be entered DCMA OUTPUT H3 SOURCE SRC 2 V_1 mag DCMA OUTPUT H3 RANGE 0 to 1 mA DCMA OUTPUT H3 MIN VAL 0 404 pu DCMA OUTPUT H3 MAX VAL 0 635 pu The limit settings differ from th...

Page 294: ...input and output using the force contact inputs and force contact outputs test functions described in the follow ing sections 5 9 2 FORCE CONTACT INPUTS PATH SETTINGS ÖØ TESTING ÖØ FORCE CONTACT INPUTS The relay digital inputs contact inputs could be pre programmed to respond to the test mode in the following ways If set to Disabled the input remains fully operational It is controlled by the volta...

Page 295: ...uld open and digital input 4 should close Also contact output 1 should freeze contact output 2 should open contact output 3 should close and contact output 4 should remain fully operational The required settings are shown below To enable user programmable pushbutton 1 to initiate the test mode make the following changes in the SETTINGS ÖØ TESTING Ö TEST MODE menu TEST MODE FUNCTION Enabled and TES...

Page 296: ...5 174 F35 Multiple Feeder Protection System GE Multilin 5 9 TESTING 5 SETTINGS 5 ...

Page 297: ...S See page 6 4 VIRTUAL OUTPUTS See page 6 5 AUTORECLOSE See page 6 5 REMOTE DEVICES STATUS See page 6 5 REMOTE DEVICES STATISTICS See page 6 5 DIGITAL COUNTERS See page 6 6 SELECTOR SWITCHES See page 6 6 FLEX STATES See page 6 6 ETHERNET See page 6 7 DIRECT INPUTS See page 6 7 DIRECT DEVICES STATUS See page 6 8 EGD PROTOCOL STATUS See page 6 8 TELEPROT CH TESTS See page 6 8 INCIPIENT FAULT See pag...

Page 298: ... See page 6 19 IEC 61850 GOOSE ANALOGS See page 6 19 TRANSDUCER I O DCMA INPUTS See page 6 20 TRANSDUCER I O RTD INPUTS See page 6 20 ACTUAL VALUES RECORDS FAULT REPORTS See page 6 21 EVENT RECORDS See page 6 21 OSCILLOGRAPHY See page 6 22 DATA LOGGER See page 6 22 MAINTENANCE See page 6 23 ACTUAL VALUES PRODUCT INFO MODEL INFORMATION See page 6 24 FIRMWARE REVISIONS See page 6 24 ...

Page 299: ...indicates the ID of the virtual input For example Virt Ip 1 refers to the virtual input in terms of the default name The second line of the display indicates the logic state of the virtual input 6 2 3 REMOTE INPUTS PATH ACTUAL VALUES Ö STATUS ÖØ REMOTE INPUTS The present state of the 32 remote inputs is shown here The state displayed will be that of the remote point unless the remote device has be...

Page 300: ...act output in terms of the default name array index The second line of the display indicates the logic state of the contact output For form A contact outputs the state of the voltage and current detectors is displayed as Off VOff IOff On VOn and IOn For form C contact outputs the state is displayed as Off or On TELEPROTECTION INPUTS TELEPROTECTION INPUT 1 1 Off Range Off On MESSAGE TELEPROTECTION ...

Page 301: ...US The present state of up to 16 programmed remote devices is shown here The ALL REMOTE DEVICES ONLINE message indi cates whether or not all programmed remote devices are online If the corresponding state is No then at least one required remote device is not online b STATISTICS PATH ACTUAL VALUES Ö STATUS ÖØ REMOTE DEVICES STATISTICS Ö REMOTE DEVICE 1 16 Statistical data two types for up to 16 pro...

Page 302: ...appear Also included is the date and time stamp for the frozen count The COUNTER 1 MICROS value refers to the microsecond portion of the time stamp 6 2 10 SELECTOR SWITCHES PATH ACTUAL VALUES Ö STATUS ÖØ SELECTOR SWITCHES The display shows both the current position and the full range The current position only an integer from 0 through 7 is the actual value 6 2 11 FLEX STATES PATH ACTUAL VALUES Ö S...

Page 303: ...es that do not make the trip around the communications ring The CRC FAIL COUNT values one per communications channel count the direct output messages that have been received but fail the CRC check High values for either of these counts may indicate on a problem with wiring the communication channel or one or more relays The UNRETURNED MSG COUNT and CRC FAIL COUNT values can be cleared using the CL...

Page 304: ...ging an EGD network The EGD signature and packet size for the slow EGD exchanges are displayed 6 2 16 TELEPROTECTION CHANNEL TESTS PATH ACTUAL VALUES Ö STATUS ÖØ TELEPROT CH TESTS The status information for two channels is shown here DIRECT DEVICES STATUS DIRECT DEVICE 1 STATUS Offline Range Offline Online MESSAGE DIRECT DEVICE 2 STATUS Offline Range Offline Online MESSAGE DIRECT DEVICE 16 STATUS ...

Page 305: ...FAULT Ö INCIPIENT FAULT 1 6 The number of detected incipient faults for each incipient fault element are displayed here for each phase These values can be reset to zero with the COMMANDS ÖØ CLEAR RECORDS ÖØ CLEAR INCIPENT FAULT COUNTERS command 6 2 18 ETHERNET SWITCH PATH ACTUAL VALUES Ö STATUS ÖØ ETHERNET SWITCH These actual values appear only if the F35 is ordered with an Ethernet switch module ...

Page 306: ...sitive PF Lag Current Voltage WATTS Positive VARS Negative PF Lead Current Voltage WATTS Negative VARS Negative PF Lag Current Voltage WATTS Negative VARS Positive PF Lead Current Generator Generator Inductive Inductive Resistive Resistive Generator Generator UR RELAY UR RELAY UR RELAY UR RELAY G G M M G G VCG IC VAG IA VBG IB 1 VCG IC VAG IA VBG IB 2 VCG IC VAG IA VBG IB 3 VCG IC VAG IA VBG IB 4 ...

Page 307: ...on is not measurable the phase angles are not referenced The phase angles are assigned as positive in the leading direction and are presented as negative in the lagging direction to more closely align with power system metering conventions This is illustrated below Figure 6 2 UR PHASE ANGLE MEASUREMENT CONVENTION c UR CONVENTION FOR MEASURING SYMMETRICAL COMPONENTS The UR series of relays calculat...

Page 308: ...is illustrated in the following figure Figure 6 3 MEASUREMENT CONVENTION FOR SYMMETRICAL COMPONENTS ABC phase rotation ACB phase rotation Table 6 1 SYMMETRICAL COMPONENTS CALCULATION EXAMPLE SYSTEM VOLTAGES SEC V VT CONN RELAY INPUTS SEC V SYMM COMP SEC V VAG VBG VCG VAB VBC VCA F5AC F6AC F7AC V0 V1 V2 13 9 0 76 2 125 79 7 250 84 9 313 138 3 97 85 4 241 WYE 13 9 0 76 2 125 79 7 250 19 5 192 56 5 7...

Page 309: ...PATH ACTUAL VALUES ÖØ METERING Ö SOURCE SRC 1 Ö PHASE CURRENT SOURCE SRC 1 PHASE CURRENT SRC 1 See page 6 13 MESSAGE GROUND CURRENT SRC 1 See page 6 14 MESSAGE PHASE VOLTAGE SRC 1 See page 6 14 MESSAGE AUXILIARY VOLTAGE SRC 1 See page 6 15 MESSAGE POWER SRC 1 See page 6 15 MESSAGE ENERGY SRC 1 See page 6 16 MESSAGE DEMAND SRC 1 See page 6 16 MESSAGE FREQUENCY SRC 1 See page 6 17 MESSAGE VOLTAGE HA...

Page 310: ...ed source see SETTINGS ÖØ SYSTEM SETUP ÖØ SIGNAL SOURCES d PHASE VOLTAGE METERING PATH ACTUAL VALUES ÖØ METERING Ö SOURCE SRC 1 Ö PHASE VOLTAGE MESSAGE SRC 1 PHASOR In 0 000 A 0 0 MESSAGE SRC 1 ZERO SEQ I0 0 000 A 0 0 MESSAGE SRC 1 POS SEQ I1 0 000 A 0 0 MESSAGE SRC 1 NEG SEQ I2 0 000 A 0 0 GROUND CURRENT SRC 1 SRC 1 RMS Ig 0 000 A MESSAGE SRC 1 PHASOR Ig 0 000 A 0 0 MESSAGE SRC 1 PHASOR Igd 0 000...

Page 311: ...TTINGS ÖØ SYSTEM SETUP ÖØ SIGNAL SOURCES f POWER METERING PATH ACTUAL VALUES ÖØ METERING Ö SOURCE SRC 1 ÖØ POWER MESSAGE SRC 1 PHASOR Vbc 0 000 V 0 0 MESSAGE SRC 1 PHASOR Vca 0 000 V 0 0 MESSAGE SRC 1 ZERO SEQ V0 0 000 V 0 0 MESSAGE SRC 1 POS SEQ V1 0 000 V 0 0 MESSAGE SRC 1 NEG SEQ V2 0 000 V 0 0 AUXILIARY VOLTAGE SRC 1 SRC 1 RMS Vx 0 00 V MESSAGE SRC 1 PHASOR Vx 0 000 V 0 0 POWER SRC 1 SRC 1 REA...

Page 312: ...ÖØ SIGNAL SOURCES Because energy values are accumulated these values should be recorded and then reset immediately prior to changing CT or VT characteristics h DEMAND METERING PATH ACTUAL VALUES ÖØ METERING Ö SOURCE SRC 1 ÖØ DEMAND MESSAGE SRC 1 APPARENT PWR φb 0 000 VA MESSAGE SRC 1 APPARENT PWR φc 0 000 VA MESSAGE SRC 1 POWER FACTOR 3φ 1 000 MESSAGE SRC 1 POWER FACTOR φa 1 000 MESSAGE SRC 1 POWE...

Page 313: ...S ÖØ METERING Ö SOURCE SRC 1 ÖØ FREQUENCY The metered frequency values are displayed in this menu The SRC 1 text will be replaced by whatever name was pro grammed by the user for the associated source see SETTINGS ÖØ SYSTEM SETUP ÖØ SIGNAL SOURCES SOURCE FREQUENCY is measured via software implemented zero crossing detection of an AC signal The signal is either a Clarke transformation of three phas...

Page 314: ...tained as a ratio of harmonic amplitude to fundamental ampli tude multiplied by 100 The total harmonic distortion THD is the ratio of the total harmonic content to the fundamental EQ 6 2 Voltage harmonics are calculated only for Wye connected phase VTs Ensure the SYSTEM SETUP Ö AC INPUTS ÖØ VOLTAGE BANK F5 ÖØ PHASE VT XX CONNECTION setting is Wye to enable voltage harmonics metering 6 3 3 TRACKING...

Page 315: ...points are displayed in this menu The GGIO3 analog data values are received via IEC 61850 GOOSE messages sent from other devices FLEXELEMENT 1 FLEXELEMENT 1 OpSig 0 000 pu Table 6 2 FLEXELEMENT BASE UNITS dcmA BASE maximum value of the DCMA INPUT MAX setting for the two transducers configured under the IN and IN inputs FREQUENCY fBASE 1 Hz PHASE ANGLE ϕBASE 360 degrees see the UR angle referencing...

Page 316: ... that is enabled are displayed with the top line as the programmed channel ID and the bottom line as the value followed by the programmed units PATH ACTUAL VALUES ÖØ METERING ÖØ TRANSDUCER I O RTD INPUTS Ö RTD INPUT xx Actual values for each RTD input channel that is enabled are displayed with the top line as the programmed channel ID and the bottom line as the value DCMA INPUT xx DCMA INPUT xx 0 ...

Page 317: ...to the last 1024 events listed in chronological order from most recent to oldest If all 1024 event records have been filled the oldest record will be removed as a new record is added Each event record shows the event identifier sequence number cause and date time stamp associated with the event trigger Refer to the COMMANDS Ø CLEAR RECORDS menu for clearing event records NO FAULTS TO REPORT or FAU...

Page 318: ...y records 6 4 4 DATA LOGGER PATH ACTUAL VALUES ÖØ RECORDS ÖØ DATA LOGGER The OLDEST SAMPLE TIME represents the time at which the oldest available samples were taken It will be static until the log gets full at which time it will start counting at the defined sampling rate The NEWEST SAMPLE TIME represents the time the most recent samples were taken It counts up at the defined sampling rate If the ...

Page 319: ...les Refer to the COMMANDS ÖØ CLEAR RECORDS menu for clearing breaker arcing current records The BREAKER OPERATING TIME is defined as the slowest operating time of breaker poles that were initiated to open BREAKER 1 BKR 1 ARCING AMP φA 0 00 kA2 cyc MESSAGE BKR 1 ARCING AMP φB 0 00 kA2 cyc MESSAGE BKR 1 ARCING AMP φC 0 00 kA2 cyc MESSAGE BKR 1 OPERATING TIME φA 0 ms MESSAGE BKR 1 OPERATING TIME φB 0...

Page 320: ...SAGE SERIAL NUMBER Range standard GE multilin serial number format MESSAGE ETHERNET MAC ADDRESS 000000000000 Range standard Ethernet MAC address format MESSAGE MANUFACTURING DATE 0 Range YYYY MM DD HH MM SS MESSAGE CT VT ADVANCED DIAG ACTIVE No Range Yes No MESSAGE OPERATING TIME 0 00 00 Range opearting time in HH MM SS MESSAGE LAST SETTING CHANGE 1970 01 01 23 11 19 Range YYYY MM DD HH MM SS FIRM...

Page 321: ...puts are changed here The first line of the display indicates the ID of the virtual input The second line indicates the current or selected status of the virtual input This status will be a state off logic 0 or on logic 1 7 1 3 CLEAR RECORDS PATH COMMANDS ÖØ CLEAR RECORDS COMMANDS Ø MESSAGE COMMANDS VIRTUAL INPUTS MESSAGE COMMANDS CLEAR RECORDS MESSAGE COMMANDS SET DATE AND TIME MESSAGE COMMANDS R...

Page 322: ... command setting will then automatically revert to No The PERFORM LAMPTEST command turns on all faceplate LEDs and display pixels for a short duration The UPDATE ORDER CODE command causes the relay to scan the backplane for the hardware modules and update the order code to match If an update occurs the following message is shown There is no impact if there have been no changes to the hardware modu...

Page 323: ...tings have not been programmed 7 2 3 RELAY SELF TESTS a DESCRIPTION The relay performs a number of self test diagnostic checks to ensure device integrity The two types of self tests major and minor are listed in the tables below When either type of self test error occurs the Trouble LED Indicator will turn on and a target message displayed All errors record an event in the event recorder Latched e...

Page 324: ... often the test is performed On power up Afterwards the backplane is checked for missing cards every five sec onds What to do Check all modules against the order code ensure they are inserted properly and cycle control power If the problem persists contact the factory Latched target message No Description of problem A FlexLogic equation is incorrect How often the test is performed The test is even...

Page 325: ...ernet switch How often the test is performed Monitored every five seconds An error is issued after five consecutive failures What to do Check the F35 device and switch IP configuration settings Check for incorrect UR port port 7 settings on the Ethernet switch Check the power to the switch Latched target message No Description of problem The Ethernet connection has failed for the specified port Ho...

Page 326: ...ormed Upon initiation of a contact output state change What to do Verify the state of the output contact and contact the factory if the problem persists Latched target message No Description of problem A data item in a configurable GOOSE data set is oscillating How often the test is performed Upon scanning of each configurable GOOSE data set What to do The xxx text denotes the data item that has b...

Page 327: ...ceiving This can be from 1 to 60 seconds depending on GOOSE packets What to do Check GOOSE setup Latched target message Yes Description of problem Abnormal restart from modules being removed or inserted while the F35 is powered up when there is an abnormal DC supply or as a result of internal relay failure How often the test is performed Event driven What to do Contact the factory UNEXPECTED RESTA...

Page 328: ...7 8 F35 Multiple Feeder Protection System GE Multilin 7 2 TARGETS 7 COMMANDS AND TARGETS 7 ...

Page 329: ... pu distance to fault Z positive sequence impedance of the line The currents from the local and remote systems can be parted between their fault F and pre fault load pre components EQ 8 2 and neglecting shunt parameters of the line EQ 8 3 Inserting the IA and IB equations into the VA equation and solving for the fault resistance yields EQ 8 4 Assuming the fault components of the currents IAF and I...

Page 330: ...EPORT 1 VT SUBSTITUTION setting value is V0 and the VTs are connected in a wye configuration the fault location is performed based on the actual phase to ground voltages If the VTs are connected in a delta configuration fault location is performed based on the delta voltages and externally supplied neutral voltage EQ 8 13 If the FAULT REPORT 1 VT SUBSTITUTION setting value is I0 and the VTs are co...

Page 331: ... SRC 50DD OP X VA or VAB VC or VCA VB or VBC 827094A5 CDR Off 0 AND FAULT LOCATOR 1 RUN 0 3 SEC ACTUAL VALUES DATE TIME FAULT TYPE FAULT LOCATION FAULT RECLOSE SHOT FAULT REPORT Vn or V_0 FAULT REPORT 1 Z1 MAG FAULT REPORT 1 Z1 ANGLE FAULT REPORT 1 Z0 MAG FAULT REPORT 1 Z0 ANGLE FAULT REPORT 1 LENGTH UNITS FAULT REPORT 1 LENGTH FAULT REPORT 1 VT SUBSTITUTION FAULT REP 1 SYSTEM Z0 MAG FAULT REP 1 S...

Page 332: ...8 4 F35 Multiple Feeder Protection System GE Multilin 8 1 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...

Page 333: ...mponent As such the same signal must not be injected to all three phases or the injected signal will be completely filtered out For an underfrequency element using phase quantities the phase A signal must be above the MIN VOLT AMP setting value There fore either inject into phase A only or inject a balanced three phase signal Figure 9 1 TYPICAL UNDERFREQUENCY ELEMENT TEST TIMING The static accurac...

Page 334: ... timer This is exclusive of the time taken by the frequency responding component to pickup The F35 oscillography can be used to measure the time between the calculated source frequency crossing the threshold and element operation however this method omits the delay in the calculated source frequency The security features of the source frequency measurement algorithm result in the calculated freque...

Page 335: ... Degrees Source 1 negative sequence current magnitude 6177 SRC 1 I_2 Angle Amps Source 1 negative sequence current angle 6178 SRC 1 Igd Mag Degrees Source 1 differential ground current magnitude 6180 SRC 1 Igd Angle Amps Source 1 differential ground current angle 6208 SRC 2 Ia RMS Amps Source 2 phase A current RMS 6210 SRC 2 Ib RMS Amps Source 2 phase B current RMS 6212 SRC 2 Ic RMS Amps Source 2 ...

Page 336: ...3 Igd Mag Degrees Source 3 differential ground current magnitude 6308 SRC 3 Igd Angle Amps Source 3 differential ground current angle 6336 SRC 4 Ia RMS Amps Source 4 phase A current RMS 6338 SRC 4 Ib RMS Amps Source 4 phase B current RMS 6340 SRC 4 Ic RMS Amps Source 4 phase C current RMS 6342 SRC 4 In RMS Amps Source 4 neutral current RMS 6344 SRC 4 Ia Mag Amps Source 4 phase A current magnitude ...

Page 337: ...ude 6436 SRC 5 Igd Angle Amps Source 5 differential ground current angle 6464 SRC 6 Ia RMS Amps Source 6 phase A current RMS 6466 SRC 6 Ib RMS Amps Source 6 phase B current RMS 6468 SRC 6 Ic RMS Amps Source 6 phase C current RMS 6470 SRC 6 In RMS Amps Source 6 neutral current RMS 6472 SRC 6 Ia Mag Amps Source 6 phase A current magnitude 6474 SRC 6 Ia Angle Degrees Source 6 phase A current angle 64...

Page 338: ...94 SRC 1 V_1 Mag Volts Source 1 positive sequence voltage magnitude 6696 SRC 1 V_1 Angle Degrees Source 1 positive sequence voltage angle 6697 SRC 1 V_2 Mag Volts Source 1 negative sequence voltage magnitude 6699 SRC 1 V_2 Angle Degrees Source 1 negative sequence voltage angle 6720 SRC 2 Vag RMS Volts Source 2 phase AG voltage RMS 6722 SRC 2 Vbg RMS Volts Source 2 phase BG voltage RMS 6724 SRC 2 V...

Page 339: ...ltage angle 6811 SRC 3 Vca Mag Volts Source 3 phase CA voltage magnitude 6813 SRC 3 Vca Angle Degrees Source 3 phase CA voltage angle 6814 SRC 3 Vx RMS Volts Source 3 auxiliary voltage RMS 6816 SRC 3 Vx Mag Volts Source 3 auxiliary voltage magnitude 6818 SRC 3 Vx Angle Degrees Source 3 auxiliary voltage angle 6819 SRC 3 V_0 Mag Volts Source 3 zero sequence voltage magnitude 6821 SRC 3 V_0 Angle De...

Page 340: ...CG voltage angle 6927 SRC 5 Vab RMS Volts Source 5 phase AB voltage RMS 6929 SRC 5 Vbc RMS Volts Source 5 phase BC voltage RMS 6931 SRC 5 Vca RMS Volts Source 5 phase CA voltage RMS 6933 SRC 5 Vab Mag Volts Source 5 phase AB voltage magnitude 6935 SRC 5 Vab Angle Degrees Source 5 phase AB voltage angle 6936 SRC 5 Vbc Mag Volts Source 5 phase BC voltage magnitude 6938 SRC 5 Vbc Angle Degrees Source...

Page 341: ...s Source 6 negative sequence voltage angle 7168 SRC 1 P Watts Source 1 three phase real power 7170 SRC 1 Pa Watts Source 1 phase A real power 7172 SRC 1 Pb Watts Source 1 phase B real power 7174 SRC 1 Pc Watts Source 1 phase C real power 7176 SRC 1 Q Vars Source 1 three phase reactive power 7178 SRC 1 Qa Vars Source 1 phase A reactive power 7180 SRC 1 Qb Vars Source 1 phase B reactive power 7182 S...

Page 342: ... 4 three phase real power 7266 SRC 4 Pa Watts Source 4 phase A real power 7268 SRC 4 Pb Watts Source 4 phase B real power 7270 SRC 4 Pc Watts Source 4 phase C real power 7272 SRC 4 Q Vars Source 4 three phase reactive power 7274 SRC 4 Qa Vars Source 4 phase A reactive power 7276 SRC 4 Qb Vars Source 4 phase B reactive power 7278 SRC 4 Qc Vars Source 4 phase C reactive power 7280 SRC 4 S VA Source ...

Page 343: ...y Hz Source 1 frequency 7553 SRC 2 Frequency Hz Source 2 frequency 7554 SRC 3 Frequency Hz Source 3 frequency 7555 SRC 4 Frequency Hz Source 4 frequency 7556 SRC 5 Frequency Hz Source 5 frequency 7557 SRC 6 Frequency Hz Source 6 frequency 7680 SRC 1 Demand Ia Amps Source 1 phase A current demand 7682 SRC 1 Demand Ib Amps Source 1 phase B current demand 7684 SRC 1 Demand Ic Amps Source 1 phase C cu...

Page 344: ...pre fault phase A voltage magnitude 9035 Prefault Va Ang 0 Degrees Fault 1 pre fault phase A voltage angle 9036 Prefault Vb Mag 0 Volts Fault 1 pre fault phase B voltage magnitude 9038 Prefault Vb Ang 0 Degrees Fault 1 pre fault phase B voltage angle 9039 Prefault Vc Mag 0 Volts Fault 1 pre fault phase C voltage magnitude 9041 Prefault Vc Ang 0 Degrees Fault 1 pre fault phase C voltage angle 9042 ...

Page 345: ...Amps Fault 3 pre fault phase A current magnitude 9102 Prefault Ia Ang 2 Degrees Fault 3 pre fault phase A current angle 9103 Prefault Ib Mag 2 Amps Fault 3 pre fault phase B current magnitude 9105 Prefault Ib Ang 2 Degrees Fault 3 pre fault phase B current angle 9106 Prefault Ic Mag 2 Amps Fault 3 pre fault phase C current magnitude 9108 Prefault Ic Ang 2 Degrees Fault 3 pre fault phase C current ...

Page 346: ... magnitude 9170 Postfault Vb Ang 3 Degrees Fault 4 post fault phase B voltage angle 9171 Postfault Vc Mag 3 Volts Fault 4 post fault phase C voltage magnitude 9173 Postfault Vc Ang 3 Degrees Fault 4 post fault phase C voltage angle 9174 Fault Type 3 Fault 4 type 9175 Fault Location 3 Fault 4 location 9176 Prefault Ia Mag 4 Amps Fault 5 pre fault phase A current magnitude 9178 Prefault Ia Ang 4 Deg...

Page 347: ...ctual value 13534 DCMA Inputs 16 Value mA dcmA input 16 actual value 13536 DCMA Inputs 17 Value mA dcmA input 17 actual value 13538 DCMA Inputs 18 Value mA dcmA input 18 actual value 13540 DCMA Inputs 19 Value mA dcmA input 19 actual value 13542 DCMA Inputs 20 Value mA dcmA input 20 actual value 13544 DCMA Inputs 21 Value mA dcmA input 21 actual value 13546 DCMA Inputs 22 Value mA dcmA input 22 ac...

Page 348: ... actual value 13591 RTD Inputs 40 Value RTD input 40 actual value 13592 RTD Inputs 41 Value RTD input 41 actual value 13593 RTD Inputs 42 Value RTD input 42 actual value 13594 RTD Inputs 43 Value RTD input 43 actual value 13595 RTD Inputs 44 Value RTD input 44 actual value 13596 RTD Inputs 45 Value RTD input 45 actual value 13597 RTD Inputs 46 Value RTD input 46 actual value 13598 RTD Inputs 47 Va...

Page 349: ...g In 6 IEC 61850 GOOSE analog input 6 45596 GOOSE Analog In 7 IEC 61850 GOOSE analog input 7 45598 GOOSE Analog In 8 IEC 61850 GOOSE analog input 8 45600 GOOSE Analog In 9 IEC 61850 GOOSE analog input 9 45602 GOOSE Analog In 10 IEC 61850 GOOSE analog input 10 45604 GOOSE Analog In 11 IEC 61850 GOOSE analog input 11 45606 GOOSE Analog In 12 IEC 61850 GOOSE analog input 12 45608 GOOSE Analog In 13 I...

Page 350: ...A 16 F35 Multiple Feeder Protection System GE Multilin A 1 PARAMETER LIST APPENDIXA A ...

Page 351: ...00 2400 4800 9600 14400 19200 28800 33600 38400 57600 or 115200 bps are available Even odd and no parity are avail able Refer to the Communications section of chapter 5 for further details The master device in any system must know the address of the slave device with which it is to communicate The relay will not act on a request from a master if the address in the request does not match the relay ...

Page 352: ...ission all slaves start listening for a new packet from the master except for the addressed slave B 1 4 CRC 16 ALGORITHM The CRC 16 algorithm essentially treats the entire data stream data bits only start stop and parity ignored as one contin uous binary number This number is first shifted left 16 bits and then divided by a characteristic polynomial 11000000000000101B The 16 bit remainder of the d...

Page 353: ...starting address will determine the type of data being read Function codes 03h and 04h are therefore identical The following table shows the format of the master and slave packets The example shows a master device requesting three register values starting at address 4050h from slave device 11h 17 decimal the slave device responds with the val ues 40 300 and 0 from registers 4050h 4051h and 4052h r...

Page 354: ...SMISSION EXAMPLE MASTER TRANSMISSION SLAVE RESPONSE PACKET FORMAT EXAMPLE HEX PACKET FORMAT EXAMPLE HEX SLAVE ADDRESS 11 SLAVE ADDRESS 11 FUNCTION CODE 05 FUNCTION CODE 05 OPERATION CODE high 00 OPERATION CODE high 00 OPERATION CODE low 01 OPERATION CODE low 01 CODE VALUE high FF CODE VALUE high FF CODE VALUE low 00 CODE VALUE low 00 CRC low DF CRC low DF CRC high 6A CRC high 6A Table B 5 SUMMARY ...

Page 355: ...f the function code set to 1 The following table shows the format of the master and slave packets The example shows a master device sending the unsupported function code 39h to slave device 11 Table B 7 MASTER AND SLAVE DEVICE PACKET TRANSMISSION EXAMPLE MASTER TRANSMISSION SLAVE RESPONSE PACKET FORMAT EXAMPLE HEX PACKET FORMAT EXMAPLE HEX SLAVE ADDRESS 11 SLAVE ADDRESS 11 FUNCTION CODE 10 FUNCTIO...

Page 356: ...retains connection specific file transfer information so files may be read simultaneously on multiple Modbus connections b OTHER PROTOCOLS All the files available via Modbus may also be retrieved using the standard file transfer mechanisms in other protocols for example TFTP or MMS c COMTRADE OSCILLOGRAPHY AND DATA LOGGER FILES Oscillography and data logger files are formatted using the COMTRADE f...

Page 357: ... via EnerVista or any serial interface the user must enter the correspond ing connection password If the connection is to the back of the F35 the remote password must be used If the connection is to the RS232 port of the faceplate the local password must be used The command password is set up at memory location 4000 Storing a value of 0 removes command password protection When reading the password...

Page 358: ... Command 64 modules 0400 Virtual Input 1 State 0 to 1 1 F108 0 Off 0401 Virtual Input 2 State 0 to 1 1 F108 0 Off 0402 Virtual Input 3 State 0 to 1 1 F108 0 Off 0403 Virtual Input 4 State 0 to 1 1 F108 0 Off 0404 Virtual Input 5 State 0 to 1 1 F108 0 Off 0405 Virtual Input 6 State 0 to 1 1 F108 0 Off 0406 Virtual Input 7 State 0 to 1 1 F108 0 Off 0407 Virtual Input 8 State 0 to 1 1 F108 0 Off 0408...

Page 359: ...tate 0 to 1 1 F108 0 Off 0434 Virtual Input 53 State 0 to 1 1 F108 0 Off 0435 Virtual Input 54 State 0 to 1 1 F108 0 Off 0436 Virtual Input 55 State 0 to 1 1 F108 0 Off 0437 Virtual Input 56 State 0 to 1 1 F108 0 Off 0438 Virtual Input 57 State 0 to 1 1 F108 0 Off 0439 Virtual Input 58 State 0 to 1 1 F108 0 Off 043A Virtual Input 59 State 0 to 1 1 F108 0 Off 043B Virtual Input 60 State 0 to 1 1 F1...

Page 360: ...outputs unreturned message count Ch 2 0 to 65535 1 F001 0 15D0 Direct device states 0 to 65535 1 F500 0 15D1 Reserved 0 to 65535 1 F001 0 15D2 Direct inputs outputs CRC fail count 1 0 to 65535 1 F001 0 15D3 Direct inputs outputs CRC fail count 2 0 to 65535 1 F001 0 Ethernet Fibre Channel Status Read Write 1610 Ethernet primary fibre channel status 0 to 2 1 F134 0 Fail 1611 Ethernet secondary fibre...

Page 361: ...99 V 0 001 F060 0 1A0E Source 1 Phase CG Voltage Angle 359 9 to 0 degrees 0 1 F002 0 1A0F Source 1 Phase AB or AC Voltage RMS 0 to 999999 999 V 0 001 F060 0 1A11 Source 1 Phase BC or BA Voltage RMS 0 to 999999 999 V 0 001 F060 0 1A13 Source 1 Phase CA or CB Voltage RMS 0 to 999999 999 V 0 001 F060 0 1A15 Source 1 Phase AB or AC Voltage Magnitude 0 to 999999 999 V 0 001 F060 0 1A17 Source 1 Phase A...

Page 362: ...r 0 999 to 1 0 001 F013 0 1C1C Reserved 4 items F001 0 1C20 Repeated for Source 2 1C40 Repeated for Source 3 1C60 Repeated for Source 4 1C80 Repeated for Source 5 1CA0 Repeated for Source 6 Source Energy Read Only Non Volatile 6 modules 1D00 Source 1 Positive Watthour 0 to 1000000000000 Wh 0 001 F060 0 1D02 Source 1 Negative Watthour 0 to 1000000000000 Wh 0 001 F060 0 1D04 Source 1 Positive Varhou...

Page 363: ...6 modules 1F80 Source 1 Va THD 0 to 99 9 0 1 F001 0 1F81 Source 1 Va Harmonics 2nd to 25th 24 items 0 to 99 9 0 1 F001 0 1F99 Source 1 Vb THD 0 to 99 9 0 1 F001 0 1F9A Source 1 Vb Harmonics 2nd to 25th 24 items 0 to 99 9 0 1 F001 0 1FB2 Source 1 Vc THD 0 to 99 9 0 1 F001 0 1FB3 Source 1 Vc Harmonics 2nd to 25th 24 items 0 to 99 9 0 1 F001 0 1FCB Repeated for Source 2 2016 Repeated for Source 3 206...

Page 364: ...le 359 9 to 0 degrees 0 1 F002 0 2361 Fault 1 Phase C Voltage Magnitude 0 to 999999 999 V 0 001 F060 0 2363 Fault 1 Phase C Voltage Angle 359 9 to 0 degrees 0 1 F002 0 2364 Fault 1 Type 0 to 11 1 F148 0 NA 2365 Fault 1 Location based on Line length units km or miles 3276 7 to 3276 7 0 1 F002 0 2366 Repeated for Fault 2 238C Repeated for Fault 3 23B2 Repeated for Fault 4 23D8 Repeated for Fault 5 A...

Page 365: ...967295 1 F003 0 3402 Number of Available Events 0 to 4294967295 1 F003 0 3404 Event Recorder Last Cleared Date 0 to 4294967295 1 F050 0 Event recorder commands read write 3406 Event Recorder Clear Command 0 to 1 1 F126 0 No DCMA Input Values Read Only 24 modules 34C0 DCMA Inputs 1 Value 9999999 to 9999999 1 F004 0 34C2 DCMA Inputs 2 Value 9999999 to 9999999 1 F004 0 34C4 DCMA Inputs 3 Value 999999...

Page 366: ...D Input 24 Value 32768 to 32767 C 1 F002 0 3508 RTD Input 25 Value 32768 to 32767 C 1 F002 0 3509 RTD Input 26 Value 32768 to 32767 C 1 F002 0 350A RTD Input 27 Value 32768 to 32767 C 1 F002 0 350B RTD Input 28 Value 32768 to 32767 C 1 F002 0 350C RTD Input 29 Value 32768 to 32767 C 1 F002 0 350D RTD Input 30 Value 32768 to 32767 C 1 F002 0 350E RTD Input 31 Value 32768 to 32767 C 1 F002 0 350F RT...

Page 367: ...1 1 F102 0 Disabled 4054 Screen Saver Wait Time 1 to 65535 min 1 F001 30 4055 Current Cutoff Level 0 002 to 0 02 pu 0 001 F001 20 4056 Voltage Cutoff Level 0 1 to 1 V 0 1 F001 10 Communications Read Write Setting 407E COM1 minimum response time 0 to 1000 ms 10 F001 0 407F COM2 minimum response time 0 to 1000 ms 10 F001 0 4080 Modbus Slave Address 1 to 254 1 F001 254 4083 RS485 Com1 Baud Rate 0 to ...

Page 368: ... F001 0 40E3 IEC 60870 5 104 protocol cyclic data transmit period 1 to 65535 s 1 F001 60 40E4 IEC 60870 5 104 current default threshold 0 to 65535 1 F001 30000 40E6 IEC 60870 5 104 voltage default threshold 0 to 65535 1 F001 30000 40E8 IEC 60870 5 104 power default threshold 0 to 65535 1 F001 30000 40EA IEC 60870 5 104 energy default threshold 0 to 65535 1 F001 30000 40EC IEC 60870 5 104 power def...

Page 369: ...DST Start Month 0 to 11 1 F237 0 January 41AB Daylight Savings Time DST Start Day 0 to 6 1 F238 0 Sunday 41AC Daylight Savings Time DST Start Day Instance 0 to 4 1 F239 0 First 41AD Daylight Savings Time DST Start Hour 0 to 23 1 F001 2 41AE Daylight Savings Time DST Stop Month 0 to 11 1 F237 0 January 41AF Daylight Savings Time DST Stop Day 0 to 6 1 F238 0 Sunday 41B0 Daylight Savings Time DST Sto...

Page 370: ...ed for User Programmable LED 33 42C2 Repeated for User Programmable LED 34 42C4 Repeated for User Programmable LED 35 42C6 Repeated for User Programmable LED 36 42C8 Repeated for User Programmable LED 37 42CA Repeated for User Programmable LED 38 42CC Repeated for User Programmable LED 39 42CE Repeated for User Programmable LED 40 42D0 Repeated for User Programmable LED 41 42D2 Repeated for User P...

Page 371: ...urce 2 458E Repeated for Source 3 4595 Repeated for Source 4 459C Repeated for Source 5 45A3 Repeated for Source 6 Power System Read Write Setting 4600 Nominal Frequency 25 to 60 Hz 1 F001 60 4601 Phase Rotation 0 to 1 1 F106 0 ABC 4602 Frequency And Phase Reference 0 to 5 1 F167 0 SRC 1 4603 Frequency Tracking Function 0 to 1 1 F102 1 Enabled Incipient cable fault detector read write settings 46B...

Page 372: ...Repeated for breaker 4 4764 Repeated for breaker 5 477D Repeated for breaker 6 Demand Read Write Setting 47D0 Demand Current Method 0 to 2 1 F139 0 Thrm Exponential 47D1 Demand Power Method 0 to 2 1 F139 0 Thrm Exponential 47D2 Demand Interval 0 to 5 1 F132 2 15 MIN 47D3 Demand Input 0 to 65535 1 F300 0 Demand Read Write Command 47D4 Demand Clear Record 0 to 1 1 F126 0 No Flexcurves A and B Read W...

Page 373: ...on 1 Reset 0 to 65535 1 F300 0 4E29 User Programmable Pushbutton 1 Set 0 to 65535 1 F300 0 4E2A Repeated for User Programmable Pushbutton 2 4E54 Repeated for User Programmable Pushbutton 3 4E7E Repeated for User Programmable Pushbutton 4 4EA8 Repeated for User Programmable Pushbutton 5 4ED2 Repeated for User Programmable Pushbutton 6 4EFC Repeated for User Programmable Pushbutton 7 4F26 Repeated f...

Page 374: ... Repeated for RTD Input 45 5757 Repeated for RTD Input 46 576A Repeated for RTD Input 47 577D Repeated for RTD Input 48 Flexlogic Timers Read Write Setting 32 modules 5800 FlexLogic Timer 1 Type 0 to 2 1 F129 0 millisecond 5801 FlexLogic Timer 1 Pickup Delay 0 to 60000 1 F001 0 5802 FlexLogic Timer 1 Dropout Delay 0 to 60000 1 F001 0 5803 Reserved 5 items 0 to 65535 1 F001 0 5808 Repeated for Flex...

Page 375: ...t 2 5920 Repeated for Phase Time Overcurrent 3 5930 Repeated for Phase Time Overcurrent 4 5940 Repeated for Phase Time Overcurrent 5 5950 Repeated for Phase Time Overcurrent 6 Phase Instantaneous Overcurrent Read Write Grouped Setting 12 modules 5A00 Phase Instantaneous Overcurrent 1 Function 0 to 1 1 F102 0 Disabled 5A01 Phase Instantaneous Overcurrent 1 Signal Source 0 to 5 1 F167 0 SRC 1 5A02 P...

Page 376: ...tral Instantaneous Overcurrent 1 Target 0 to 2 1 F109 0 Self reset 5C07 Neutral Instantaneous Overcurrent 1 Events 0 to 1 1 F102 0 Disabled 5C08 Reserved 8 items 0 to 1 1 F001 0 5C10 Repeated for Neutral Instantaneous Overcurrent 2 5C20 Repeated for Neutral Instantaneous Overcurrent 3 5C30 Repeated for Neutral Instantaneous Overcurrent 4 5C40 Repeated for Neutral Instantaneous Overcurrent 5 5C50 R...

Page 377: ...ead only 5EC0 Incipient cable fault detector 1 phase A counter 0 to 65535 1 F001 0 5EC1 Incipient cable fault detector 1 phase B counter 0 to 65535 1 F001 0 5EC2 Incipient cable fault detector 1 phase C counter 0 to 65535 1 F001 0 5EC3 Repeated for incipient cable fault detector 2 5EC6 Repeated for incipient cable fault detector 3 5EC9 Repeated for incipient cable fault detector 4 5ECC Repeated fo...

Page 378: ...00 Phase Undervoltage 1 Function 0 to 1 1 F102 0 Disabled 7001 Phase Undervoltage 1 Signal Source 0 to 5 1 F167 0 SRC 1 7002 Phase Undervoltage 1 Pickup 0 to 3 pu 0 001 F001 1000 7003 Phase Undervoltage 1 Curve 0 to 1 1 F111 0 Definite Time 7004 Phase Undervoltage 1 Delay 0 to 600 s 0 01 F001 100 7005 Phase Undervoltage 1 Minimum Voltage 0 to 3 pu 0 001 F001 100 7006 Phase Undervoltage 1 Block 0 t...

Page 379: ...ted for dcmA Inputs 21 74F8 Repeated for dcmA Inputs 22 7510 Repeated for dcmA Inputs 23 7528 Repeated for dcmA Inputs 24 Disconnect switches read write settings 7540 Disconnect switch 1 function 0 to 1 1 F102 0 Disabled 7541 Disconnect switch 1 name F206 SW 1 7544 Disconnect switch 1 mode 0 to 1 1 F157 0 3 Pole 7545 Disconnect switch 1 open 0 to 65535 1 F300 0 7546 Disconnect switch 1 block open ...

Page 380: ...LED Operand 0 to 65535 1 F300 0 7B83 User Programmable Pushbutton 1 Autoreset Delay 0 to 600 s 0 05 F001 0 7B84 User Programmable Pushbutton 1 Autoreset Function 0 to 1 1 F102 0 Disabled 7B85 User Programmable Pushbutton 1 Local Lock 0 to 65535 1 F300 0 7B86 User Programmable Pushbutton 1 Message Priority 0 to 2 1 F220 0 Disabled 7B87 User Programmable Pushbutton 1 Remote Lock 0 to 65535 1 F300 0 ...

Page 381: ...for Neutral Overvoltage 3 Auxiliary Overvoltage Read Write Grouped Setting 3 modules 7F30 Auxiliary Overvoltage 1 Function 0 to 1 1 F102 0 Disabled 7F31 Auxiliary Overvoltage 1 Signal Source 0 to 5 1 F167 0 SRC 1 7F32 Auxiliary Overvoltage 1 Pickup 0 to 3 pu 0 001 F001 300 7F33 Auxiliary Overvoltage 1 Pickup Delay 0 to 600 s 0 01 F001 100 7F34 Auxiliary Overvoltage 1 Reset Delay 0 to 600 s 0 01 F0...

Page 382: ...a Item 1 20 items 0 to 65535 1 F001 0 8418 Reserved 80 items F001 0 EGD Slow Production Read Write Setting 2 modules 8500 EGD Slow Producer Exchange 1 Function 0 to 1 1 F102 0 Disabled 8501 EGD Fast Producer Exchange 1 Destination 0 to 4294967295 1 F003 0 8503 EGD Slow Producer Exchange 1 Data Rate 500 to 1000 ms 50 F001 1000 8504 EGD Slow Producer Exchange 1 Data Item 1 50 items 0 to 65535 1 F001...

Page 383: ...l Element 35 8CBC Repeated for Digital Element 36 8CD0 Repeated for Digital Element 37 8CE4 Repeated for Digital Element 38 8CF8 Repeated for Digital Element 39 8D0C Repeated for Digital Element 40 8D20 Repeated for Digital Element 41 8D34 Repeated for Digital Element 42 8D48 Repeated for Digital Element 43 8D5C Repeated for Digital Element 44 8D70 Repeated for Digital Element 45 8D84 Repeated for...

Page 384: ...0A FlexElement 1 Pickup 90 to 90 pu 0 001 F004 1000 900C FlexElement 1 DeltaT Units 0 to 2 1 F518 0 Milliseconds 900D FlexElement 1 DeltaT 20 to 86400 1 F003 20 900F FlexElement 1 Pickup Delay 0 to 65 535 s 0 001 F001 0 9010 FlexElement 1 Reset Delay 0 to 65 535 s 0 001 F001 0 9011 FlexElement 1 Block 0 to 65535 1 F300 0 9012 FlexElement 1 Target 0 to 2 1 F109 0 Self reset 9013 FlexElement 1 Event...

Page 385: ...Output 9 9336 Repeated for dcmA Output 10 933C Repeated for dcmA Output 11 9342 Repeated for dcmA Output 12 9348 Repeated for dcmA Output 13 934E Repeated for dcmA Output 14 9354 Repeated for dcmA Output 15 935A Repeated for dcmA Output 16 9360 Repeated for dcmA Output 17 9366 Repeated for dcmA Output 18 936C Repeated for dcmA Output 19 9372 Repeated for dcmA Output 20 9378 Repeated for dcmA Outpu...

Page 386: ... FlexElement 10 Actual 2147483 647 to 2147483 647 0 001 F004 0 9A15 FlexElement 11 Actual 2147483 647 to 2147483 647 0 001 F004 0 9A17 FlexElement 12 Actual 2147483 647 to 2147483 647 0 001 F004 0 9A19 FlexElement 13 Actual 2147483 647 to 2147483 647 0 001 F004 0 9A1B FlexElement 14 Actual 2147483 647 to 2147483 647 0 001 F004 0 9A1D FlexElement 15 Actual 2147483 647 to 2147483 647 0 001 F004 0 9A...

Page 387: ...items 1 F001 0 A298 Repeated for Selector 2 DNP IEC Points Read Write Setting A300 DNP IEC 60870 5 104 Binary Input Points 256 items 0 to 65535 1 F300 0 A400 DNP IEC 60870 5 104 Analog Input Points 256 items 0 to 65535 1 F300 0 Flexcurves C and D Read Write Setting A600 FlexCurve C 120 items 0 to 65535 ms 1 F011 0 A680 FlexCurve D 120 items 0 to 65535 ms 1 F011 0 Non Volatile Latches Read Write Se...

Page 388: ...og input 1 per unit base 0 to 999999999 999 0 001 F060 1 AA07 Repeated for IEC 61850 GOOSE analog input 2 AA0E Repeated for IEC 61850 GOOSE analog input 3 AA15 Repeated for IEC 61850 GOOSE analog input 4 AA1C Repeated for IEC 61850 GOOSE analog input 5 AA23 Repeated for IEC 61850 GOOSE analog input 6 AA2A Repeated for IEC 61850 GOOSE analog input 7 AA31 Repeated for IEC 61850 GOOSE analog input 8 ...

Page 389: ...o 65534 1 F206 none AC7A IEC 61850 logical node PTOVx name prefix 10 items 0 to 65534 1 F206 none AC98 IEC 61850 logical node PDISx name prefix 10 items 0 to 65534 1 F206 none ACB6 IEC 61850 logical node RBRFx name prefix 24 items 0 to 65534 1 F206 none ACFE IEC 61850 logical node RPSBx name prefix 0 to 65534 1 F206 none AD01 IEC 61850 logical node RRECx name prefix 6 items 0 to 65534 1 F206 none ...

Page 390: ...F IEC 61850 Logical Node PDISx Name Prefix 10 items 0 to 65534 1 F206 None ACAD IEC 61850 Logical Node RRBFx Name Prefix 24 items 0 to 65534 1 F206 None ACF5 IEC 61850 Logical Node RPSBx Name Prefix 0 to 65534 1 F206 None ACF8 IEC 61850 Logical Node RRECx Name Prefix 6 items 0 to 65534 1 F206 None AD0A IEC 61850 Logical Node MMXUx Name Prefix 6 items 0 to 65534 1 F206 None AD1C IEC 61850 Logical N...

Page 391: ... 61850 GGIO2 CF SPCSO7 ctlModel Value 0 to 2 1 F001 2 B247 IEC 61850 GGIO2 CF SPCSO8 ctlModel Value 0 to 2 1 F001 2 B248 IEC 61850 GGIO2 CF SPCSO9 ctlModel Value 0 to 2 1 F001 2 B249 IEC 61850 GGIO2 CF SPCSO10 ctlModel Value 0 to 2 1 F001 2 B24A IEC 61850 GGIO2 CF SPCSO11 ctlModel Value 0 to 2 1 F001 2 B24B IEC 61850 GGIO2 CF SPCSO12 ctlModel Value 0 to 2 1 F001 2 B24C IEC 61850 GGIO2 CF SPCSO13 c...

Page 392: ...SPCSO55 ctlModel Value 0 to 2 1 F001 2 B277 IEC 61850 GGIO2 CF SPCSO56 ctlModel Value 0 to 2 1 F001 2 B278 IEC 61850 GGIO2 CF SPCSO57 ctlModel Value 0 to 2 1 F001 2 B279 IEC 61850 GGIO2 CF SPCSO58 ctlModel Value 0 to 2 1 F001 2 B27A IEC 61850 GGIO2 CF SPCSO59 ctlModel Value 0 to 2 1 F001 2 B27B IEC 61850 GGIO2 CF SPCSO60 ctlModel Value 0 to 2 1 F001 2 B27C IEC 61850 GGIO2 CF SPCSO61 ctlModel Value...

Page 393: ... for Module 4 BA00 Repeated for Module 5 BA40 Repeated for Module 6 BA80 Repeated for Module 7 BAC0 Repeated for Module 8 Contact Inputs Read Write Setting 96 modules BB00 Contact Input 1 Name F205 Cont Ip 1 BB06 Contact Input 1 Events 0 to 1 1 F102 0 Disabled BB07 Contact Input 1 Debounce Time 0 to 16 ms 0 5 F001 20 BB08 Repeated for Contact Input 2 BB10 Repeated for Contact Input 3 BB18 Repeated...

Page 394: ...eated for Contact Input 51 BC98 Repeated for Contact Input 52 BCA0 Repeated for Contact Input 53 BCA8 Repeated for Contact Input 54 BCB0 Repeated for Contact Input 55 BCB8 Repeated for Contact Input 56 BCC0 Repeated for Contact Input 57 BCC8 Repeated for Contact Input 58 BCD0 Repeated for Contact Input 59 BCD8 Repeated for Contact Input 60 BCE0 Repeated for Contact Input 61 BCE8 Repeated for Conta...

Page 395: ...ts 0 to 1 1 F102 0 Disabled BE39 Reserved 3 items F001 0 BE3C Repeated for Virtual Input 2 BE48 Repeated for Virtual Input 3 BE54 Repeated for Virtual Input 4 BE60 Repeated for Virtual Input 5 BE6C Repeated for Virtual Input 6 BE78 Repeated for Virtual Input 7 BE84 Repeated for Virtual Input 8 BE90 Repeated for Virtual Input 9 BE9C Repeated for Virtual Input 10 BEA8 Repeated for Virtual Input 11 B...

Page 396: ...l Input 56 C0D0 Repeated for Virtual Input 57 C0DC Repeated for Virtual Input 58 C0E8 Repeated for Virtual Input 59 C0F4 Repeated for Virtual Input 60 C100 Repeated for Virtual Input 61 C10C Repeated for Virtual Input 62 C118 Repeated for Virtual Input 63 C124 Repeated for Virtual Input 64 Virtual Outputs Read Write Setting 96 modules C130 Virtual Output 1 Name F205 Virt Op 1 C136 Virtual Output 1...

Page 397: ...ted for Virtual Output 43 C288 Repeated for Virtual Output 44 C290 Repeated for Virtual Output 45 C298 Repeated for Virtual Output 46 C2A0 Repeated for Virtual Output 47 C2A8 Repeated for Virtual Output 48 C2B0 Repeated for Virtual Output 49 C2B8 Repeated for Virtual Output 50 C2C0 Repeated for Virtual Output 51 C2C8 Repeated for Virtual Output 52 C2D0 Repeated for Virtual Output 53 C2D8 Repeated ...

Page 398: ...2 0 Disabled C431 Force VFD and LED 0 to 1 1 F126 0 No C432 Test Mode Initiate 0 to 65535 1 F300 1 Clear commands read write C433 Clear All Relay Records Command 0 to 1 1 F126 0 No Contact Outputs Read Write Setting 64 modules C440 Contact Output 1 Name F205 Cont Op 1 C446 Contact Output 1 Operation 0 to 65535 1 F300 0 C447 Contact Output 1 Seal In 0 to 65535 1 F300 0 C448 Latching Output 1 Reset ...

Page 399: ... Contact Output 43 C644 Repeated for Contact Output 44 C650 Repeated for Contact Output 45 C65C Repeated for Contact Output 46 C668 Repeated for Contact Output 47 C674 Repeated for Contact Output 48 C680 Repeated for Contact Output 49 C68C Repeated for Contact Output 50 C698 Repeated for Contact Output 51 C6A4 Repeated for Contact Output 52 C6B0 Repeated for Contact Output 53 C6BC Repeated for Con...

Page 400: ...t Output x State 64 items 0 to 3 1 F131 0 Disabled Direct Inputs Outputs Read Write Setting C880 Direct Device ID 1 to 16 1 F001 1 C881 Direct I O Channel 1 Ring Configuration Function 0 to 1 1 F126 0 No C882 Platform Direct I O Data Rate 64 to 128 kbps 64 F001 64 C883 Direct I O Channel 2 Ring Configuration Function 0 to 1 1 F126 0 No C884 Platform Direct I O Crossover Function 0 to 1 1 F102 0 Di...

Page 401: ...A28 Repeated for Direct Output 13 CA2A Repeated for Direct Output 14 CA2C Repeated for Direct Output 15 CA2E Repeated for Direct Output 16 CA30 Repeated for Direct Output 17 CA32 Repeated for Direct Output 18 CA34 Repeated for Direct Output 19 CA36 Repeated for Direct Output 20 CA38 Repeated for Direct Output 21 CA3A Repeated for Direct Output 22 CA3C Repeated for Direct Output 23 CA3E Repeated fo...

Page 402: ...e 1 GOOSE Ethernet APPID 0 to 16383 1 F001 0 CB22 Remote Device 1 GOOSE Dataset 0 to 8 1 F184 0 Fixed CB23 Repeated for Device 2 CB46 Repeated for Device 3 CB69 Repeated for Device 4 CB8C Repeated for Device 5 CBAF Repeated for Device 6 CBD2 Repeated for Device 7 CBF5 Repeated for Device 8 CC18 Repeated for Device 9 CC3B Repeated for Device 10 CC5E Repeated for Device 11 CC81 Repeated for Device 1...

Page 403: ...Remote Output 6 D238 Repeated for Remote Output 7 D23C Repeated for Remote Output 8 D240 Repeated for Remote Output 9 D244 Repeated for Remote Output 10 D248 Repeated for Remote Output 11 D24C Repeated for Remote Output 12 D250 Repeated for Remote Output 13 D254 Repeated for Remote Output 14 D258 Repeated for Remote Output 15 D25C Repeated for Remote Output 16 D260 Repeated for Remote Output 17 D2...

Page 404: ...tput 25 D304 Repeated for Remote Output 26 D308 Repeated for Remote Output 27 D30C Repeated for Remote Output 28 D310 Repeated for Remote Output 29 D314 Repeated for Remote Output 30 D318 Repeated for Remote Output 31 D31C Repeated for Remote Output 32 Remote Device Status Read Only 16 modules D380 Remote Device 1 StNum 0 to 4294967295 1 F003 0 D382 Remote Device 1 SqNum 0 to 4294967295 1 F003 0 D...

Page 405: ...f ten LSB indicates the number of decimal points to display Example Current values are stored as 32 bit numbers with three decimal places and base units in Amps If the retrieved value is 12345 678 A and the display scale equals 0x0302 then the dis played value on the unit is 12 35 kA F013 POWER_FACTOR SIGNED 16 BIT INTEGER Positive values indicate lagging power factor negative values indicate lead...

Page 406: ...Pole 1 1 Pole 2 3 Pole A 3 3 Pole B F083 ENUMERATION SELECTOR MODES 0 Time Out 1 Acknowledge F084 ENUMERATION SELECTOR POWER UP 0 Restore 1 Synchronize 2 Sync Restore F086 ENUMERATION DIGITAL INPUT DEFAULT STATE 0 Off 1 On 2 Latest Off 3 Latest On F090 ENUMERATION LATCHING OUTPUT TYPE 0 Operate dominant 1 Reset dominant F100 ENUMERATION VT CONNECTION TYPE 0 Wye 1 Delta F101 ENUMERATION MESSAGE DIS...

Page 407: ...8400 10 28800 3 4800 7 57600 11 33600 mask value mask value mask value mask value 0 0 00 30 0 88 60 2 90 90 5 90 1 0 05 31 0 90 61 3 00 91 6 00 2 0 10 32 0 91 62 3 10 92 6 50 3 0 15 33 0 92 63 3 20 93 7 00 4 0 20 34 0 93 64 3 30 94 7 50 5 0 25 35 0 94 65 3 40 95 8 00 6 0 30 36 0 95 66 3 50 96 8 50 7 0 35 37 0 96 67 3 60 97 9 00 8 0 40 38 0 97 68 3 70 98 9 50 9 0 45 39 0 98 69 3 80 99 10 00 10 0 48...

Page 408: ...aneous Overcurrent 6 70 Ground Instantaneous Overcurrent 7 71 Ground Instantaneous Overcurrent 8 72 Ground Instantaneous Overcurrent 9 73 Ground Instantaneous Overcurrent 10 74 Ground Instantaneous Overcurrent 11 75 Ground Instantaneous Overcurrent 12 80 Ground Time Overcurrent 1 81 Ground Time Overcurrent 2 82 Ground Time Overcurrent 3 83 Ground Time Overcurrent 4 bitmask element 84 Ground Time O...

Page 409: ...6 550 Digital Counter 7 551 Digital Counter 8 692 Digital Element 1 693 Digital Element 2 694 Digital Element 3 695 Digital Element 4 bitmask element 696 Digital Element 5 697 Digital Element 6 698 Digital Element 7 699 Digital Element 8 700 Digital Element 9 701 Digital Element 10 702 Digital Element 11 703 Digital Element 12 704 Digital Element 13 705 Digital Element 14 706 Digital Element 15 70...

Page 410: ...ushbutton 5 905 User Programmable Pushbutton 6 906 User Programmable Pushbutton 7 907 User Programmable Pushbutton 8 bitmask element 908 User Programmable Pushbutton 9 909 User Programmable Pushbutton 10 910 User Programmable Pushbutton 11 911 User Programmable Pushbutton 12 912 User Programmable Pushbutton 13 913 User Programmable Pushbutton 14 914 User Programmable Pushbutton 15 915 User Program...

Page 411: ... Disabled 1 Self Reset 2 Latched F138 ENUMERATION OSCILLOGRAPHY FILE TYPE 0 Data File 1 Configuration File 2 Header File F139 ENUMERATION DEMAND CALCULATIONS 0 Thermal Exponential 1 Block Interval 2 Rolling Demand F140 ENUMERATION CURRENT SENS CURRENT VOLTAGE DISABLED 0 Disabled 1 Current 46 A 2 Voltage 280 V 3 Current 4 6 A 4 Current 2 A 5 Notched 4 6 A 6 Notched 2 A F141 ENUMERATION SELF TEST ER...

Page 412: ...mask type bitmask type bitmask type 0 null 7 G 14 N 21 U 1 A 8 H 15 O 22 V 2 B 9 I 16 P 23 W 3 C 10 J 17 Q 24 X 4 D 11 K 18 R 25 Y 5 E 12 L 19 S 26 Z 6 F 13 M 20 T bitmask error bitmask definition 0 Events Cleared 1 Oscillography Triggered 2 Date time Changed 3 Default Settings Loaded 4 Test Mode On 5 Test Mode Off 6 Power On 7 Power Off 8 Relay In Service 9 Relay Out Of Service 10 Watchdog Reset ...

Page 413: ... 26 42 RTD 42 10 RTD 10 27 RTD 27 43 RTD 43 11 RTD 11 28 RTD 28 44 RTD 44 12 RTD 12 29 RTD 29 45 RTD 45 13 RTD 13 30 RTD 30 46 RTD 46 14 RTD 14 31 RTD 31 47 RTD 47 15 RTD 15 32 RTD 32 48 RTD 48 16 RTD 16 bitmask value bitmask value 0 NONE 35 UserSt 3 1 DNA 1 36 UserSt 4 2 DNA 2 37 UserSt 5 3 DNA 3 38 UserSt 6 4 DNA 4 39 UserSt 7 5 DNA 5 40 UserSt 8 6 DNA 6 41 UserSt 9 7 DNA 7 42 UserSt 10 8 DNA 8 ...

Page 414: ...Network UDP F178 ENUMERATION DATA LOGGER RATES 0 1 sec 1 1 min 2 5 min 3 10 min 4 15 min 5 20 min 6 30 min 7 60 min 8 15 ms 9 30 ms 10 100 ms 11 500 ms F179 ENUMERATION NEGATIVE SEQUENCE DIRECTIONAL OVERCURRENT TYPE 0 Neg Sequence 1 Zero Sequence F180 ENUMERATION PHASE GROUND 0 PHASE 1 GROUND F181 ENUMERATION ODD EVEN NONE 0 ODD 1 EVEN 2 NONE F183 ENUMERATION AC INPUT WAVEFORMS F184 ENUMERATION RE...

Page 415: ... ENUMERATION TEST ENUMERATION 0 Test Enumeration 0 1 Test Enumeration 1 F226 ENUMERATION REMOTE INPUT OUTPUT TRANSFER METHOD 0 None 1 GSSE 2 GOOSE F227 ENUMERATION RELAY SERVICE STATUS 0 Unknown 1 Relay In Service 2 Relay Out Of Service bitmsk keypress bitmsk keypress 0 use between real keys 23 Reset 24 User 1 1 1 25 User 2 2 2 26 User 3 3 3 27 User programmable key 1 4 4 28 User programmable key ...

Page 416: ...TotVA mag f 297 MMXU2 MX TotPF mag f 298 MMXU2 MX Hz mag f 299 MMXU2 MX PPV phsAB cVal mag f 300 MMXU2 MX PPV phsAB cVal ang f 301 MMXU2 MX PPV phsBC cVal mag f 302 MMXU2 MX PPV phsBC cVal ang f 303 MMXU2 MX PPV phsCA cVal mag f 304 MMXU2 MX PPV phsCA cVal ang f 305 MMXU2 MX PhV phsA cVal mag f 306 MMXU2 MX PhV phsA cVal ang f 307 MMXU2 MX PhV phsB cVal mag f 308 MMXU2 MX PhV phsB cVal ang f 309 M...

Page 417: ...400 MMXU4 MX VA phsB cVal mag f 401 MMXU4 MX VA phsC cVal mag f 402 MMXU4 MX PF phsA cVal mag f 403 MMXU4 MX PF phsB cVal mag f value GOOSE dataset item 404 MMXU4 MX PF phsC cVal mag f 405 MMXU5 MX TotW mag f 406 MMXU5 MX TotVAr mag f 407 MMXU5 MX TotVA mag f 408 MMXU5 MX TotPF mag f 409 MMXU5 MX Hz mag f 410 MMXU5 MX PPV phsAB cVal mag f 411 MMXU5 MX PPV phsAB cVal ang f 412 MMXU5 MX PPV phsBC cV...

Page 418: ...X AnIn10 mag f 489 GGIO4 MX AnIn11 mag f 490 GGIO4 MX AnIn12 mag f 491 GGIO4 MX AnIn13 mag f 492 GGIO4 MX AnIn14 mag f 493 GGIO4 MX AnIn15 mag f 494 GGIO4 MX AnIn16 mag f 495 GGIO4 MX AnIn17 mag f 496 GGIO4 MX AnIn18 mag f 497 GGIO4 MX AnIn19 mag f 498 GGIO4 MX AnIn20 mag f 499 GGIO4 MX AnIn21 mag f 500 GGIO4 MX AnIn22 mag f 501 GGIO4 MX AnIn23 mag f 502 GGIO4 MX AnIn24 mag f 503 GGIO4 MX AnIn25 m...

Page 419: ...40 OR 2 to 16 inputs 42 AND 2 to 16 inputs 44 NOR 2 to 16 inputs 46 NAND 2 to 16 inputs 48 TIMER 1 to 32 50 ASSIGN VIRTUAL OUTPUT 1 to 96 52 SELF TEST ERROR see F141 for range 56 ACTIVE SETTING GROUP 1 to 6 62 MISCELLANEOUS EVENTS see F146 for range 64 to 127 ELEMENT STATES F400 UR_UINT16 CT VT BANK SELECTION F491 ENUMERATION ANALOG INPUT MODE 0 Default Value 1 Last Known F500 UR_UINT16 PACKED BIT...

Page 420: ...olute F516 ENUMERATION ELEMENT COMPARE MODE 0 Level 1 Delta F518 ENUMERATION FLEXELEMENT UNITS 0 Milliseconds 1 Seconds 2 Minutes F519 ENUMERATION NON VOLATILE LATCH 0 Reset Dominant 1 Set Dominant F522 ENUMERATION TRANSDUCER DCMA OUTPUT RANGE 0 1 to 1 mA 1 0 to 1 mA 2 4 to 20 mA F523 ENUMERATION DNP OBJECTS 20 22 AND 23 DEFAULT VARIATION F524 ENUMERATION DNP OBJECT 21 DEFAULT VARIATION F525 ENUME...

Page 421: ...be used as Flex Analogs basically all metering quantities used in protection value keypress value keypress value keypress 0 None 15 3 33 User PB 3 1 Menu 16 Enter 34 User PB 4 2 Message Up 17 Message Down 35 User PB 5 3 7 18 0 36 User PB 6 4 8 19 Decimal 37 User PB 7 5 9 20 38 User PB 8 6 Help 21 Value Up 39 User PB 9 7 Message Left 22 Value Down 40 User PB 10 8 4 23 Reset 41 User PB 11 9 5 24 Use...

Page 422: ...B 72 F35 Multiple Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIXB B ...

Page 423: ...uring Message Specification MMS at the upper application layer for transfer of real time data This protocol has been in existence for several of years and provides a set of services suitable for the transfer of data within a substation LAN environment Actual MMS protocol services are mapped to IEC 61850 abstract ser vices in IEC 61850 8 1 The F35 relay supports IEC 61850 server services over both ...

Page 424: ...e used for SOE logs since the buffering capability reduces the chances of missing data state changes Unbuffered reporting should generally be used for local status display C 2 3 GGIO2 DIGITAL CONTROL VALUES The GGIO2 logical node is available to provide access to the F35 virtual inputs Virtual inputs are single point control binary values that can be written by clients They are generally used as c...

Page 425: ...phase power factor MMXU1 MX Hz frequency MMXU1 MX PPV phsAB phase AB voltage magnitude and angle MMXU1 MX PPV phsBC phase BC voltage magnitude and angle MMXU1 MX PPV phsCA Phase CA voltage magnitude and angle MMXU1 MX PhV phsA phase AG voltage magnitude and angle MMXU1 MX PhV phsB phase BG voltage magnitude and angle MMXU1 MX PhV phsC phase CG voltage magnitude and angle MMXU1 MX A phsA phase A cu...

Page 426: ...equence overvoltage RBRF breaker failure RREC autoreclosure RPSB power swing detection RFLO fault locator XCBR breaker control The protection elements listed above contain start pickup and operate flags For example the start flag for PIOC1 is PIOC1 ST Str general The operate flag for PIOC1 is PIOC1 ST Op general For the F35 protection elements these flags take their values from the pickup and oper...

Page 427: ...time of the last change of either the value or quality flags of the data item To accomplish this functionality all IEC 61850 data items must be regularly scanned for data changes and the timestamp updated when a change is detected regardless of the connection status of any IEC 61850 cli ents For applications where there is no IEC 61850 client in use the IEC 61850 SERVER SCANNING setting can be pro...

Page 428: ...nnection for greater than two minutes the connection will be aborted by the F35 This frees up the con nection to be used by other clients Therefore when using IEC 61850 reporting clients should configure report control block items such that an integrity report will be issued at least every 2 minutes 120000 ms This ensures that the F35 will not abort the connection If other MMS data is being polled...

Page 429: ... in two pre defined data structures named DNA and UserSt Each DNA and UserSt item is referred to as a bit pair GSSE messages are transmit ted in response to state changes in any of the data points contained in the message GSSE messages always contain the same number of DNA and UserSt bit pairs Depending the on the configuration only some of these bit pairs may have val ues that are of interest to ...

Page 430: ...ransfer between UR series IEDs and devices from other manufacturers Fixed GOOSE is recommended for applications that require GOOSE data transfer between UR series IEDs IEC 61850 GOOSE messaging contains a number of configurable parameters all of which must be correct to achieve the successful transfer of data It is critical that the configured datasets at the transmission and reception devices are...

Page 431: ...tus Boolean value and a floating point ana log value This matches the transmission dataset configuration above 2 Configure the GOOSE service settings by making the following changes in the INPUTS OUTPUTS ÖØ REMOTE DEVICES ÖØ REMOTE DEVICE 1 settings menu Set REMOTE DEVICE 1 ID to match the GOOSE ID string for the transmitting device Enter GOOSEOut_1 Set REMOTE DEVICE 1 ETYPE APPID to match the Eth...

Page 432: ...it set Thus if the local MAC address is 00 A0 F4 01 02 03 then the destination MAC address will be 01 A0 F4 01 02 03 C 4 6 GSSE ID AND GOOSE ID SETTINGS GSSE messages contain an identifier string used by receiving devices to identify the sender of the message defined in IEC 61850 part 8 1 as GsID This is a programmable 65 character string This string should be chosen to provide a descriptive name ...

Page 433: ...iguration process for IEC 61850 BDA Basic Data Attribute that is not structured DAI Instantiated Data Attribute DO Data Object type or instance depending on the context 842790A1 CDR Ethernet System configurator SCD file System specification tool SSD file System specification data ICD file 2 Process of creating ICD vendor 2 Creating ICD GE Multilin EnerVista UR Setup ICD file 1 IED UR series OR ICD...

Page 434: ...file SCD to set communication configuration parame ters that is required addresses reception GOOSE datasets IDs of incoming GOOSE datasets etc for the IED The IED configurator functionality is implemented in the GE Multilin EnerVista UR Setup software C 5 2 CONFIGURING IEC 61850 SETTINGS Before creating an ICD file the user can customize the IEC 61850 related settings for the IED For example the I...

Page 435: ...gurators we recommend configuring transmission GOOSE for GE Multilin IEDs before creating the ICD and strictly within EnerVista UR Setup software or the front panel display access through the Settings Product Setup Com munications IEC 61850 GSSE GOOSE Configuration Transmission Tx Configurable GOOSE menu tree in EnerVista UR Setup Configurable reception GOOSE which includes eight configurable data...

Page 436: ...dress node contains the address parameters of the access point The GSE node provides the address element for stat ing the control block related address parameters where IdInst is the instance identification of the logical device within the IED on which the control block is located and cbName is the name of the control block The IED node describes the pre configuration of an IED its access points t...

Page 437: ...st DataSet name Other DataSet elements FCDA fc doName daName IdInst prefix InClass InInst Other FCDA elements DOI name SDI name Val Text Other DOI elements GSEControl name datSet type confRev appID LN InType InClass prefix inst DataSet name FCDA IdInst prefix InClass InInst doName fc Other FCDA elements ReportControl name datSet intgPd rptID confRev buffered TrgOps dchg OptFields seqNum RptEnabled...

Page 438: ...s SDO The attribute DA has a func tional constraint and can either have a basic type be an enumeration or a structure of a DAType The DAType is built from BDA elements defining the structure elements which again can be BDA elements of have a base type such as DA Figure 0 5 ICD FILE STRUCTURE DATATYPETEMPLATES NODE 842798A1 CDR DataTypeTemplates LNodeType id InClass DO name type Other LNodeType ele...

Page 439: ...the procedure is pretty much the same First a substation project must be created either as an empty template or with some system information by importing a system specification file SSD Then IEDs are added to the substation Since each IED is represented by its associated ICD the ICD files are imported into the substation project and the system configurator validates the ICD files during the import...

Page 440: ...CD file and its version and specifies options for the mapping of names to signals The Substation node describes the substation parameters Figure 0 7 SCD FILE STRUCTURE SUBSTATION NODE 842791A1 CDR SCL Header id version revision toolID nameStructure IED Section IED 2 Communication IED Section IED 1 Substation Other IED Sections DataTypeTemplates 842792A1 CDR Substation EquipmentContainer VoltageLev...

Page 441: ...onnectedAP node describes the IED access point connected to this sub network The Address node contains the address parameters of the access point The GSE node provides the address element for stat ing the control block related address parameters where IdInst is the instance identification of the logical device within the IED on which the control block is located and cbName is the name of the contr...

Page 442: ... update the F35 with the new configuration from an SCD file with the EnerVista UR Setup software 1 Right click anywhere in the files panel and select the Import Contents From SCD File item 2 Select the saved SCD file and click Open 842794A1 CDR IED Section IED 1 AccessPoint name Server Authentication none LDevice inst LN0 InType InClass inst DataSet elements DOI elements Inputs GSEControl elements...

Page 443: ...han one GE Multilin IED defined in the SCD file the software prompt the user to save a UR series set tings file for each IED 4 After the URS file is created modify any settings if required 5 To update the relay with the new settings right click on the settings file in the settings tree and select the Write Set tings File to Device item 6 The software will prompt for the target device Select the ta...

Page 444: ...23 SCSM IEC 61850 9 2 used B24 SCSM other GENERIC SUBSTATION EVENT MODEL GSE B31 Publisher side O Yes B32 Subscriber side Yes TRANSMISSION OF SAMPLED VALUE MODEL SVC B41 Publisher side O B42 Subscriber side SERVICES SERVER PUBLISHER UR FAMILY IF SERVER SIDE B11 SUPPORTED M1 Logical device c2 Yes M2 Logical node c3 Yes M3 Data c4 Yes M4 Data set c5 Yes M5 Substitution O M6 Setting group control O R...

Page 445: ...4 data set name M8 5 data reference M8 6 BufTm M8 7 IntgPd M8 8 GI Logging O M9 Log control O M9 1 IntgPd M10 Log O M11 Control M Yes IF GSE B31 32 IS SUPPORTED GOOSE O Yes M12 1 entryID M12 2 DataReflnc M13 GSSE O Yes IF SVC B41 B42 IS SUPPORTED M14 Multicast SVC O M15 Unicast SVC O M16 Time M Yes M17 File transfer O Yes SERVICES AA TP MC SERVER PUBLISHER UR FAMILY SERVER CLAUSE 6 S1 ServerDirect...

Page 446: ...chg change qchg S24 3 data update dupd S25 GetBRCBValues TP c6 Yes S26 SetBRCBValues TP c6 Yes UNBUFFERED REPORT CONTROL BLOCK URCB S27 Report TP c6 Yes S27 1 data change dchg Yes S27 2 qchg change qchg S27 3 data update dupd S28 GetURCBValues TP c6 Yes S29 SetURCBValues TP c6 Yes LOGGING CLAUSE 14 LOG CONTROL BLOCK S30 GetLCBValues TP M S31 SetLCBValues TP M LOG S32 QueryLogByTime TP M S33 QueryL...

Page 447: ...EL SVC CLAUSE 16 MULTICAST SVC S45 SendMSVMessage MC c10 S46 GetMSVCBValues TP O S47 SetMSVCBValues TP O UNICAST SVC S48 SendUSVMessage MC c10 S49 GetUSVCBValues TP O S50 SetUSVCBValues TP O CONTROL CLAUSE 16 4 8 S51 Select O Yes S52 SelectWithValue TP O S53 Cancel TP O Yes S54 Operate TP M Yes S55 Command Termination TP O S56 TimeActivated Operate TP O FILE TRANSFER CLAUSE 20 S57 GetFile TP M Yes...

Page 448: ...f change of frequency PHAR Harmonic restraint PHIZ Ground detector PIOC Instantaneous overcurrent Yes PMRI Motor restart inhibition PMSS Motor starting time supervision POPF Over power factor PPAM Phase angle measuring PSCH Protection scheme PSDE Sensitive directional earth fault PTEF Transient earth fault PTOC Time overcurrent Yes PTOF Overfrequency PTOV Overvoltage Yes PTRC Protection trip condi...

Page 449: ...VCO Voltage control M LOGICAL NODES FOR METERING AND MEASUREMENT MDIF Differential measurements MHAI Harmonics or interharmonics MHAN Non phase related harmonics or interharmonic MMTR Metering MMXN Non phase related measurement Yes MMXU Measurement Yes MSQI Sequence and imbalance MSTA Metering statistics S LOGICAL NODES FOR SENSORS AND MONITORING SARC Monitoring and diagnostics for arcs SIMG Insul...

Page 450: ...attery ZBSH Bushing ZCAB Power cable ZCAP Capacitor bank ZCON Converter ZGEN Generator ZGIL Gas insulated line ZLIN Power overhead line ZMOT Motor ZREA Reactor ZRRC Rotating reactive component ZSAR Surge arrestor ZTCF Thyristor controlled frequency converter ZTRC Thyristor controlled reactive component Table 0 1 IEC 61850 LOGICAL NODES Sheet 3 of 3 NODES UR FAMILY ...

Page 451: ...nterchange Circuit V 24 V 28 Recommended if 1200 bits s Balanced Interchange Circuit X 24 X 27 100 bits sec 200 bits sec 300 bits sec 600 bits sec 1200 bits sec 2400 bits sec 4800 bits sec 9600 bits sec 2400 bits sec 4800 bits sec 9600 bits sec 19200 bits sec 38400 bits sec 56000 bits sec 64000 bits sec Unbalanced Interchange Circuit V 24 V 28 Standard Unbalanced Interchange Circuit V 24 V 28 Reco...

Page 452: ... following 4 used in standard direction not used cannot be selected in IEC 60870 5 104 standard Process information in monitor direction 4 1 Single point information M_SP_NA_1 2 Single point information with time tag M_SP_TA_1 3 Double point information M_DP_NA_1 4 Double point information with time tag M_DP_TA_1 5 Step position information M_ST_NA_1 6 Step position information with time tag M_ST_...

Page 453: ...of protection equipment with time tag CP56Time2a M_EP_TE_1 40 Packed output circuit information of protection equipment with time tag CP56Time2a M_EP_TF_1 4 45 Single command C_SC_NA_1 46 Double command C_DC_NA_1 47 Regulating step command C_RC_NA_1 48 Set point command normalized value C_SE_NA_1 49 Set point command scaled value C_SE_NB_1 50 Set point command short floating point value C_SE_NC_1 ...

Page 454: ... Call directory select file call file call section F_SC_NA_1 123 Last section last segment F_LS_NA_1 124 Ack file ack section F_AF_NA_1 125 Segment F_SG_NA_1 126 Directory blank or X available only in monitor standard direction C_CD_NA_1 TYPE IDENTIFICATION CAUSE OF TRANSMISSION NO MNEMONIC 1 2 3 4 5 6 7 8 9 10 11 12 13 20 to 36 37 to 41 44 45 46 47 1 M_SP_NA_1 X X X X X 2 M_SP_TA_1 3 M_DP_NA_1 4 ...

Page 455: ...C_RC_NA_1 48 C_SE_NA_1 49 C_SE_NB_1 50 C_SE_NC_1 51 C_BO_NA_1 58 C_SC_TA_1 X X X X X 59 C_DC_TA_1 60 C_RC_TA_1 TYPE IDENTIFICATION CAUSE OF TRANSMISSION NO MNEMONIC 1 2 3 4 5 6 7 8 9 10 11 12 13 20 to 36 37 to 41 44 45 46 47 PERIODIC CYCLIC BACKGROUND SCAN SPONTANEOUS INITIALIZED REQUEST OR REQUESTED ACTIVATION ACTIVATION CONFIRMATION DEACTIVATION DEACTIVATION CONFIRMATION ACTIVATION TERMINATION R...

Page 456: ...E_NB_1 112 P_ME_NC_1 X X X 113 P_AC_NA_1 120 F_FR_NA_1 121 F_SR_NA_1 122 F_SC_NA_1 123 F_LS_NA_1 124 F_AF_NA_1 125 F_SG_NA_1 126 F_DR_TA_1 TYPE IDENTIFICATION CAUSE OF TRANSMISSION NO MNEMONIC 1 2 3 4 5 6 7 8 9 10 11 12 13 20 to 36 37 to 41 44 45 46 47 PERIODIC CYCLIC BACKGROUND SCAN SPONTANEOUS INITIALIZED REQUEST OR REQUESTED ACTIVATION ACTIVATION CONFIRMATION DEACTIVATION DEACTIVATION CONFIRMAT...

Page 457: ...E_TC_1 and M_ME_TF_1 Station interrogation Clock synchronization 4 Clock synchronization optional see Clause 7 6 Command transmission 4 Direct command transmission Direct setpoint command transmission 4 Select and execute command Select and execute setpoint command 4 C_SE ACTTERM used 4 No additional definition 4 Short pulse duration duration determined by a system parameter in the outstation 4 Lo...

Page 458: ...ssion of sequences of events Transmission of sequences of recorded analog values File transfer in control direction Transparent file Background scan Background scan Acquisition of transmission delay Acquisition of transmission delay Definition of time outs Maximum range of values for all time outs 1 to 255 s accuracy 1 s Maximum number of outstanding I format APDUs k and latest acknowledge APDUs w...

Page 459: ...ermined by the Internet Architecture Board IAB It offers a broad spectrum of actual standards used in the Inter net The suitable selection of documents from RFC 2200 defined in this standard for given projects has to be chosen by the user of this standard 4 Ethernet 802 3 Serial X 21 interface Other selection s from RFC 2200 list below if selected D 1 2 POINTS LIST The IEC 60870 5 104 data points ...

Page 460: ...D 10 F35 Multiple Feeder Protection System GE Multilin D 1 IEC 60870 5 104 PROTOCOL APPENDIXD D ...

Page 461: ...ed in addition to the Highest DNP Levels Supported the complete list is described in the attached table Binary Inputs Object 1 Binary Input Changes Object 2 Binary Outputs Object 10 Control Relay Output Block Object 12 Binary Counters Object 20 Frozen Counters Object 21 Counter Change Event Object 22 Frozen Counter Event Object 23 Analog Inputs Object 30 Analog Input Changes Object 32 Analog Deadb...

Page 462: ...ry Outputs 4 Never Always Sometimes Configurable SELECT OPERATE Never 4 Always Sometimes Configurable DIRECT OPERATE Never 4 Always Sometimes Configurable DIRECT OPERATE NO ACK Never 4 Always Sometimes Configurable Count 1 4 Never Always Sometimes Configurable Pulse On Never Always 4 Sometimes Configurable Pulse Off Never Always 4 Sometimes Configurable Latch On Never Always 4 Sometimes Configurab...

Page 463: ...nfigurable Only certain objects Sometimes attach explanation 4 ENABLE DISABLE unsolicited Function codes supported Sends Static Data in Unsolicited Responses 4 Never When Device Restarts When Status Flags Change No other options are permitted Default Counter Object Variation No Counters Reported Configurable attach explanation 4 Default Object 20 Default Variation 1 4 Point by point list attached ...

Page 464: ...esp 17 28 index 3 Binary Input Change with Relative Time 1 read 06 no range or all 07 08 limited quantity 10 0 Binary Output Status Variation 0 is used to request default variation 1 read 00 01 start stop 06 no range or all 07 08 limited quantity 17 28 index 2 Binary Output Status 1 read 00 01 start stop 06 no range or all 07 08 limited quantity 17 28 index 129 response 00 01 start stop 17 28 inde...

Page 465: ... Variation 0 is used to request default variation 1 read 06 no range or all 07 08 limited quantity 1 32 Bit Counter Change Event 1 read 06 no range or all 07 08 limited quantity 129 response 130 unsol resp 17 28 index 2 16 Bit Counter Change Event 1 read 06 no range or all 07 08 limited quantity 129 response 130 unsol resp 17 28 index 5 32 Bit Counter Change Event with Time 1 read 06 no range or a...

Page 466: ...response 130 unsol resp 17 28 index 3 32 Bit Analog Change Event with Time 1 read 06 no range or all 07 08 limited quantity 129 response 130 unsol resp 17 28 index 4 16 Bit Analog Change Event with Time 1 read 06 no range or all 07 08 limited quantity 129 response 130 unsol resp 17 28 index 5 short floating point Analog Change Event without Time 1 read 06 no range or all 07 08 limited quantity 129...

Page 467: ...26 close 30 abort 5b free format 129 response 130 unsol resp 5b free format 5 File transfer 1 read 2 write 5b free format 129 response 130 unsol resp 5b free format 6 File transfer status 129 response 130 unsol resp 5b free format 7 File descriptor 28 get file info 5b free format 129 response 130 unsol resp 5b free format 80 1 Internal Indications 1 read 00 01 start stop index 7 129 response 00 01...

Page 468: ...nction is performed on a binary counter point the frozen value is available in the corresponding frozen counter point BINARY INPUT POINTS Static Steady State Object Number 1 Change Event Object Number 2 Request Function Codes supported 1 read 22 assign class Static Variation reported when variation 0 requested 2 Binary Input with status Configurable Change Event Variation reported when variation 0...

Page 469: ...Virtual Input 15 15 Virtual Input 16 16 Virtual Input 17 17 Virtual Input 18 18 Virtual Input 19 19 Virtual Input 20 20 Virtual Input 21 21 Virtual Input 22 22 Virtual Input 23 23 Virtual Input 24 24 Virtual Input 25 25 Virtual Input 26 26 Virtual Input 27 27 Virtual Input 28 28 Virtual Input 29 29 Virtual Input 30 30 Virtual Input 31 31 Virtual Input 32 32 Virtual Input 33 33 Virtual Input 34 34 ...

Page 470: ...0 freeze and clear noack 22 assign class Static Variation reported when variation 0 requested 1 32 Bit Binary Counter with Flag Change Event Variation reported when variation 0 requested 1 32 Bit Counter Change Event without time Change Event Buffer Size 10 Default Class for all points 3 FROZEN COUNTERS Static Steady State Object Number 21 Change Event Object Number 23 Request Function Codes suppo...

Page 471: ...ds for all Analog Input points are in the same units as the Analog Input quantity For example an Analog Input quantity measured in volts has a corresponding deadband in units of volts This is in conformance with DNP Technical Bul letin 9809 001 Analog Input Reporting Deadband Relay settings are available to set default deadband values according to data type Deadbands for individual Analog Input Po...

Page 472: ...E 12 F35 Multiple Feeder Protection System GE Multilin E 2 DNP POINT LISTS APPENDIXE E ...

Page 473: ...ruary 2003 URF 043 1601 0106 D2 3 2x 02 June 2003 URX 084 1601 0106 E1 3 3x 01 May 2003 URX 080 1601 0106 E2 3 3x 29 May 2003 URX 083 1601 0106 F1 3 4x 10 December 2003 URX 111 1601 0106 F2 3 4x 09 February 2004 URX 115 1601 0106 G1 4 0x 23 March 2004 URX 123 1601 0106 G2 4 0x 17 May 2004 URX 136 1601 0106 H1 4 2x 30 June 2004 URX 145 1601 0106 H2 4 2x 23 July 2004 URX 151 1601 0106 J1 4 4x 15 Sep...

Page 474: ...ed USING SETTINGS FILES section 5 46 5 46 Update Updated USER PROGRAMMABLE PUSHBUTTONS section 5 73 5 73 Update Updated DISCONNECT SWITCHES section 5 135 5 135 Update Updated DIGITAL ELEMENTS section 5 165 Add Added IEC 61850 GOOSE ANALOGS section B 55 B 55 Update Updated DATA FORMATS section Table F 2 MAJOR UPDATES FOR F35 MANUAL REVISION S4 PAGE S3 PAGE S4 CHANGE DESCRIPTION Title Title Update M...

Page 475: ...12 2 13 Update Updated COMMUNICATIONS specifications section 3 35 3 36 Update Updated IEEE C37 94 INTERFACE section 3 40 Add Added MANAGED ETHERNET SWITCH MODULES section 4 23 Add Added BREAKER CONTROL section 5 8 5 8 Update Updated PASSWORD SECURITY section now titled SECURITY 5 32 Add Added ETHERNET SWITCH sub section 5 45 5 46 Update Updated USER PROGRAMMABLE PUSHBUTTONS section 5 69 Add Added ...

Page 476: ...high set FDL Fault Detector low set FLA Full Load Current FO Fiber Optic FREQ Frequency FSK Frequency Shift Keying FTP File Transfer Protocol FxE FlexElement FWD Forward G Generator GE General Electric GND Ground GNTR Generator GOOSE General Object Oriented Substation Event GPS Global Positioning System HARM Harmonic Harmonics HCT High Current Time HGF High Impedance Ground Fault CT HIZ High Imped...

Page 477: ...erminal Unit RX Rx Receive Receiver s second S Sensitive SAT CT Saturation SBO Select Before Operate SCADA Supervisory Control and Data Acquisition SEC Secondary SEL Select Selector Selection SENS Sensitive SEQ Sequence SIR Source Impedance Ratio SNTP Simple Network Time Protocol SRC Source SSB Single Side Band SSEL Session Selector STATS Statistics SUPN Supervision SUPV Supervise Supervision SV S...

Page 478: ...ve and it is returned with all transportation charges prepaid to an authorized service centre or the factory Repairs or replacement under war ranty will be made without charge Warranty shall not apply to any relay which has been subject to misuse negligence accident incorrect installation or use not in accordance with instructions nor any unit that has been altered outside a GE Multilin authorized...

Page 479: ...AUXILIARY VOLTAGE METERING 6 15 B BANKS 5 6 5 64 5 65 BATTERY FAILURE 7 5 BINARY INPUT POINTS E 8 BINARY OUTPUT POINTS E 9 BLOCK DIAGRAM 1 3 BLOCK SETTING 5 5 BREAKER ARCING CURRENT actual values 6 23 clearing 5 13 7 2 FlexLogic operands 5 85 logic 5 144 measurement 5 144 Modbus registers B 13 B 28 settings 5 143 specifications 2 7 BREAKER CONTROL control of 2 breakers 4 23 description 4 23 dual b...

Page 480: ...s B 7 Modbus registers B 10 B 19 settings 5 38 specifications 2 9 via COMTRADE B 6 DATE 7 2 DCMA INPUTS 6 20 Modbus registers B 15 B 29 settings 5 166 specifications 2 10 DCMA OUTPUTS description 3 21 Modbus registers B 35 settings 5 169 specifications 2 12 DEFINITE TIME CURVE 5 107 5 115 DEMAND Modbus registers B 12 B 13 B 22 DEMAND METERING actual values 6 16 settings 5 40 specifications 2 10 DE...

Page 481: ...04 EQUIPMENT MISMATCH ERROR 7 4 ETHERNET actual values 6 7 configuration 1 8 error messages 7 6 Modbus registers B 10 quick connect 1 10 settings 5 15 ETHERNET SWITCH actual values 6 9 configuration 3 41 hardware 3 40 Modbus registers B 18 overview 3 40 saving setting files 3 42 settings 5 32 uploading setting files 3 42 EVENT CAUSE INDICATORS 4 15 4 16 EVENT RECORDER actual values 6 21 clearing 5...

Page 482: ... 113 specifications 2 7 GROUPED ELEMENTS 5 103 GSSE 5 157 5 158 6 6 H HALF DUPLEX B 1 HARMONICS METERING specifications 2 10 HTTP PROTOCOL 5 29 I I2T CURVES 5 107 IAC CURVES 5 106 IEC 60870 5 104 PROTOCOL interoperability document D 1 Modbus registers B 18 settings 5 29 IEC 61850 GOOSE ANALOGS settings 5 165 IEC 61850 PROTOCOL device ID 5 157 DNA2 assignments 5 158 error messages 7 6 Modbus regist...

Page 483: ...lography B 6 passwords B 7 read write settings actual values B 3 settings 5 15 5 32 store multiple settings B 5 store single setting B 4 supported function codes B 3 user map 5 32 B 10 B 22 MODEL INFORMATION 6 24 MODIFICATION FILE NUMBER 6 24 MODULE FAILURE ERROR 7 4 MODULES communications 3 23 contact inputs outputs 3 15 3 17 3 18 CT 3 12 CT VT 3 11 5 6 direct inputs outputs 3 29 insertion 3 5 3 ...

Page 484: ...HASE TIME OVERCURRENT see entry for PHASE TOC PHASE TOC FlexLogic operands 5 87 logic 5 109 Modbus registers B 25 settings 5 108 specifications 2 7 PHASE UNDERVOLTAGE FlexLogic operands 5 87 logic 5 117 Modbus registers B 28 settings 5 117 specifications 2 7 PHONE NUMBERS 1 1 POWER METERING Modbus registers B 11 specifications 2 9 values 6 15 POWER SUPPLY description 3 10 low range 2 11 specificat...

Page 485: ... 2 SITE LIST CREATING 4 1 SNTP PROTOCOL error messages 7 6 Modbus registers B 19 settings 5 30 SOFTWARE installation 1 5 see entry for ENERVISTA UR SETUP SOFTWARE ARCHITECTURE 1 4 SOFTWARE PC see entry for EnerVista UR Setup SOURCE FREQUENCY 6 17 SOURCE TRANSFER SCHEMES 5 115 SOURCES description 5 5 example use of 5 67 metering 6 13 Modbus registers B 21 settings 5 66 5 67 SPECIFICATIONS 2 7 ST TY...

Page 486: ...2 settings 5 52 5 54 specifications 2 8 USER PROGRAMMABLE LEDs custom labeling 4 21 defaults 4 16 description 4 15 4 16 Modbus registers B 19 settings 5 43 specifications 2 8 USER PROGRAMMABLE PUSHBUTTONS FlexLogic operands 5 90 Modbus registers B 23 B 30 settings 5 46 specifications 2 8 USER PROGRAMMABLE SELF TESTS Modbus registers B 20 settings 5 44 USERST 1 BIT PAIR 5 158 V VAR HOURS 2 9 6 16 V...

Reviews: