5-86
F35 Multiple Feeder Protection System
GE Multilin
5.4 FLEXLOGIC™
5 SETTINGS
5
ELEMENT:
Breaker control
BREAKER 1 OFF CMD
BREAKER 1 ON CMD
BREAKER 1
Φ
A BAD ST
BREAKER 1
Φ
A INTERM
BREAKER 1
Φ
A CLSD
BREAKER 1
Φ
A OPEN
BREAKER 1
Φ
B BAD ST
BREAKER 1
Φ
A INTERM
BREAKER 1
Φ
B CLSD
BREAKER 1
Φ
B OPEN
BREAKER 1
Φ
C BAD ST
BREAKER 1
Φ
A INTERM
BREAKER 1
Φ
C CLSD
BREAKER 1
Φ
C OPEN
BREAKER 1 BAD STATUS
BREAKER 1 CLOSED
BREAKER 1 OPEN
BREAKER 1 DISCREP
BREAKER 1 TROUBLE
BREAKER 1 MNL CLS
BREAKER 1 TRIP A
BREAKER 1 TRIP B
BREAKER 1 TRIP C
BREAKER 1 ANY P OPEN
BREAKER 1 ONE P OPEN
BREAKER 1 OOS
Breaker 1 open command initiated
Breaker 1 close command initiated
Breaker 1 phase A bad status is detected (discrepancy between the 52/a and
52/b contacts)
Breaker 1 phase A intermediate status is detected (transition from one
position to another)
Breaker 1 phase A is closed
Breaker 1 phase A is open
Breaker 1 phase B bad status is detected (discrepancy between the 52/a and
52/b contacts)
Breaker 1 phase A intermediate status is detected (transition from one
position to another)
Breaker 1 phase B is closed
Breaker 1 phase B is open
Breaker 1 phase C bad status is detected (discrepancy between the 52/a and
52/b contacts)
Breaker 1 phase A intermediate status is detected (transition from one
position to another)
Breaker 1 phase C is closed
Breaker 1 phase C is open
Breaker 1 bad status is detected on any pole
Breaker 1 is closed
Breaker 1 is open
Breaker 1 has discrepancy
Breaker 1 trouble alarm
Breaker 1 manual close
Breaker 1 trip phase A command
Breaker 1 trip phase B command
Breaker 1 trip phase C command
At least one pole of breaker 1 is open
Only one pole of breaker 1 is open
Breaker 1 is out of service
BREAKER 2...
Same set of operands as shown for BREAKER 1
ELEMENT:
Digital counters
Counter 1 HI
Counter 1 EQL
Counter 1 LO
Digital counter 1 output is ‘more than’ comparison value
Digital counter 1 output is ‘equal to’ comparison value
Digital counter 1 output is ‘less than’ comparison value
Counter 2 to Counter 8
Same set of operands as shown for Counter 1
ELEMENT:
Digital elements
Dig Element 1 PKP
Dig Element 1 OP
Dig Element 1 DPO
Digital Element 1 is picked up
Digital Element 1 is operated
Digital Element 1 is dropped out
Dig Element 2 to Dig Element 48
Same set of operands as shown for Dig Element 1
ELEMENT:
FlexElements™
FxE 1 PKP
FxE 1 OP
FxE 1 DPO
FlexElement™ 1 has picked up
FlexElement™ 1 has operated
FlexElement™ 1 has dropped out
FxE 2 to FxE 16
Same set of operands as shown for FxE 1
ELEMENT:
Ground
instantaneous
overcurrent
GROUND IOC1 PKP
GROUND IOC1 OP
GROUND IOC1 DPO
Ground instantaneous overcurrent 1 has picked up
Ground instantaneous overcurrent 1 has operated
Ground instantaneous overcurrent 1 has dropped out
GROUND IOC2 to IOC12
Same set of operands as shown for GROUND IOC 1
ELEMENT:
Ground time
overcurrent
GROUND TOC1 PKP
GROUND TOC1 OP
GROUND TOC1 DPO
Ground time overcurrent 1 has picked up
Ground time overcurrent 1 has operated
Ground time overcurrent 1 has dropped out
GROUND TOC2 to TOC6
Same set of operands as shown for GROUND TOC1
ELEMENT:
Incipient cable fault
detection
INCIPNT FLT 1 OP
INCIPNT FLT 1 OP A
INCIPNT FLT 1 OP B
INCIPNT FLT 1 OP C
INCIPNT FLT 1 PKP
INCIPNT FLT 1 PKP A
INCIPNT FLT 1 PKP B
INCIPNT FLT 1 PKP C
Asserted when incipient cable fault detector 1 operates in any phase
Asserted when incipient cable fault detector 1 operates in phase A
Asserted when incipient cable fault detector 1 operates in phase B
Asserted when incipient cable fault detector 1 operates in phase C
Asserted when incipient cable fault detector 1 picks up in any phase
Asserted when incipient cable fault detector 1 picks up in phase A
Asserted when incipient cable fault detector 1 picks up in phase B
Asserted when incipient cable fault detector 1 picks up in phase C
INCIPNT FLT 2...
Same set of operands as shown for INCIPNT FLT 1
ELEMENT
Non-volatile latches
LATCH 1 ON
LATCH 1 OFF
Non-volatile latch 1 is ON (Logic = 1)
Non-voltage latch 1 is OFF (Logic = 0)
LATCH 2 to LATCH 16
Same set of operands as shown for LATCH 1
Table 5–7: F35 FLEXLOGIC™ OPERANDS (Sheet 2 of 6)
OPERAND TYPE
OPERAND SYNTAX
OPERAND DESCRIPTION
Summary of Contents for F35
Page 2: ......
Page 4: ......
Page 296: ...5 174 F35 Multiple Feeder Protection System GE Multilin 5 9 TESTING 5 SETTINGS 5 ...
Page 328: ...7 8 F35 Multiple Feeder Protection System GE Multilin 7 2 TARGETS 7 COMMANDS AND TARGETS 7 ...
Page 350: ...A 16 F35 Multiple Feeder Protection System GE Multilin A 1 PARAMETER LIST APPENDIXA A ...
Page 422: ...B 72 F35 Multiple Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIXB B ...
Page 472: ...E 12 F35 Multiple Feeder Protection System GE Multilin E 2 DNP POINT LISTS APPENDIXE E ...