5 SETTINGS
5.4 SYSTEM SETUP
5
All five triggering functions and the user-definable condition are consolidated (ORed) and connected to the PMU recorder.
Each trigger can be programmed to log its operation into the event recorder, and to signal its operation via targets. The five
triggers drive the STAT bits of the data frame to inform the destination of the synchrophasor data regarding the cause of
trigger. The following convention is adopted to drive bits 11, 3, 2, 1, and 0 of the STAT word.
Figure 5–47: STAT BITS LOGIC
The trigger reset (drop-off) timer is available for all five triggering functions (FREQ, ROCOF, VOLT, CURR, POWER) in indi-
vidual trigger settings under the TRIGGER DPO TIME setting. This asserts individual trigger operand and overall PMU x
TRIGGERED operand with stat bits 3 and 11 for a fixed interval defined by this setting. If it is required that PMU x TRIG-
GERED operand with stat bits 3 and 11 stay longer than the individual reset timer, then use the PMU x USER TRIGGER
setting assigned with appropriate elements and FlexLogic. In short, in case of USER TRIGGER, the drop-off time needs to
be implemented using FlexLogic.
e) USER TRIGGERING
PATH: SETTINGS
SYSTEM SETUP
PHASOR MEASUREMENT...
PMU 1 TRIGGERING
PMU 1 USER TRIGGER
The user trigger allows customized triggering logic to be constructed from FlexLogic. The entire triggering logic is refreshed
once every two power system cycles.
f) FREQUENCY TRIGGERING
PATH: SETTINGS
SYSTEM SETUP
PHASOR MEASUREMENT...
PMU 1 TRIGGERING
PMU 1 FREQUENCY TRIGGER
PMU 1 USER
TRIGGER
PMU1 USER TRIGGER:
Off
Range: FlexLogic operands
PMU 1 FREQUENCY
TRIGGER
PMU 1 FREQ TRIGGER
FUNCTION: Disabled
Range: Enabled, Disabled
MESSAGE
PMU 1 FREQ TRIGGER
LOW-FREQ: 49.00 Hz
Range: 20.00 to 70.00 Hz in steps of 0.01
MESSAGE
PMU 1 FREQ TRIGGER
HIGH-FREQ: 61.00 Hz
Range: 20.00 to 70.00 Hz in steps of 0.01
MESSAGE
PMU 1 FREQ TRIGGER
PKP TIME: 0.10 s
Range: 0.00 to 600.00 s in steps of 0.01
MESSAGE
PMU 1 FREQ TRIGGER
DPO TIME: 1.00 s
Range: 0.00 to 600.00 s in steps of 0.01
MESSAGE
PMU 1 FREQ TRIG BLK:
Off
Range: FlexLogic operand
MESSAGE
PMU 1 FREQ TRIGGER
TARGET: Self-Reset
Range: Self-Reset, Latched, Disabled
MESSAGE
PMU 1 FREQ TRIGGER
EVENTS: Disabled
Range: Enabled, Disabled
8470004A2.CDR
bit 0
PMU 1 recorder
SETTING
Off = 0
User Trigger
FLEXLOGIC OPERANDS
PMU 1 FREQ TRIGGER
PMU 1 ROCOF TRIGGER
PMU 1 VOLT TRIGGER
PMU 1 CURR TRIGGER
PMU 1 POWER TRIGGER
OR
OR
bit 1
bit 2
OR
bit 3, bit 11
FLEXLOGIC OPERAND
PMU 1 TRIGGERED
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...