5-106
F35 Multiple Feeder Protection System
GE Multilin
5.5 GROUPED ELEMENTS
5 SETTINGS
5
IAC CURVES:
The curves for the General Electric type IAC relay family are derived from the formulae:
,
(EQ 5.10)
where:
T
= operate time (in seconds),
TDM
= Multiplier setting,
I
= Input current,
I
pkp
= Pickup Current setting,
A to
E
=
constants,
t
r
= characteristic constant, and
T
RESET
= reset time in seconds (assuming energy capacity is 100%
and
RESET
is “Timed”)
Table 5–16: GE TYPE IAC INVERSE TIME CURVE CONSTANTS
IAC CURVE SHAPE
A
B
C
D
E
T
R
IAC Extreme Inverse
0.0040
0.6379
0.6200
1.7872
0.2461
6.008
IAC Very Inverse
0.0900
0.7955
0.1000
–1.2885
7.9586
4.678
IAC Inverse
0.2078
0.8630
0.8000
–0.4180
0.1947
0.990
IAC Short Inverse
0.0428
0.0609
0.6200
–0.0010
0.0221
0.222
Table 5–17: IAC CURVE TRIP TIMES
MULTIPLIER
(TDM)
CURRENT ( I / I
pickup
)
1.5
2.0
3.0
4.0
5.0
6.0
7.0
8.0
9.0
10.0
IAC EXTREMELY INVERSE
0.5
1.699
0.749
0.303
0.178
0.123
0.093
0.074
0.062
0.053
0.046
1.0
3.398
1.498
0.606
0.356
0.246
0.186
0.149
0.124
0.106
0.093
2.0
6.796
2.997
1.212
0.711
0.491
0.372
0.298
0.248
0.212
0.185
4.0
13.591
5.993
2.423
1.422
0.983
0.744
0.595
0.495
0.424
0.370
6.0
20.387
8.990
3.635
2.133
1.474
1.115
0.893
0.743
0.636
0.556
8.0
27.183
11.987
4.846
2.844
1.966
1.487
1.191
0.991
0.848
0.741
10.0
33.979
14.983
6.058
3.555
2.457
1.859
1.488
1.239
1.060
0.926
IAC VERY INVERSE
0.5
1.451
0.656
0.269
0.172
0.133
0.113
0.101
0.093
0.087
0.083
1.0
2.901
1.312
0.537
0.343
0.266
0.227
0.202
0.186
0.174
0.165
2.0
5.802
2.624
1.075
0.687
0.533
0.453
0.405
0.372
0.349
0.331
4.0
11.605
5.248
2.150
1.374
1.065
0.906
0.810
0.745
0.698
0.662
6.0
17.407
7.872
3.225
2.061
1.598
1.359
1.215
1.117
1.046
0.992
8.0
23.209
10.497
4.299
2.747
2.131
1.813
1.620
1.490
1.395
1.323
10.0
29.012
13.121
5.374
3.434
2.663
2.266
2.025
1.862
1.744
1.654
IAC INVERSE
0.5
0.578
0.375
0.266
0.221
0.196
0.180
0.168
0.160
0.154
0.148
1.0
1.155
0.749
0.532
0.443
0.392
0.360
0.337
0.320
0.307
0.297
2.0
2.310
1.499
1.064
0.885
0.784
0.719
0.674
0.640
0.614
0.594
4.0
4.621
2.997
2.128
1.770
1.569
1.439
1.348
1.280
1.229
1.188
6.0
6.931
4.496
3.192
2.656
2.353
2.158
2.022
1.921
1.843
1.781
8.0
9.242
5.995
4.256
3.541
3.138
2.878
2.695
2.561
2.457
2.375
10.0
11.552
7.494
5.320
4.426
3.922
3.597
3.369
3.201
3.072
2.969
IAC SHORT INVERSE
0.5
0.072
0.047
0.035
0.031
0.028
0.027
0.026
0.026
0.025
0.025
1.0
0.143
0.095
0.070
0.061
0.057
0.054
0.052
0.051
0.050
0.049
2.0
0.286
0.190
0.140
0.123
0.114
0.108
0.105
0.102
0.100
0.099
4.0
0.573
0.379
0.279
0.245
0.228
0.217
0.210
0.204
0.200
0.197
6.0
0.859
0.569
0.419
0.368
0.341
0.325
0.314
0.307
0.301
0.296
8.0
1.145
0.759
0.559
0.490
0.455
0.434
0.419
0.409
0.401
0.394
10.0
1.431
0.948
0.699
0.613
0.569
0.542
0.524
0.511
0.501
0.493
T
TDM
A
B
I I
pkp
⁄
(
)
C
–
------------------------------
D
I I
pkp
⁄
(
)
C
–
(
)
2
--------------------------------------
E
I I
pkp
⁄
(
)
C
–
(
)
3
--------------------------------------
+
+
+
⎝
⎠
⎜
⎟
⎛
⎞
×
=
T
RESET
TDM
t
r
1
I I
pkp
⁄
(
)
2
–
--------------------------------
×
=
Summary of Contents for F35
Page 2: ......
Page 4: ......
Page 296: ...5 174 F35 Multiple Feeder Protection System GE Multilin 5 9 TESTING 5 SETTINGS 5 ...
Page 328: ...7 8 F35 Multiple Feeder Protection System GE Multilin 7 2 TARGETS 7 COMMANDS AND TARGETS 7 ...
Page 350: ...A 16 F35 Multiple Feeder Protection System GE Multilin A 1 PARAMETER LIST APPENDIXA A ...
Page 422: ...B 72 F35 Multiple Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIXB B ...
Page 472: ...E 12 F35 Multiple Feeder Protection System GE Multilin E 2 DNP POINT LISTS APPENDIXE E ...