![GE Grid Solutions F60 Instruction Manual Download Page 311](http://html.mh-extra.com/html/ge-grid-solutions/f60/f60_instruction-manual_571876311.webp)
GE Multilin
F60 Feeder Protection System
5-173
5 SETTINGS
5.6 GROUPED ELEMENTS
5
IEC CURVES
For European applications, the relay offers three standard curves defined in IEC 255-4 and British standard BS142. These
are defined as IEC Curve A, IEC Curve B, and IEC Curve C. The formulae for these curves are:
,
(EQ 5.9)
where:
T
= operate time (in seconds),
TDM
= Multiplier setting,
I
= input current,
I
pickup
= Pickup Current setting,
K
,
E
=
constants,
t
r
= characteristic constant, and
T
RESET
= reset time in seconds (assuming energy capacity is 100%
and
RESET
is “Timed”)
Table 5–25: IEC (BS) INVERSE TIME CURVE CONSTANTS
IEC (BS) CURVE SHAPE
K
E
T
R
IEC Curve A (BS142)
0.140
0.020
9.7
IEC Curve B (BS142)
13.500
1.000
43.2
IEC Curve C (BS142)
80.000
2.000
58.2
IEC Short Inverse
0.050
0.040
0.500
Table 5–26: IEC CURVE TRIP TIMES (IN SECONDS)
MULTIPLIER
(TDM)
CURRENT (
I
/
I
pickup
)
1.5
2.0
3.0
4.0
5.0
6.0
7.0
8.0
9.0
10.0
IEC CURVE A
0.05
0.860
0.501
0.315
0.249
0.214
0.192
0.176
0.165
0.156
0.149
0.10
1.719
1.003
0.630
0.498
0.428
0.384
0.353
0.330
0.312
0.297
0.20
3.439
2.006
1.260
0.996
0.856
0.767
0.706
0.659
0.623
0.594
0.40
6.878
4.012
2.521
1.992
1.712
1.535
1.411
1.319
1.247
1.188
0.60
10.317
6.017
3.781
2.988
2.568
2.302
2.117
1.978
1.870
1.782
0.80
13.755
8.023
5.042
3.984
3.424
3.070
2.822
2.637
2.493
2.376
1.00
17.194
10.029
6.302
4.980
4.280
3.837
3.528
3.297
3.116
2.971
IEC CURVE B
0.05
1.350
0.675
0.338
0.225
0.169
0.135
0.113
0.096
0.084
0.075
0.10
2.700
1.350
0.675
0.450
0.338
0.270
0.225
0.193
0.169
0.150
0.20
5.400
2.700
1.350
0.900
0.675
0.540
0.450
0.386
0.338
0.300
0.40
10.800
5.400
2.700
1.800
1.350
1.080
0.900
0.771
0.675
0.600
0.60
16.200
8.100
4.050
2.700
2.025
1.620
1.350
1.157
1.013
0.900
0.80
21.600
10.800
5.400
3.600
2.700
2.160
1.800
1.543
1.350
1.200
1.00
27.000
13.500
6.750
4.500
3.375
2.700
2.250
1.929
1.688
1.500
IEC CURVE C
0.05
3.200
1.333
0.500
0.267
0.167
0.114
0.083
0.063
0.050
0.040
0.10
6.400
2.667
1.000
0.533
0.333
0.229
0.167
0.127
0.100
0.081
0.20
12.800
5.333
2.000
1.067
0.667
0.457
0.333
0.254
0.200
0.162
0.40
25.600
10.667
4.000
2.133
1.333
0.914
0.667
0.508
0.400
0.323
0.60
38.400
16.000
6.000
3.200
2.000
1.371
1.000
0.762
0.600
0.485
0.80
51.200
21.333
8.000
4.267
2.667
1.829
1.333
1.016
0.800
0.646
1.00
64.000
26.667
10.000
5.333
3.333
2.286
1.667
1.270
1.000
0.808
IEC SHORT TIME
0.05
0.153
0.089
0.056
0.044
0.038
0.034
0.031
0.029
0.027
0.026
0.10
0.306
0.178
0.111
0.088
0.075
0.067
0.062
0.058
0.054
0.052
0.20
0.612
0.356
0.223
0.175
0.150
0.135
0.124
0.115
0.109
0.104
0.40
1.223
0.711
0.445
0.351
0.301
0.269
0.247
0.231
0.218
0.207
0.60
1.835
1.067
0.668
0.526
0.451
0.404
0.371
0.346
0.327
0.311
0.80
2.446
1.423
0.890
0.702
0.602
0.538
0.494
0.461
0.435
0.415
1.00
3.058
1.778
1.113
0.877
0.752
0.673
0.618
0.576
0.544
0.518
T
TDM
K
I I
pickup
⁄
(
)
E
1
–
---------------------------------------
×
=
T
RESET
TDM
t
r
1
I I
pickup
⁄
(
)
2
–
---------------------------------------
×
=
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...